Yes you add up your continuous amperages if they are all connected to the same power cord. And that appears to be the 3.8 + 7.2 = 11 amps.
LRA is not quite the same as starting amperage though the two can be about the same value. LRA will likely always be a higher number. Both will only be a momentary increase in demand for a very brief time. I think starting amperage is a older term defined differently.
You don't have to have a device that is built for 30 amps of draw. It just has to be built to briefly handle that amount of current. You'd be okay if you found a device rated at over the 11 amps your refrigerator continuously draws when cooling. And typically the next step up is 15 amps. Then your only concern is how much momentary draw the device can handle.
Not all or even many sold for us as untrained in electrical knowledge will have that specification. But many are built to handle expected overloads due to surges and starting of stuff. But the amount they can handle varies on what the designer or engineer thought it should be for that devices expected use.
And take the above with the understanding that I don't have the training to even state that. Other than maybe for a what if discussion at the Pub with a round of beers going to all. So if someone knows more or needs to set me straight on that, then please do so.
Cheers!
LRA is not quite the same as starting amperage though the two can be about the same value. LRA will likely always be a higher number. Both will only be a momentary increase in demand for a very brief time. I think starting amperage is a older term defined differently.
You don't have to have a device that is built for 30 amps of draw. It just has to be built to briefly handle that amount of current. You'd be okay if you found a device rated at over the 11 amps your refrigerator continuously draws when cooling. And typically the next step up is 15 amps. Then your only concern is how much momentary draw the device can handle.
Not all or even many sold for us as untrained in electrical knowledge will have that specification. But many are built to handle expected overloads due to surges and starting of stuff. But the amount they can handle varies on what the designer or engineer thought it should be for that devices expected use.
And take the above with the understanding that I don't have the training to even state that. Other than maybe for a what if discussion at the Pub with a round of beers going to all. So if someone knows more or needs to set me straight on that, then please do so.
Cheers!