Hi,

I have a PID controller which has it's output configured as a relay. It is fed by 220vac. If I want to use it to control a solenoid valve (24vdc) can I just purchase a AC to DC converter and hook up the relay output from the PID controller to the AC input on the converter and the DC output to the solenoid valve?

Thanks,
 
Joined
Nov 22, 2007
Messages
76
Reaction score
28
Location
Portland, OR
Your plan seems perfectly reasonable, as long as the "converter" (aka AC adaptor) is happy with 240VAC input, puts out 24VDC, and can provide enough current for the solenoid's needs. My quick check did not reveal what those needs are...
1604068420168.png
 

Konadog

Bird Call Brewing
HBT Supporter
Joined
Oct 14, 2013
Messages
854
Reaction score
341
Location
Long Beach, CA
You say that the 220v feeds a relay, are you sure the output of the relay is 220v, or is it another voltage out, or even a dry contact out?
 

gavinr

Active Member
Joined
Aug 29, 2017
Messages
37
Reaction score
20
Location
los angeles
A relay output is a dry-contact output. On PIDs they are typically single pole NO (normally open) contacts. Think of it as a switch that is triggered by the PID. You need to wire this switch in series with the load, i.e. your solenoid. Wire one OUTPUT terminal of a 24V DC transformer directly to the valve, and the other one to a PID relay contact. The third wire goes from the open PID relay contact to the open valve contact. AC is NOT switched at the relay. It goes directly to the transformer input.
 
OP
B

birzzz

Well-Known Member
Joined
Mar 26, 2017
Messages
78
Reaction score
22
OK thank you guys,

So if I understand well, my first assumption was good, albeit my converter can provide enough current.
 