E-Brewers,

I can't remember what type of SSR I need, but I believe that to run a 240v 2500watt RIMS I need a 40AMP DC in/AC out using a SYL-2352 PID. Correct?

Thanks!

-Dogman
 

Gameface

Well-Known Member
Joined
Jul 13, 2010
Messages
2,102
Reaction score
686
Location
Salt Lake City
A 240V 25A SSR would be the bare minimum you'd need for a 5500W element. For a 2500W element you could get away with a lot less. You'll only be pulling a little over 10A. But the price difference is pretty small and 40A SSRs are all over the place and frequently used by electric home brewers, so it might be just as easy and inexpensive to go that way. Doesn't hurt anything to have the extra capacity.
 

FuzzeWuzze

I Love DIY
Joined
Jun 19, 2012
Messages
3,140
Reaction score
458
Location
Newberg
A 240V 25A SSR would be the bare minimum you'd need for a 5500W element. For a 2500W element you could get away with a lot less. You'll only be pulling a little over 10A. But the price difference is pretty small and 40A SSRs are all over the place and frequently used by electric home brewers, so it might be just as easy and inexpensive to go that way. Doesn't hurt anything to have the extra capacity.
Yup i'd just pay the extra few dollars and get the 40A, it wont output much heat because it wont be getting taxed at all.
 

thekraken

Well-Known Member
Joined
Aug 18, 2014
Messages
1,957
Reaction score
449
Location
DFW
E-Brewers,

I can't remember what type of SSR I need, but I believe that to run a 240v 2500watt RIMS I need a 40AMP DC in/AC out using a SYL-2352 PID. Correct?

Thanks!

-Dogman
Just to elaborate on what has already been said: 2500 watts / 240 volts = 10.42 amps --> you need a SSR that can handle more than 10.42 amps. A 40 amp relay will do just fine and leave room for upgrades later.

I just needed to handle 11.5 amps but went with this 50 amp relay: http://www.ebay.com/itm/TELEDYNE-SD...E-RELAY-NEW-/321711347394?hash=item4ae77d96c2 (Man, I'm linking this relay a lot today)
That said, I have a large heatsink on the thing and despite being such a small load relative to the ssr's capacity the thing still gets pretty warm. I've measured the heatsink up to 115F. So even if you get a large capacity ssr don't skimp on the thermal protection.
 
OP
MI_Dogman

MI_Dogman

Well-Known Member
Lifetime Supporter
Joined
Oct 21, 2014
Messages
248
Reaction score
25
Location
Traverse City
Awesome guys! I'm build a 50 amp panel for upgrades later down the road to a nice herms build. Right now I'm going with a two vessel MLT with 2500watt RIMS and 4500watt HLT/BK build in a utility cart. I will post pics once I really get underway with the build. Thanks for the advice Brewers!
 

kal

Well-Known Member
Joined
Nov 21, 2006
Messages
2,708
Reaction score
492
Location
Ottawa, Canada
Equally important to sizing the SSR correctly is to get a heat sink that is the correct size too. All that heat needs somewhere to go. Using a properly sized SSR but undersized heat sink can fry the SSR.

Kal
 

2bluewagons

Well-Known Member
Joined
Jan 27, 2009
Messages
356
Reaction score
27
Location
Taichung, TW / Portland, OR
Yup i'd just pay the extra few dollars and get the 40A, it wont output much heat because it wont be getting taxed at all.
Not to raise a fuss, but is this a true statement? Seems to me that the heat produced by an SSR would be related to the current flowing through the relay, not the amperage rating of the relay.
 

doug293cz

BIABer, Beer Math Nerd, ePanel Designer, Pilot
Staff member
Mod
Lifetime Supporter
Joined
May 14, 2014
Messages
11,922
Reaction score
8,293
Location
Renton
Not to raise a fuss, but is this a true statement? Seems to me that the heat produced by an SSR would be related to the current flowing through the relay, not the amperage rating of the relay.
The heat dissipated by an SSR is equal to the current flowing thru it times the forward voltage drop within the SSR. A higher current rated SSR is usually going to have a slightly smaller forward voltage drop for the same current vs. a lower current rated SSR. The internal heat spreader and bonding may also be slightly better in order to be able to better dissipate the heat at high currents. Lastly, the junction cross section area may be slightly larger in order to keep the current density down at higher currents.