Get your HBT Growlers, Shirts and Membership before the Rush!


Home Brew Forums > Home Brewing Beer > Electric Brewing > Does turning off the contactor cause the PID to adjust itself?
Reply
 
LinkBack Thread Tools
Old 01-18-2013, 12:31 PM   #21
BadNewsBrewery
Basement Brewer
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
BadNewsBrewery's Avatar
Recipes 
 
Join Date: Oct 2012
Location: Severn, MD
Posts: 1,159
Liked 116 Times on 95 Posts
Likes Given: 55

Default

Quote:
Originally Posted by jeffmeh View Post
No problem. Is there a simple way to set the PID not to heat other than backing the setpoint down? Manual mode at 0%? Any other method?
The only ways I know are as you described. You could also unplug the RTD from the panel, which would cause the PID to go into alarm and stop sending signals. Unfortunately, the 2352 sounds an alarm tone if that happens (the SWA-2451 does not), so if you don't have an on/off switch on your alarm then that rapidly becomes a terrible idea.
__________________
Building a Bad News Brewery - eHERMS

2014:
5gal Scottish Wee Heavy
5gal Saison
15gal American Pale Ale
20gal Belgian Wit
10gal Oktoberfest
10gal Southern Pecan Ale
5gal Winter Spice Ale

Keg 1: Apfelwein
Keg 2: Oktoberfest
Keg 3: Southern Pecan
Keg 4: Winter Spice Ale
BadNewsBrewery is offline
 
Reply With Quote Quick reply to this message
Old 01-18-2013, 04:21 PM   #22
biertourist
Feedback Score: 1 reviews
Recipes 
 
Join Date: Oct 2012
Location: Woodinville, WA
Posts: 655
Liked 66 Times on 57 Posts
Likes Given: 29

Default

BadNews,

I have a single PID control panel that I just finished with one RTD going to my HLT and one to my BK, I plan on unplugging the RTD to the HLT and plugging in the RTD to the BK after I finish mash-in. I've tested this with a simple walk-through with water in my vessels but ran out of wire and never connected my alarm (my next to-do item) -I don't have a switch to turn off my alarm -is there any configuration setting that I can use in the 2352 to disable the alarm upon disconnecting an RTD? -I still want the alarm to go off when my BK reaches 205F, but I don't want it to go off when I swap RTDs.

Note: I do have an on/off switch for the PID controller itself. If I could just turn off the PID, then swap the RTDs and then turn it back on that is a workaround that would work for me, but I'd prefer to disable the "disconnected RTD" alarm.


Adam

__________________
biertourist is offline
 
Reply With Quote Quick reply to this message
Old 01-18-2013, 04:23 PM   #23
biertourist
Feedback Score: 1 reviews
Recipes 
 
Join Date: Oct 2012
Location: Woodinville, WA
Posts: 655
Liked 66 Times on 57 Posts
Likes Given: 29

Default

Apologize for the thread hijack; Badnews's post just instantly concerned me while I'm only 7 days away from brewing my first batch on this system.

Adam

__________________
biertourist is offline
 
Reply With Quote Quick reply to this message
Old 01-18-2013, 05:58 PM   #24
BadNewsBrewery
Basement Brewer
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
BadNewsBrewery's Avatar
Recipes 
 
Join Date: Oct 2012
Location: Severn, MD
Posts: 1,159
Liked 116 Times on 95 Posts
Likes Given: 55

Default

Answered via PM to stay on topic.

