I'm really having a hard time getting my head around how this contactor thing works. I'm in the process of wiring up a system that will use 2 - 5500W heating elements with 2 pumps. It'll be HERMS based. In the picture below I can't see how the heating element wouldn't have 120V going through it at all times as long as switch 7 is on. This certainly wouldn't be good. Can someone take a look at this and let me know if I'm just going crazy here? Maybe explain how it's supposed to work?
Click image for larger version

Name:	contactor question.jpg
Views:	274
Size:	51.6 KB
ID:	50974  

 
Reply With Quote
Old 03-04-2012, 03:19 PM   #2
fbold1
Brew Nut
HBT_SUPPORTER.png
 
fbold1's Avatar
Recipes 
 
Dec 2011
North Coast, Ohio
Posts: 254
Liked 8 Times on 8 Posts


I see that, but what about sw 5. It looks to me that when sw 7 is in the other position it may be using the thermal to control it and the other position may be a manual over ride to turn the heater on manually. Since only part of the drawing is shown I can't tell.
__________________
"Whoever makes a poor beer is transferred to the dung-hill." Edict in the City of Danzig, 11th Century.

 
Reply With Quote
Old 03-04-2012, 03:22 PM   #3
BigHefty
HBT_LIFETIMESUPPORTER.png
 
BigHefty's Avatar
Recipes 
 
Dec 2009
Davison, MI
Posts: 181
Liked 5 Times on 4 Posts


I wondered about that too but regardless of what position #5 is in, the one leg is always going to be energizing the coil as long as #7 is in the 1-2 position. Below is the complete schematic. It's one of P-J's drawings.

Sigh... the picture is hard to read but the original is here http://www.pjmuth.org/beerstuff/imag...ring-2-4-a.jpg
Click image for larger version

Name:	BCS-460-wiring-2-4-a.jpg
Views:	1045
Size:	47.4 KB
ID:	50981  

 
Reply With Quote
Old 03-04-2012, 03:33 PM   #4
P-J
HBT_LIFETIMESUPPORTER.png
Recipes 
 
Mar 2010
Charlotte, NC
Posts: 3,336
Liked 301 Times on 235 Posts


Quote:
Originally Posted by BigHefty View Post
I'm really having a hard time getting my head around how this contactor thing works. I'm in the process of wiring up a system that will use 2 - 5500W heating elements with 2 pumps. It'll be HERMS based. In the picture below I can't see how the heating element wouldn't have 120V going through it at all times as long as switch 7 is on. This certainly wouldn't be good. Can someone take a look at this and let me know if I'm just going crazy here? Maybe explain how it's supposed to work?
The heating element is a 240V element. It has one side of the 240V connected (blue wire) when the contactor is energized. The other side of the 240V is connected through the contactor and then through the SSR (red wire). The element will have power applied only when the SSR is allowing current flow. When the SSR is blocking current flow it is effectively disconnected. With only one side connected there is no path for current to flow.

 
Reply With Quote
Old 03-04-2012, 03:38 PM   #5
BigHefty
HBT_LIFETIMESUPPORTER.png
 
BigHefty's Avatar
Recipes 
 
Dec 2009
Davison, MI
Posts: 181
Liked 5 Times on 4 Posts


Quote:
Originally Posted by P-J View Post
The heating element is a 240V element. It has one side of the 240V connected (blue wire) when the contactor is energized. The other side of the 240V is connected through the contactor and then through the SSR (red wire). The element will have power applied only when the SSR is allowing current flow. When the SSR is blocking current flow it is effectively disconnected. With only one side connected there is no path for current to flow.
Hmmmm..... I'm still not getting it. Isn't the contactor energized at all times, meaning the blue is providing 1 leg of current to the heating element? And, when the SSR allows, the 2nd leg is providing current to the heating element? I guess I'm not seeing how the SSR is prohibiting current from reaching the element when it doesn't appear to be controlling the contactor.

