PID SSR stuck

HomeBrewTalk.com - Beer, Wine, Mead, & Cider Brewing Discussion Community.

Help Support Homebrew Talk:

aeviaanah

Well-Known Member
Joined
Jul 1, 2012
Messages
1,549
Reaction score
171
I have a PID controlling cleaner temp in keg washer. SSR is showing off but is stuck open causing overheat issues. Even with the installed heat sink, my issue may be caused by excessive heat or poor SSR. I bought a 5 pack on Amazon and most of them show the same symptoms. Heatsink and SSR are both internal to the panel but I'm seeing the issue even with the panel door left open.

I either need to swap out for a PID with contactor/relay output or find a better SSR. Thoughts? Perhaps oversizing the SSR would help?
 

Jayjay1976

Bubblegazer
Joined
Nov 26, 2016
Messages
3,569
Reaction score
2,877
Location
Chicago
SSR's typically fail in the closed position. I'd recommend buying better quality from a reputable source. Good quality doesn't come so cheap.

Also, use adequate heatsinks and fans to keep them cool.
 
Joined
Mar 6, 2011
Messages
781
Reaction score
142
Location
Denver, PA
Even good ones can fail. But, get a good one and have a spare. I have a indicator light for the element firing on my rims controller. This is how I found out mine got stuck. This was after 7 years of use, not bad.
 

Jayjay1976

Bubblegazer
Joined
Nov 26, 2016
Messages
3,569
Reaction score
2,877
Location
Chicago
Even good ones can fail. But, get a good one and have a spare. I have a indicator light for the element firing on my rims controller. This is how I found out mine got stuck. This was after 7 years of use, not bad.
Damn, an indicator light is a great idea. Is it simply wired in parallel with the element?
 

doug293cz

BIABer, Beer Math Nerd, ePanel Designer, Pilot
Staff member
Mod
Lifetime Supporter
Joined
May 14, 2014
Messages
11,171
Reaction score
7,311
Location
Renton
Damn, an indicator light is a great idea. Is it simply wired in parallel with the element?
Yes, the element firing light is wired in parallel with the element. All my designs include one.

There is a quirk with the element firing light, in that it will light up if the element is disconnected, even when the SSR is off. This is an artifact caused by the "off" leakage current of the SSR.

Brew on :mug:
 

doug293cz

BIABer, Beer Math Nerd, ePanel Designer, Pilot
Staff member
Mod
Lifetime Supporter
Joined
May 14, 2014
Messages
11,171
Reaction score
7,311
Location
Renton
Even good ones can fail. But, get a good one and have a spare. I have a indicator light for the element firing on my rims controller. This is how I found out mine got stuck. This was after 7 years of use, not bad.
I highly recommend an "element firing light" in parallel with the element for exactly this reason.

Brew on :mug:
 
OP
aeviaanah

aeviaanah

Well-Known Member
Joined
Jul 1, 2012
Messages
1,549
Reaction score
171
I dont need the accuracy a PID/SSR provide but panel is already cut for a standard PID. Do you know of a thermostat with same form factor as a typical PID but built to suit contactor (without the rapid cycles SSRs use)?
 

Jayjay1976

Bubblegazer
Joined
Nov 26, 2016
Messages
3,569
Reaction score
2,877
Location
Chicago
I dont need the accuracy a PID/SSR provide but panel is already cut for a standard PID. Do you know of a thermostat with same form factor as a typical PID but built to suit contactor (without the rapid cycles SSRs use)?
An inkbird PID is so cheap, why not just use one of those?
 
OP
aeviaanah

aeviaanah

Well-Known Member
Joined
Jul 1, 2012
Messages
1,549
Reaction score
171
An inkbird PID is so cheap, why not just use one of those?
I'm attempting to overcome cheap SSR and or overheat issues since it's mounted inside a small panel. I'd use a cheap PID if it can be quieted for use with contactor
 

doug293cz

BIABer, Beer Math Nerd, ePanel Designer, Pilot
Staff member
Mod
Lifetime Supporter
Joined
May 14, 2014
Messages
11,171
Reaction score
7,311
Location
Renton
I'm attempting to overcome cheap SSR and or overheat issues since it's mounted inside a small panel. I'd use a cheap PID if it can be quieted for use with contactor
Mounting a heat producing component inside a small enclosure with no fan is a recipe for overheating. SSR's can latch up (get stuck on) when they overheat. I'd look at putting the heatsink out in the open air, or adding a fan in the enclosure, along with air inlets and outlets (fan should be mounted to either inlet or outlet.)

Brew on :mug:
 

Beer666

Well-Known Member
Joined
Apr 10, 2018
Messages
388
Reaction score
377
I highly recommend an "element firing light" in parallel with the element for exactly this reason.

Brew on :mug:
At the risk of sounding like a moron is there a wiring diagram anywhere and what sort of light would i need? Thanks
 

doug293cz

BIABer, Beer Math Nerd, ePanel Designer, Pilot
Staff member
Mod
Lifetime Supporter
Joined
May 14, 2014
Messages
11,171
Reaction score
7,311
Location
Renton
At the risk of sounding like a moron is there a wiring diagram anywhere and what sort of light would i need? Thanks
Here's a simple schematic that shows an "element firing lamp." Here is a link to a suitable lamp. If you are running the element at 120V you want a 120V LED, and likewise 240V for 240V. You can substitute any equivalent lamp - you don't have to use Auber as a source. Lamps just have to be rated for the element operating voltage, and AC current.

DSPR300 1-Pump 1-Element 240V rev-2.PNG


Brew on :mug:
 
OP
aeviaanah

aeviaanah

Well-Known Member
Joined
Jul 1, 2012
Messages
1,549
Reaction score
171
Mounting a heat producing component inside a small enclosure with no fan is a recipe for overheating. SSR's can latch up (get stuck on) when they overheat. I'd look at putting the heatsink out in the open air, or adding a fan in the enclosure, along with air inlets and outlets (fan should be mounted to either inlet or outlet.)

Brew on :mug:
It's getting stuck open in an open panel when it's 50deg outside. Not much usage either
 