ITC-308 wifi is always heating or cooling

HomeBrewTalk.com - Beer, Wine, Mead, & Cider Brewing Discussion Community.

Help Support Homebrew Talk:

m1k3

Well-Known Member
Joined
Jun 27, 2011
Messages
1,066
Reaction score
219
Location
El Dorado Hills
I just got a new ITC-308 wifi and it's always heating or cooling.

I own the old Inkbird wifi and dual stage units so I understand how to set it.

The issue is that it does not respect any Difference Value settings.
(and it does not respect Refridgeration Delay)

Is it broken, need updated? Did anyone else have this issue. Thanks!
 
Last edited:
OP
m1k3

m1k3

Well-Known Member
Joined
Jun 27, 2011
Messages
1,066
Reaction score
219
Location
El Dorado Hills
I guess mine is busted. Thanks for testing! Mine does not do that... it's heat or cool all the time.
 
OP
m1k3

m1k3

Well-Known Member
Joined
Jun 27, 2011
Messages
1,066
Reaction score
219
Location
El Dorado Hills
I used my new ITC-308 wifi to ferment a beer.
Here are my issues with it:


Let's say the temp was 69.5F... If I change the temp to 69F, the cooling turns on. If I change the temp to 70F the heating turns on.
It should respect the Difference setting and not turn on. (see video)

The chest freezer and Reptile heater seem to be cycling more than with other Temp controllers that I own.
(usual fermentartion... two fermenters with thermowells... 2F Difference Setting)

Unplugging the heat or cooling and running it single stage helps reduce cycling.
 

GoeHaarden

Well-Known Member
Joined
Feb 1, 2017
Messages
1,015
Reaction score
513
Do you let it settle first?

I've noticed on mine that if I change the target then it will heat/cool if not at the exact target. However, once it hits the target initially then it will respect the difference setting. It doesn't stop the cycle until target is achieved exactly.

Let it ride out a few cycles and see if it starts to respect the difference setting.
 
Joined
Sep 25, 2014
Messages
932
Reaction score
696
Hi, everyone, we sincerely apologize for the inconvenience. We have already reported to our engineering team, we will try our best to solve the problem. We will keep you posted. Thanks for your patience.
 
Joined
Sep 25, 2014
Messages
932
Reaction score
696
Hi, we just check with our engineering team. And here is the details:

After setting the parameters, save or exit or power on for the first time, it enters heating or cooling according to the TS value, not based on the difference value. Then when the heating or cooling is turned off, the following control is controlled according to the TS and the difference. Here is the user manual for your reference.

upload_2019-6-26_14-43-38.png
 

neal0329

New Member
Joined
Mar 2, 2020
Messages
1
Reaction score
0
Hi, we just check with our engineering team. And here is the details:

After setting the parameters, save or exit or power on for the first time, it enters heating or cooling according to the TS value, not based on the difference value. Then when the heating or cooling is turned off, the following control is controlled according to the TS and the difference. Here is the user manual for your reference.

View attachment 632771

I reset mine today as the set temperature function on the app was not working. It was at 64.9 degrees and I set it to 65. It ran heat til it hit 65 and shut off. I then turned the heat back down to 64 and it started cooling. My heat differential is 2 and cooling is 8 as I do not intend to use this in the winter. It is still running the cooling.
 

MrEggSandwich

Well-Known Member
Joined
Feb 26, 2012
Messages
298
Reaction score
20
Location
Hunterdon County, NJ
Having same issue here. Fired mine up yesterday for first time in a while, it's always in heating or cooling mode. I have mine heat diff @ 2, and my cooling at 10. Temp is set at 64. Heat should only go on at 61, and cooling at 75. Otherwise, "off".

Last night, it was in heating mode for two hours, yet the temp never moved. Good thing I switched it out for another controller, as the temp was higher than indicated on Inkbird.

Its also making a hissing noise (yes, really).
 
Joined
Sep 25, 2014
Messages
932
Reaction score
696
Having same issue here. Fired mine up yesterday for first time in a while, it's always in heating or cooling mode. I have mine heat diff @ 2, and my cooling at 10. Temp is set at 64. Heat should only go on at 61, and cooling at 75. Otherwise, "off".

Last night, it was in heating mode for two hours, yet the temp never moved. Good thing I switched it out for another controller, as the temp was higher than indicated on Inkbird.

Its also making a hissing noise (yes, really).
Hey there! You should be get it wrong.. According to your settings, heat will go on at 62, will be off at 64. cooling will go on at 74, will be off at 64. As for the reading problem, please put the probe to another place and see if the reading is accurate.
 

MrEggSandwich

Well-Known Member
Joined
Feb 26, 2012
Messages
298
Reaction score
20
Location
Hunterdon County, NJ
Hey there! You should be get it wrong.. According to your settings, heat will go on at 62, will be off at 64. cooling will go on at 74, will be off at 64. As for the reading problem, please put the probe to another place and see if the reading is accurate.
Its still always either in heating or cooling mode. What about the hissing? I don’t have this issue with any other controllers I own.

I’ve unplugged it.
 