 
Reply With Quote
Old 03-04-2012, 03:43 PM   #6
P-J
HBT_LIFETIMESUPPORTER.png
Recipes 
 
Mar 2010
Charlotte, NC
Posts: 3,336
Liked 301 Times on 235 Posts


Quote:
Originally Posted by BigHefty View Post
Hmmmm..... I'm still not getting it. Isn't the contactor energized at all times, meaning the blue is providing 1 leg of current to the heating element? And, when the SSR allows, the 2nd leg is providing current to the heating element? I guess I'm not seeing how the SSR is prohibiting current from reaching the element when it doesn't appear to be controlling the contactor.
Ok... Question for you. What is the path for current to flow through the element when the SSR is set to not conduct current?

 
Reply With Quote
Old 03-04-2012, 03:50 PM   #7
danbass
Recipes 
 
May 2008
Milwaukee, WI
Posts: 132
Liked 1 Times on 1 Posts


The SSR acts as a very fast digital light switch, controlled by the PID. The one leg that might always be on still won't power the element because the other leg is open.

Remember old christmas lights, where if one of the last bulbs went out, the entire string went out? There was still always power there, even to the first bulbs, but the entire circuit was open because one of the bulbs had burnt out. If you pulled out the neutral leg on a light bulb, and powered the hot leg, the light bulb wouldn't turn on. Circuit needs to be complete for any power to move.
__________________
Quote:
Originally Posted by paulthenurse View Post
And we also decided to make a Barley Wine this weekend as a starter. (That is probably one of the silliest sentences I've ever written.)
On tap: Russian Imperial Stout (nitro), Imperial Red, Kentucky Common Rye, Ruination Clone.
Secondary: RedWine (Imperial Red x2)
Primary: Chocolate Rye Stout, Utopias Inspired 2nd attempt, Oberon Clone
On Deck: Imperial Red, Kentucky Common. TBD.

 
Reply With Quote
Old 03-04-2012, 03:54 PM   #8
BigHefty
HBT_LIFETIMESUPPORTER.png
 
BigHefty's Avatar
Recipes 
 
Dec 2009
Davison, MI
Posts: 181
Liked 5 Times on 4 Posts


This is what I'm envisioning the current of the blue (line 1) to be doing when #7 is switched to 1-2. Am I wrong?
Click image for larger version

Name:	contactor question2.jpg
Views:	205
Size:	51.1 KB
ID:	50987  

 
Reply With Quote
Old 03-04-2012, 03:55 PM   #9
fbold1
Brew Nut
HBT_SUPPORTER.png
 
fbold1's Avatar
Recipes 
 
Dec 2011
North Coast, Ohio
Posts: 254
Liked 8 Times on 8 Posts


I see, the contactor stays on but the controller cycles power to the element.
__________________
"Whoever makes a poor beer is transferred to the dung-hill." Edict in the City of Danzig, 11th Century.

 
Reply With Quote
Old 03-04-2012, 04:01 PM   #10
P-J
HBT_LIFETIMESUPPORTER.png
Recipes 
 
Mar 2010
Charlotte, NC
Posts: 3,336
Liked 301 Times on 235 Posts


Quote:
Originally Posted by BigHefty View Post
This is what I'm envisioning the current of the blue (line 1) to be doing when #7 is switched to 1-2. Am I wrong?
You are showing a power path through the equipment ground connection at the element (green wire). There is no electrical path from the element shell to the power input terminals.

 
Reply With Quote
Reply
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
SSR, Contactor? both? help me K.I.S.S mavrick1903 Electric Brewing 19 02-13-2013 06:57 AM
P-J Diagrams 240 V Contactor? rcooper44537 Electric Brewing 8 12-02-2011 01:50 PM
Contactor question GRHunter Electric Brewing 3 05-25-2011 11:32 AM
Contactor load HHP Electric Brewing 3 05-03-2011 01:13 AM
Mercury contactor vs. SSR burglar Electric Brewing 8 01-26-2011 02:48 AM


Forum Jump