I have a friend who wants to convert their old 2 bbl system to electric. I want to start off by saying that I am an engineer by trade with automation experience and home wiring experience including an entire electric service. We are looking to do 3X 5500W elements in the BK and I am not sure what in the HLT just yet. I was hoping to find a 100A GFCI breaker or spa panel, but I have had no luck. I think we are going to have to do 2 separate spa panels or 3 separate 30A GFCI breakers. For a 200A service this will be a huge load, but doable. No electric heat, no electric dryer, maybe hold off on making that huge Sunday dinner until after brewday. What are your thoughts for the power mains since 3-phase is not an option and we definitely want ground fault protection.