So I'm purchasing all parts needed to build P-Js 60 amp 4 5500 watt element HERMS controller.... and the contactors are listed as 240 volt - 30 amp 120 volt coils. So my question is which exact contactor is this? they are all listed as either 30 amp 240 volt or 30 amp 120 volt coils... nothing listed as 240 volt - 30 amp 120 volt coil. thanks in advance!!!! :rockin::rockin::rockin:
 
Ok so now my question becomes it this calls for the 120v coil will it run my 5500 watt HE at the lower 120 strength or will I still get the full 5500 watts?

Thanks man!
 
Coil voltage has no relationship to the capacity of the contactor.
The only relevant specification is the ampacity of the contacts, which in your case is 30 amps.
Your element will be operate at full capacity just fine.
 