Anyone want to offer pro/con on connecting the SSR either before or after the contactor in the element wiring loop?
 

Riot

Well-Known Member
Joined
Jul 25, 2013
Messages
716
Reaction score
99
Connect it after the contractor, the SSR isn't entirely reliable to turn things off. If you switch the contractor you know the element is completely off
 

cegan09

Supporting Member
HBT Supporter
Joined
Dec 16, 2015
Messages
930
Reaction score
353
I have a single contactor that the main power comes into before it goes to anything else. Guaranteed that I can kill power to everything that way. For the elements I have a traditional relay first that is controlled by a switch, then I go to the SSR, then the outlet for the element. So I know I can kill just the element if the SSR fails on.
 

WrQth

Well-Known Member
Joined
Jul 28, 2015
Messages
213
Reaction score
68
Location
Semi-Coastal
The SSR should be after the contactor, in such a circuit the contactor passes through the power which is to be switched by the SSR and ultimately delivered to the element.

Putting the SSR before the contactor would cause the contact to be cycled quickly greatly reducing the lifespan of the contactor.
 
OP
N

NivBrew

Active Member
Joined
Aug 28, 2015
Messages
32
Reaction score
9
Not controlling the contactor with the SSR....just passing the 220v through it. Shouldn't diminish the life span of the contactor as it is not cycling.
 

golfindia

Well-Known Member
Joined
Dec 6, 2015
Messages
527
Reaction score
155
I put contactors as far upstream as possible, just seems like better engineering to minimize the amount of energized stuff when the switch is off.
 

hio3791

Well-Known Member
Joined
Mar 23, 2011
Messages
535
Reaction score
153
Location
Pittsburgh
In this particular case, I don't think it matters since current is pulled not pushed. Since there's no load, it doesn't matter where the circuit is broken.

I'm not an electrician!
 

hio3791

Well-Known Member
Joined
Mar 23, 2011
Messages
535
Reaction score
153
Location
Pittsburgh
Remember the latter before you restate the former! :mug:

Anyway, put the contactor before ("upstream") the SSR.
That's fair. Can you help me understand the logic? I built my controller almost 4 years ago, following PJ's diagrams and Kal's site. They put the contactor downstream from the SSR.

Personally, I like the design since the contactor is the last line of defense before the kettle. Has the consensus on this changed?

Thank you.
 

golfindia

Well-Known Member
Joined
Dec 6, 2015
Messages
527
Reaction score
155
Personally, I like the design since the contactor is the last line of defense before the kettle. Has the consensus on this changed?
Bad engineering principles cannot be morphed into good engineering principles by consensus.
 
Joined
Dec 19, 2014
Messages
5,408
Reaction score
1,571
Location
West Palm Beach
Well, like you said its part of a whole circuit, so if any part breaks, current won't flow. Honestly doing this way is not breaking any laws of the universe or anything. It is just that SSRs tend to fail, and fail closed. So if this happens, you have it on, applying power and generating heat when it isn't called for. Of course it wouldn't get past the contactor (aka relay) to the downstream circuitry, but its still a live part of your circuit. If the SSR is after the contactor, and it gets stuck on, it will be powering your element or pump or whatever and you will be aware as your contactor is closed.
 

hio3791

Well-Known Member
Joined
Mar 23, 2011
Messages
535
Reaction score
153
Location
Pittsburgh
Well, like you said its part of a whole circuit, so if any part breaks, current won't flow. Honestly doing this way is not breaking any laws of the universe or anything. It is just that SSRs tend to fail, and fail closed. So if this happens, you have it on, applying power and generating heat when it isn't called for. Of course it wouldn't get past the contactor (aka relay) to the downstream circuitry, but its still a live part of your circuit. If the SSR is after the contactor, and it gets stuck on, it will be powering your element or pump or whatever and you will be aware as your contactor is closed.
Thank you for the explanation.

So we could agree that either approach is safe. Placing the SSR downstream from the contactor may increase its life. That gain, I would think, is negligible compared to the characteristics of the entire system and its effects on the life of the SSR.

Not trying to argue your point. Rather, I want to emphasize that there's no significant advantage to either approach necessitating me, or anyone who has the contactor downstream, to open their controller and rewire it.
 

srice

Well-Known Member
Joined
Oct 21, 2012
Messages
262
Reaction score
58
Thank you for the explanation.

Placing the SSR downstream from the contactor may increase its life.
Not sure where that came from.

If you want to muddy it up a little more, when current is actually "flowing", it is Alternating directions every 8.3 ms. So technically the contactor alternates from being upstream and downstream from the SSR.

Back to real world construction, as an electrical engineer, I would put the contactor as close to the incoming power as possible. I would want the power to the entire control panel to be cut when the contactor opens.
 
Joined
Dec 19, 2014
Messages
5,408
Reaction score
1,571
Location
West Palm Beach
Thank you for the explanation.

So we could agree that either approach is safe. Placing the SSR downstream from the contactor may increase its life. That gain, I would think, is negligible compared to the characteristics of the entire system and its effects on the life of the SSR.

Not trying to argue your point. Rather, I want to emphasize that there's no significant advantage to either approach necessitating me, or anyone who has the contactor downstream, to open their controller and rewire it.

Correct. No real biggie worth any time thinking about it.
 

hio3791

Well-Known Member
Joined
Mar 23, 2011
Messages
535
Reaction score
153
Location
Pittsburgh
Not sure where that came from.
It came from nowhere.

It was a deduction that if the SSR is unnecessarily put under stress by placing it before the contactor then putting it after may effectively extend its life.
 

doug293cz

BIABer, Beer Math Nerd, ePanel Designer, Pilot
Staff member
Mod
Lifetime Supporter
Joined
May 14, 2014
Messages
11,236
Reaction score
7,370
Location
Renton
With the contactor off, there is no voltage (and thus no current) downstream of the contactor. At the element outlet, there will be no voltage when the contactor is off whether the contactor is upstream or downstream of the SSR. Either way you get a positive disconnect before the element outlet.

My preference is the contactor upstream of the SSR for the reason stated earlier: fewer things with voltage on them inside the control panel the further upstream the contactor. Translates to fewer places where things could go wrong under fault conditions. May not be significant in practice, but it doesn't cost anything to put the contactor upstream, so why not do it? Can't hurt, and it might actually help under some conditions.

Brew on :mug:
 