Yes.Ok, so wire the hots in/out of the gfci breaker and I am all set to have my two elements be gfci protected?
Yes.
It will function just as well with that connection on the grounding conductor.According to Seimens GFCI wiring datasheet:
Note: A load neutral is not required on the circuit.
However, the white line neutral (pigtail) must be
connected to the panel neutral for the device to
function.
Based on this statement there must be a neutral connection between the panel and the GFCI breaker in order for it to work.
What ever. Apparently you are the expert..False a neutral and a ground are different neutral is the return path for the hots to carry unbalanced load so the will have voltage on them.
False a neutral and a ground are different neutral is the return path for the hots to carry unbalanced load so the will have voltage on them.
False a neutral and a ground are different neutral is the return path for the hots to carry unbalanced load so the will have voltage on them.
Yes but only at the first means of disconnect never again. A ground touching a neutral week trip a afci breaker. It's considered a fault.
Untrue......neutral is the return path for the hots to carry unbalanced load so the will have voltage on them.
What???It's manly if you share neutrals or have fluorescent lighting the neutral will have voltage if you hold both neutrals to complete the path it will zap you.
It's manly if you share neutrals or have fluorescent lighting the neutral will have voltage if you hold both neutrals to complete the path it will zap you.