Hey everyone,

I am looking for advice regarding a melted breaker inside my control panel.

The cause of the issue is still unknown (to me anyway). The breaker started melting, but did not trip.

The reason I knew something was going on was the burnt plastic smell.

For the last couple years the panel was working just fine.

Is this just a defective breaker? The rest of the panel is still in good shape otherwise.

I will be changing the breaker, but my main concern here is to prevent this from happening again.

Let me know if there is something I should investigate further.

Thank you for your help.
 

Attachments

  • 20200101_094939.jpg
    20200101_094939.jpg
    306.3 KB
  • 20200101_094944.jpg
    20200101_094944.jpg
    462.5 KB
  • 20200101_095811.jpg
    20200101_095811.jpg
    351 KB
  • 20200101_095818.jpg
    20200101_095818.jpg
    150.5 KB
  • 20200101_095850.jpg
    20200101_095850.jpg
    173.1 KB
  • 20200101_095946.jpg
    20200101_095946.jpg
    302.2 KB
  • 20200101_095953.jpg
    20200101_095953.jpg
    212.8 KB
I'd go with poor connection too. Looks like they may have had some of the insulation inside
the clamping mechanism. Should have been stripped back further.

All the Best,
D. White
 
Loose connection?
Absolutely a loose/poor connection. Whenever you see melting or discoloration around the connections of a high current circuit, it's because the resistance of the connection went up, causing excessive heat at the connection. The discoloration/melting happens where the heat is being generated.

Brew on :mug:
 
Thank you everyone! I'll strip the next one further back.
And make sure the wire strands are all fit correctly into the clamp zone, and all connections are torqued properly. It's also a good idea to periodically go in and re-tighten all connections, since heating/cooling related to normal operations can sometimes cause connections to loosen.

Brew on :mug:
 
And make sure the wire strands are all fit correctly into the clamp zone, and all connections are torqued properly. It's also a good idea to periodically go in and re-tighten all connections, since heating/cooling related to normal operations can sometimes cause connections to loosen.

Brew on :mug:
Once I receive the new part and install it I shall re-tighten everything else. That is not something I have been doing. Might be why it took two years to finally melt.

Cheers!
 
Good thing you where around to smell the burnt plastic.

I went through my house and brewing sub panel recently and found more than one wire clamp almost a full turn loose. I guess I will put it on the calendar as an annual maintenance item.
 
A new wire is going in that's for sure. I have a spa GFCI panel running the control panel.

I would say I was lucky, since I was having breakfast as the water was heating up. I could've come down too late.
 