I recently picked up an MH1210 temperature controller for small $$ (similar appearance to the STC-1K but single stage and reads in Fahrenheit) and had it running in my office for the last couple of days before I realized it was clearly reading low. Surrounded the unit's NTC probe with the tip of my Thermapen and two other digital thermometer probes, all four within a quarter inch of each other, and after giving them all plenty of time to settle down, the three agreed that the fourth was 5.4 degrees low.
I'm going to be installing this in the front of my new keezer lid, and those 5.4 degrees would likely have led to six frozen kegs of beer.
Same old advise writ once more: never assume, always check. In this case it was pretty much dumb luck that I checked. Fortunately the controller provides +/- 10.0°F offset range for the probe channel...
Cheers!
I'm going to be installing this in the front of my new keezer lid, and those 5.4 degrees would likely have led to six frozen kegs of beer.
Same old advise writ once more: never assume, always check. In this case it was pretty much dumb luck that I checked. Fortunately the controller provides +/- 10.0°F offset range for the probe channel...
Cheers!