CidahMastah
Well-Known Member
- Joined
- Nov 12, 2010
- Messages
- 4,201
- Reaction score
- 46
I just bought and wired up a Love TSS2 with one probe.
The over all goal is to simply control the desired temp with heat and cooling. However I use a 1875watt hair dryer as my heater. Since the wattage demands are higher for this than my college refridge guts, I would like to use the 16amp output 1 for heating and the 8 amp output 2 for cooling. However all the instructions on how to program seem to use output 1 for cooling.
If you have done this I would much appreciate your providing me with details on how to do this. I tried some of the programming instructions I read and the elements both seem to be firing:
Values set are (goal is to cool to 66F in this example w/in 1.5 degrees heat if set value = 64F w/in .1 degree):
(I bought the controller used so I listed all the values)
Seem to be the most important
SP2 = 66 (R2 = 1.5) [if temp goes above 67.5 it triggers refridge until 66F]
SP1 = 64 (R1= .1) [if temp goes below 64 w/in .1, trigger hair dryer]
A1 = 88
A3 = 40
C2 = INV
P5 = 1
RO = Dep
Other values
H5 = 0
R3 = 1.0
R4 = 99.9
R5 = 99.9
R6 = 99.9
R7 = 99.9
R8 = on 1
A0 = .1
A2 = 92.7
A4 = 99.9
A5 = 18
A6 = AHL
A7 = AHL
Co = 5
C1 = dir
C3 = oPn
C4 = oPn
P0 = F
P1 = -1 (calibration on probe)
P2 = 0
P3 = Yes
P4 = Sd1
P5 = 1
H0 = 0
H1 = No
H2 = dir
H3 = dir
H4 = 0
H5 = 0
The over all goal is to simply control the desired temp with heat and cooling. However I use a 1875watt hair dryer as my heater. Since the wattage demands are higher for this than my college refridge guts, I would like to use the 16amp output 1 for heating and the 8 amp output 2 for cooling. However all the instructions on how to program seem to use output 1 for cooling.
If you have done this I would much appreciate your providing me with details on how to do this. I tried some of the programming instructions I read and the elements both seem to be firing:
Values set are (goal is to cool to 66F in this example w/in 1.5 degrees heat if set value = 64F w/in .1 degree):
(I bought the controller used so I listed all the values)
Seem to be the most important
SP2 = 66 (R2 = 1.5) [if temp goes above 67.5 it triggers refridge until 66F]
SP1 = 64 (R1= .1) [if temp goes below 64 w/in .1, trigger hair dryer]
A1 = 88
A3 = 40
C2 = INV
P5 = 1
RO = Dep
Other values
H5 = 0
R3 = 1.0
R4 = 99.9
R5 = 99.9
R6 = 99.9
R7 = 99.9
R8 = on 1
A0 = .1
A2 = 92.7
A4 = 99.9
A5 = 18
A6 = AHL
A7 = AHL
Co = 5
C1 = dir
C3 = oPn
C4 = oPn
P0 = F
P1 = -1 (calibration on probe)
P2 = 0
P3 = Yes
P4 = Sd1
P5 = 1
H0 = 0
H1 = No
H2 = dir
H3 = dir
H4 = 0
H5 = 0