Depends on how many amps you're running through the wire & what kind of receptacle you're wiring it to. The below chart may help...
Where did you get this chart? I thought the 80% rule is for sizing circuit breakers and is independent of the cable to be used. I've also been led to believe it's fine to run 55A through a cable that's rated for 55A. Please let me know if that's wrong.
Hope someone can correct me, but I think the 80% rule has something to do with the anticipated load from a given number of outlets on a circuit.The 80% "rule" is for sizing circuit breakers as far as I know.
Where did you get this chart? I thought the 80% rule is for sizing circuit breakers and is independent of the cable to be used. I've also been led to believe it's fine to run 55A through a cable that's rated for 55A. Please let me know if that's wrong.
Continuous loads (expected to operate continuoulsy for 3 hours or more) are subject to conductor derating (80% rule).
Non-continuous loads which I think applies to most of our electrical builds can be sized for 100% of the conductor capacity.