Hello I was wondering if anyone could help me out with my johnson controls a419. The problem is that when I plug it in it flashes Asd and the prob temp, everything seems to be working fine I can change the settings and pretty much do everything but it just wont turn the frezzer on it just flashes Asd anyone know how to fix this?
 

Jdk261

Well-Known Member
Joined
Apr 2, 2011
Messages
136
Reaction score
7
Location
Dallastown
Asd = anti short cycle delay. Maybe it wants you to set the delay before it considers your setup "complete". In other words, try setting it and see if it starts working.
 

Aschecte

Brewtus Maximus
Lifetime Supporter
Joined
Feb 20, 2011
Messages
1,682
Reaction score
65
Location
Florida
Yeah it is a delay so the compressor does not short cycle. Here is your fix.
#1 press menu
#2 scroll down until you see asd then press menu again.
#3 set it to like 3

What this will do is upon start up or after the unit shut off on temp it needs to wait at least 3 minute before it kicks on again.

Also maybe before doing this just press menu like 4 times to cycle the options that maybe all you need. Good luck.
 

day_trippr

Moderna Or Bust! :D
Joined
May 31, 2011
Messages
36,683
Reaction score
19,337
Location
Stow, MA
According to the Johnson manual: "If the temperature reaches the cut-in value during the delay period, the display flashes between the sensed temperature and ASd, indicating that the next On-cycle is being delayed. After the set delay time has elapsed, the A419 control returns to normal operation, restarts the equipment (if cut-in has been reached), ASd stops flashing, and the LCD reverts to the normal operating display."

So it seems likely the ASD is already set to some non-zero value, and the ASD flashing during initial power-up of the Johnson would be totally normal...

Cheers!
 

BobTheFourth

Well-Known Member
Joined
Jul 7, 2012
Messages
62
Reaction score
3
Location
Lynchburg
And to make it clear why it does this on startup, its to prevent short-cycling during a transient power outage.
 
OP
B

BeerGuy1000

Well-Known Member
Joined
Dec 6, 2010
Messages
51
Reaction score
4
Location
Landstuhl
Success it works, I just plugged it in let it set turned the Asd down to 1 and waited few min went by and boom kicked on works like a champ now thanks guys I thought I was going to have to buy another controller
 

inter01

Member
Joined
May 17, 2013
Messages
18
Reaction score
1
I know this has been touched upon quite a bit, but just wanted to be sure. I have a refrigerator/freezer combo in the garage. It is summer time and I am trying to determine if its better to have it set to Cooling Cut In or Cooling Cut Out. I will be using it to control a consistent fermenting temperature. Right now I have the SP at 69 with a differential of 1. It is also set to Cut Out. Is this the best approach or should I set to Cut in? Thanks!
 

PDX_T

Well-Known Member
Joined
Mar 9, 2013
Messages
221
Reaction score
18
I have mine set to cut out for cooling. it probably doesn't matter as long as you have your dif set where you want it, and you aren't experiencing huge temp swings or overshoots.
 