OneHoppyGuy
Well-Known Member
Okay, Here is the project:
BCS 460
24VAC Honeywell Gas valves w/intermittent spark igniters
SSR 4 relay 5V module
Note: this system was working and the same wiring has worked for other brew stands we have built (BrewSteel.com)
All grounds are tied together
24VAC Transformer runs power to panel mounted switch
From switch power goes to N.O. relay contact
Common relay contact connected to gas valve ignition module
Using Output 0 (tried 0 - 3) manually
- Nothing attached to the BCS - BCS stays connected Output 0 remains on
- BCS attached to relay - BCS stays connected Output 0 remains on
- BCS attached to relay, Gas Valve igniter NOT grounded - igniter fires, BCS stays connected Output 0 remains on
- Direct jumper between relay contacts, igniter grounded - igniter fires
- BCS attached to relay, Gas Valve igniter grounded - igniter fires for a split second, BCS disconnects
I have tried 3 different relay modules
I am am stumped. Please help if you can.
BCS 460
24VAC Honeywell Gas valves w/intermittent spark igniters
SSR 4 relay 5V module
Note: this system was working and the same wiring has worked for other brew stands we have built (BrewSteel.com)
All grounds are tied together
24VAC Transformer runs power to panel mounted switch
From switch power goes to N.O. relay contact
Common relay contact connected to gas valve ignition module
Using Output 0 (tried 0 - 3) manually
- Nothing attached to the BCS - BCS stays connected Output 0 remains on
- BCS attached to relay - BCS stays connected Output 0 remains on
- BCS attached to relay, Gas Valve igniter NOT grounded - igniter fires, BCS stays connected Output 0 remains on
- Direct jumper between relay contacts, igniter grounded - igniter fires
- BCS attached to relay, Gas Valve igniter grounded - igniter fires for a split second, BCS disconnects
I have tried 3 different relay modules
I am am stumped. Please help if you can.