I ordered an electric system which I expected to require a 4-wire outlet. When it arrived, it was actually configured for a 240V 3-wire outlet plus a separate 120V supply. (Grr.)

I can easily supply the control panel with the 240V it needs by tapping the 2 hots and the ground on my 4-wire receptacle, and simply disregarding the unneeded neutral.

Question is, is that kosher? It seems safe but I'm not an electrician. For all I know the neutral may be required by the GFCI breaker, and this would be a bad idea.

Thanks for the help!
 
This is Kosher. The only time you need the neutral is for a 120V use, or inside the breaker panel, where the neutral wire that comes off the GFCI needs to the neutral bus.
 
What isn't kosher is using the ground as a current carrying conductor; don't do that.

Your plan is fine but I would use a 4-wire plug as to not require a separate 120v supply.
 
The panel is already wired for separate 120V and 240V supplies. The manufacturer said that this is required for UL listing. Non-UL listed products from the same company use one 4-wire power connection for everything.

I have a wiring diagram showing where to connect 1 ground and 2 hot lines inside the panel. That's how they build them--they just forgot to actually attach my 240V power cable when they shipped it. You're saying that this isn't how it should be done?
 
If the ground attaches to the chassis then it is fine. If it is used in place of a neutral then it is not fine.

A single UL test session can cost upwards to $25K, I am surprised that they would pay this much and still offer a non-UL assembly.
 
In this case the ground is definitely connected to the chassis. Thanks!

Beats me about the UL strategy. The vendor offers home and commercial versions. I chose an upgrade for my home model which used some of the commercial parts, and the UL rating came along with it.
 
If the ground attaches to the chassis then it is fine. If it is used in place of a neutral then it is not fine.

A single UL test session can cost upwards to $25K, I am surprised that they would pay this much and still offer a non-UL assembly.

It sounds like they sell a unit with a single power feed with a hot, hot, neutral, earth plug that is non-UL, as well as the UL separate 240 / 120 plug version.
What is weird is their claim that they can not get UL if they use a single plug for both 240 and 120. I don't know if that is true but it doesn't seem correct to me? Anyone know either way?
 
That sounds a bit suspect - after all most factories only have a single feed coming into their buildings so it is going to be on the same feeder circuit from some point. And motor / element is not the same a 240 / 120.
I can understand separating the circuit protection for inductive/resistive loads, but not the feed into the box!
 