__________________
Building a Bad News Brewery - eHERMS

2014:
5gal Scottish Wee Heavy
5gal Saison
15gal American Pale Ale
20gal Belgian Wit
10gal Oktoberfest
10gal Southern Pecan Ale
5gal Winter Spice Ale

Keg 1: Apfelwein
Keg 2: Oktoberfest
Keg 3: Southern Pecan
Keg 4: Winter Spice Ale
BadNewsBrewery is offline
 
Reply With Quote Quick reply to this message
Old 01-18-2013, 07:07 PM   #25
Bobby_M
Vendor and Brewer
HBT_SPONSOR.png
Vendor Ads 
Feedback Score: 2 reviews
 
Bobby_M's Avatar
Recipes 
 
Join Date: Aug 2006
Location: Whitehouse Station, NJ
Posts: 22,286
Liked 1078 Times on 716 Posts
Likes Given: 28

Default

I'm still baffled by the whole "fuzzy logic" terminology. It sounds to me like another way of describing the inherent function of PID. In other words, what makes PID smarter than a simple on/off controller that happens to have a hysteresis setting. When set point is a long way away, we expect the PID to run the element balls out until it gets close, then ease back on the power cycles as it gets closer and closer. . Autotune essentially tests a few different cycle times out to see how fast the system responds and then sets the PID values appropriately.

Auber seems to suggest this unit is different than typical PID function but I'm not smart enough to understand how.

__________________
BrewHardware.com has a new website. Please check it out and let me know what you think!
New 100% Stainless Steel Heating Elements are IN!
Chugger Pumps, Pump Kits, Camlocks, Sightglasses, Clear USA made Silicone Tubing, RIMS, Electric Install Parts, etc. Did you know we are also now a full service homebrew shop selling malt, hops, yeast (Wyeast), etc?
Bobby_M is online now
 
Reply With Quote Quick reply to this message
Old 01-18-2013, 08:32 PM   #26
jeffmeh
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
jeffmeh's Avatar
Recipes 
 
Join Date: Feb 2009
Posts: 1,886
Liked 147 Times on 126 Posts
Likes Given: 19

Default

Quote:
Originally Posted by Bobby_M View Post
I'm still baffled by the whole "fuzzy logic" terminology. It sounds to me like another way of describing the inherent function of PID. In other words, what makes PID smarter than a simple on/off controller that happens to have a hysteresis setting. When set point is a long way away, we expect the PID to run the element balls out until it gets close, then ease back on the power cycles as it gets closer and closer. . Autotune essentially tests a few different cycle times out to see how fast the system responds and then sets the PID values appropriately.

Auber seems to suggest this unit is different than typical PID function but I'm not smart enough to understand how.
Bobby, I'm not smart enough either, but I did long ago understand fuzzy logic. It is really just a different method for expressing an algorithm, in an analog fashion in more or less natural language, rather than a digital one in equations. The advantage for a continuous control system should be that is easier for human beings to implement and optimize the algorithm, thus more likely (or less costly to get the algorithm there) to result in faster convergence to the setpoint and a tighter error band. I'm pretty sure that there is always an equivalent "traditional" algorithm to the fuzzy one, and vice versa.

While grossly oversimplified, the traditional algorithm would know that error = -10 def F, while the fuzzy one might have defined a function for "negative error" where anything greater than or equal to the setpoint would yield 0, anything less than 100 deg F below the setpoint would yield 1, and everything in between would yield something in between 0 and 1. Then the fuzzy algorithm could be specified with statements like "If error is negative then do x." It really just provides a layer of abstraction allowing for specification more "in words" than "in numbers."
__________________
jeffmeh is offline
 
Reply With Quote Quick reply to this message
Old 01-18-2013, 09:00 PM   #27
stlbeer
Senior Member
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
stlbeer's Avatar
Recipes 
 
Join Date: Jan 2008
Location: Fenton, MO
Posts: 913
Liked 35 Times on 34 Posts
Likes Given: 89

Default

I really think we're over thinking this. Auber makes no mention of a "break in period" which is what this sounds like you're talking about. You autotune the device and so long as during the auto tuning you're running your pumps at the same flow rate as you would when you're pumping wort, the PID parameters will be set pretty darn close. The PID learns how much energy your system can put in and how much it losses. If you change that somehow then you need to re-tune.

