So it's going to be hard to tell wtf is going on here since a tangle of wires, but let's see.

SBIfEg9.jpg


Alright, so left side is power in. I have the two hots running to the large lug nuts on the side of the breaker. Neutral and grounds running to their bars.

Then I have the two hots and neutral coming off of the breaker to the correct spots on the outlet. Ground from bus -> outlet.

I don't really see what I could be doing wrong but it's not working. Any suggestions? How would I tell if the breaker is bad?
 
Neutral from power feed needs to go to breaker, then breaker neutral (curly) goes to neutral bus, then a neutral from bus to outlet.

Hope this helps!
While that might function, I don't believe that's quite correct. The breaker should not monitor current through the entire neutral bus bar, only the circuit neutral protected by the breaker.

Power IN Neutral to the neutral bus bar.
Breaker neutral pigtail to neutral bus bar.
Power Out (Load) neutral connects to neutral clamp connection on breaker.

It appears this is how you have it connected but I'm not sure from the photo.

Is it tripping with nothing connected to the load or only when a load is connected?

Have you checked voltages across hots and hots and neutral?
 
While that might function, I don't believe that's quite correct. The breaker should not monitor current through the entire neutral bus bar, only the circuit neutral protected by the breaker.

Power IN Neutral to the neutral bus bar.
Breaker neutral pigtail to neutral bus bar.
Power Out (Load) neutral connects to neutral clamp connection on breaker.

It appears this is how you have it connected but I'm not sure from the photo.

Yeah I realized right after submitting I was wrong. :)
 
While that might function, I don't believe that's quite correct. The breaker should not monitor current through the entire neutral bus bar, only the circuit neutral protected by the breaker.

Power IN Neutral to the neutral bus bar.
Breaker neutral pigtail to neutral bus bar.
Power Out (Load) neutral connects to neutral clamp connection on breaker.

It appears this is how you have it connected but I'm not sure from the photo.

Is it tripping with nothing connected to the load or only when a load is connected?

Oh right, I should have specified that -- not tripping, just no providing power to the outlet from it seems. I'm testing with my dryer and it wont turn on.
 
Oh right, I should have specified that -- not tripping, just no providing power to the outlet from it seems. I'm testing with my dryer and it wont turn on.

I assume you know that the breaker is in the OFF position, at least in the photo.

I would suggest a few voltage readings.
 
Hah, I tried flipping it a few times! I'll have to bust out my multimeter. Don't tell anyone but I really have no idea what I'm doing with it most of the time :drunk:
 
Hah, I tried flipping it a few times! I'll have to bust out my multimeter. Don't tell anyone but I really have no idea what I'm doing with it most of the time :drunk:
Set it for AC Voltage. Should read about 240 between hots, 120 between each hot and neutral, 120 between each hot and ground, and 0 between neutral and ground. Check input feed at the lugs, at the outputs of the breaker, and at the receptacle.
 
Set it for AC Voltage. Should read about 240 between hots, 120 between each hot and neutral, 120 between each hot and ground, and 0 between neutral and ground. Check input feed at the lugs, at the outputs of the breaker, and at the receptacle.

Thanks for the lesson!

So everything reads fine at the lugs, but I'm getting nothing on the out-terminals. I guess the breaker is bad?

Edit: and no, it's not from the breaker being set to off, lol!
 
And yes, wiring in this is terrible, I know. Putting the outlet on the top (already had the conduit hole for power-in) really mucked the flow up.
 
Thanks for the lesson!

So everything reads fine at the lugs, but I'm getting nothing on the out-terminals. I guess the breaker is bad?

Edit: and no, it's not from the breaker being set to off, lol!
If that's the case, and if the breaker is holding in the ON position without tripping, then I would guess a bad breaker.

Does anything happen when pressing the TEST button on the breaker while in the ON position?
 
If that's the case, and if the breaker is holding in the ON position without tripping, then I would guess a bad breaker.

Does anything happen when pressing the TEST button on the breaker while in the ON position?

Test does nothing.
 
Alright, tried to move some wires and get cleaner pics:

NKdz9H8.jpg


anvICqm.jpg


One thing I noticed is when running my multimeter on one power-in and one load I get 120v instead of 240v. Any idea what that's aboot?
 
Your line in neutral has to go to the breaker. The load side is a seperate neutral FROM the breaker so it can monitor for faults. They cannot be tied together on the same bar.

Your line-in neutral should be connected (wirenutted) to the pigtail on the breaker and the neutral bar (load neutral) should be tied to the neutral terminal on the breaker.
 
With breaker on, check the voltage across the line side to the load side of the breaker. Pretty rare a new breaker is bad, but can happen. Maybe a neutral is rubbed raw and touching the panel. What type and size breaker is feeding that panel? Multiple gfci' son the same circuit can cause nuisance tripping. #10 is only rated for 30 amps, hopefully the breaker feeding the panel is 30 amps or less.
 
Your line in neutral has to go to the breaker. The load side is a seperate neutral from the breaker so it can monitor for faults.

How do I do that? I couldn't figure out how to remove that pig-tail so I just ran it and the power-in to the bus.
 