Did my first brew session on my new E-HERMS system over the weekend and I have a few questions that I am hoping someone can help me with.
First I followed the steps here and plugged them in to the calculator to find the initial values for my PID in the Elsinore. My values were P=14 I=400 D=30 and a Duty Time of 10s. Using these values and a set point of 154 in the HLT the element would be at 100% until the temp was in the 140's then it would drop to 14-20% until closer to temp.
This lead to really long ramp times between temp changes so I changed P to 40 and then the element would stay at 100% until within a degree or two of the set point. This did lead to some minor overshooting of the set point, but nothing too bad. Maybe 1-2 degrees over in the HLT.
I am using 20g SS Bayou Classic kettles for the HLT and MLT with a 5500w element in the HLT with a 50' 1/2" SS coil in the HLT. The temp probe is in the out flow of the HLT and the water in the HLT was continuously recirculated during heating.
Do my PID values look way off? When i used P=40 the ramp times were faster and the temp stayed within +-2 of the set point. I would like to tighten that up to +-.5 if possible.
What do most of you use for a Duty Time when using PID control? How about when using manual control of the element?
My next question is about temp difference between the MLT and the HLT. I noticed that they never really equalized on my system during the 60 min mash. The MLT was consistently 2-4 degrees lower than the HLT set point.
The temp probe for the MLT is also in the outflow of the MLT and the mash was continuously recirculated during the mash. I ran both the water and the wort pumps full open during the mash.
Is it normal to have this big of a temp difference between the HLT set point and the mash temp?
I know we can just compensate and set the HLT to 4 degrees over mash temp, but from my reading on theelectricbreweery.com I was under the impression that the temps would equalize.
sorry for the long post, but i am trying to give as much info as i can
thanks,
First I followed the steps here and plugged them in to the calculator to find the initial values for my PID in the Elsinore. My values were P=14 I=400 D=30 and a Duty Time of 10s. Using these values and a set point of 154 in the HLT the element would be at 100% until the temp was in the 140's then it would drop to 14-20% until closer to temp.
This lead to really long ramp times between temp changes so I changed P to 40 and then the element would stay at 100% until within a degree or two of the set point. This did lead to some minor overshooting of the set point, but nothing too bad. Maybe 1-2 degrees over in the HLT.
I am using 20g SS Bayou Classic kettles for the HLT and MLT with a 5500w element in the HLT with a 50' 1/2" SS coil in the HLT. The temp probe is in the out flow of the HLT and the water in the HLT was continuously recirculated during heating.
Do my PID values look way off? When i used P=40 the ramp times were faster and the temp stayed within +-2 of the set point. I would like to tighten that up to +-.5 if possible.
What do most of you use for a Duty Time when using PID control? How about when using manual control of the element?
My next question is about temp difference between the MLT and the HLT. I noticed that they never really equalized on my system during the 60 min mash. The MLT was consistently 2-4 degrees lower than the HLT set point.
The temp probe for the MLT is also in the outflow of the MLT and the mash was continuously recirculated during the mash. I ran both the water and the wort pumps full open during the mash.
Is it normal to have this big of a temp difference between the HLT set point and the mash temp?
I know we can just compensate and set the HLT to 4 degrees over mash temp, but from my reading on theelectricbreweery.com I was under the impression that the temps would equalize.
sorry for the long post, but i am trying to give as much info as i can
thanks,