Regardless, once set, it doesn't change those settings. I haven't seen my PID's overshoot their set temperature by more than 0.1*F.

I too am baffled a bit by the fuzzy logic statements. It tends to imply the values used are more of a possible range of values. Perhaps this is to offset some of the integral windup?

__________________
My RIMS eBrewery build
stlbeer is offline
 
Reply With Quote Quick reply to this message
Old 01-18-2013, 09:19 PM   #28
jeffmeh
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
jeffmeh's Avatar
Recipes 
 
Join Date: Feb 2009
Posts: 1,886
Liked 147 Times on 126 Posts
Likes Given: 19

Default

Quote:
Originally Posted by stlbeer View Post
I really think we're over thinking this. Auber makes no mention of a "break in period" which is what this sounds like you're talking about. You autotune the device and so long as during the auto tuning you're running your pumps at the same flow rate as you would when you're pumping wort, the PID parameters will be set pretty darn close. The PID learns how much energy your system can put in and how much it losses. If you change that somehow then you need to re-tune.

Regardless, once set, it doesn't change those settings. I haven't seen my PID's overshoot their set temperature by more than 0.1*F.

I too am baffled a bit by the fuzzy logic statements. It tends to imply the values used are more of a possible range of values. Perhaps this is to offset some of the integral windup?
Agreed regarding the over-thinking, but at least we answered the original question. Parameters change on autotune, or when you manually change them. End of story.

Now, back to the over-thinking on fuzzy logic. Yes, Auber's answer to me certainly implied that one thing the fuzzy logic algorithm does is detect an acceleration of the rate of change and offset the integral windup. Not that one could not do the same with a non-fuzzy algorithm, lol.
__________________
jeffmeh is offline
 
Reply With Quote Quick reply to this message
Old 01-18-2013, 11:55 PM   #29
Robhansen
Hoghead Brewing
HBT_SUPPORTER.png
Feedback Score: 0 reviews
Recipes 
 
Join Date: Sep 2012
Location: Monroe City, IN
Posts: 33
Default

And I thank ya for that!

__________________
Robhansen is online now
 
Reply With Quote Quick reply to this message
Old 01-21-2013, 03:32 PM   #30
kal
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
kal's Avatar
Recipes 
 
Join Date: Nov 2006
Location: Ottawa, Canada
Posts: 2,190
Liked 220 Times on 151 Posts
Likes Given: 6

Default

Quote:
Originally Posted by BadNewsBrewery View Post
By reading that, I thought that if I just left my PID alone, it would learn the setup over time. I could force the learning by using Auto-Tune, but it wasn't a required step as the PID would work it all out. We now know that this is not true, per Auber.
Interesting. I did indeed think that the PID would (over maybe half a dozen or so batches) "learn" the system without having to manually force auto-tune. Based on this thread it appears this is incorrect and that you should force an auto-tune the first time the setup is used and every time you make any changes to the setup.

I'll go change it on my website just to be clear that auto-tune should be run. It'll be updated in a few minutes...

Quote:
No ding on Kal - like I said, he's the veritable Godfather of electric brewing. One bit of misinformation out of the veritable tomes he has written... that's not a bad average.
It still bugs me. I don't like mistakes.

Kal
__________________
TheElectricBrewery.com: A step by step guide to building your own electric brewery
My basement/bar/brewery build 2.0
kal is offline
 
Reply With Quote Quick reply to this message
Reply



Quick Reply
Message:
Options
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
SSR, Contactor? both? help me K.I.S.S mavrick1903 Electric Brewing 19 02-13-2013 06:57 AM
One contactor for two elements? sflegacy Electric Brewing 10 12-24-2012 03:37 PM
SSR then Contactor or Contactor then SSR? biertourist Electric Brewing 18 12-12-2012 04:23 PM
What value does a contactor add? Cromwell Electric Brewing 8 09-27-2012 08:43 PM
Checking on a Contactor. Skodi Electric Brewing 4 09-02-2012 12:56 AM