Parts needed?

Discussion in 'Electric Brewing' started by shtank, Dec 28, 2012.

 

  1. #1
    shtank

    Well-Known Member

    Posted Dec 28, 2012
    Hey guys, I'm putting together a E-HLT and I need help choosing the right size (water heater) element and SSR. I have a 20A 250v outlet on a 20A breaker and nothing else is on the line. I have allready purchased a mypid ta4 controler. Here is a pic of the setup I will be using. Any input is appreciated.

    Thanks
    Chris

    [​IMG]
     
  2. #2
    slakwhere

    Well-Known Member

    Posted Dec 29, 2012
    Watts / Volts = Amps

    3500W / 240 = 14.6 amps
    4500W / 240 = 18.8 amps
    5500W / 240 = 22.9 amps

    assuming you are going to put some sort of selector switch to select only 1 element at a time? 4500 ultra low watt density (ULWD) is your best bet. you can use a contactor to do that but i doubt you'll be able to find a DPDT switch hardcore enough to handle 20 amps of 240v.

    i assume that SSR you list is a 25amp based on the part #? if you can, get a higher rated SSR, it'll get less hot as it isn't as close to its limit.
     
  3. #3
    shtank

    Well-Known Member

    Posted Dec 29, 2012
    I was not planning on using a selector switch... I was just hoping by using two elements it would use less amps.

    So basically I need something under 80% of 20Amps. It does not matter how many elements.

    Will a single 3500W / 240 = 14.6 amps element heat up and maintain my HLT to 175 degrees?

    And is the bigger the SSR the better? say 40A?
     
  4. #4
    shtank

    Well-Known Member

    Posted Dec 29, 2012
    Sorry I suck at electrical work, and I have read a weeks worth of sticky's on this lovely forum about E-Brewing and I still need help. :smack:
     
  5. #5
    slakwhere

    Well-Known Member

    Posted Dec 29, 2012
    you want 1 3500 or 4500 element. remove the second one from the diagram. the 80% rule doesn't apply to you. that's NEC code for circuits at install when other devices may be added to the circuit later.

    a 4500W element will do a great job in an electric HLT up to about 15 or 20 gallons.

    a 40 amp ssr will stay cooler and last longer than a 20 amp ssr switching a 20 amp circuit.

    now, all that being said... if you don't really understand what i posted originally, maybe building your own electric circuit isn't a good idea. water + electric = death. i see no mention of your GFCI protection, no ground anywhere in your diagram. both of those are HUGE issues. proceed with caution.
     
  6. #6
    shtank

    Well-Known Member

    Posted Dec 29, 2012
    Thanks slakwhere. I was going to look for a GFCI that is built in the power cord or is it better to have a GFCI outlet?
     
  7. #7
    shtank

    Well-Known Member

    Posted Dec 29, 2012
    Last edited by a moderator: Oct 23, 2018
  8. #8
    slakwhere

    Well-Known Member

    Posted Dec 29, 2012
    you definitely need a contactor to switch that big of a 240v load. that contactor requires a 24v transformer to trigger.

    so you'd go 120v -> transformer -> switch -> contactor coil

    240v -> contactor -> SSR in -> SSR out -> element.

    you still don't have any grounds listed anywhere in your diagram ;)
     
  9. #9
    shtank

    Well-Known Member

    Posted Dec 30, 2012
    Can I ground the control box with a post and ground everything to that?
     
  10. #10
    jeffmeh

    Well-Known Member

    Posted Dec 30, 2012
    Why a 24V coil for the contactor as opposed to a 120V or 240V coil? Do you have a need for a transformer in your control panel?

    The switch listed on ebay does not list the voltage (or I missed it).
     
  11. #11
    shtank

    Well-Known Member

    Posted Dec 31, 2012
    I though it was.
    So basically I just need 240v 40A contactor for that switch?
     
  12. #12
    slakwhere

    Well-Known Member

    Posted Dec 31, 2012
    i assumed he was using them since they are usually cheaper than the 240v coil variety. but i guess i should have said something.

    if possible you for sure want a 120v coil or a 240v coil for the contactor. and the contacts should be rated for 240v 20a or higher. for a few bucks more, i'd raise the rating of the contacts.
     
  13. #13
    shtank

    Well-Known Member

    Posted Jan 1, 2013
    Ok so my biggest hang up is using 240v vs 120v Every thing I read seems to talk about 120v if I copy Kol's wiring, Will I need a transformer for the indicator light? or should I just not use a light?

    [​IMG]

    Will this same setup work with my 240v 20Amp service?

    I can use 120v if you think it would be easier.

    Thanks again for all the help I am learning as I go and promise not to plug this thing in to the wall until further review.
     
  14. #14
    slakwhere

    Well-Known Member

    Posted Jan 1, 2013
    120v uses 1 hot, 1 neutral and 1 ground (which you are STILL ignoring).

    240v uses 2 hot, 1 neutral and 1 ground. the 2 hot lines are basically alternating phase 120v. take either hot leg, a neutral and a ground and you get 120v. take 2 hot, a neutral and you get 240v.

    this diagram will not work for 240v. you do not understand how 240v works. you're missing 2 inputs to the plug, there's no ground. i have no idea why that 50a shunt is there. there's no heating element in the diagram, so this is a really elaborate switch that turns on a light bulb.

    please, for the love of pete, find a buddy who has an electronics background to help you locally. you're missing a LOT of stuff. you're going to burn your house down, electrocute yourself or blow up a lot of gear. most probably all 3.
     
  15. #15
    jeffmeh

    Well-Known Member

    Posted Jan 2, 2013
    Actually, 240v does not have a neutral, as 2 hots will do, with a ground for safety. I absolutely agree with your last point though. The OP really should not be undertaking this without a much better understanding of the workings.

    OP, if you keep studying Kal's site, and you get to the point where you really understand how it works and why it is wired the way it is, then consider undertaking the project. Otherwise, get some help (and it's never a bad idea to get a second pair of eyes, in any case).

    Lastly, the picture you included is one of Kal's intermediate wiring steps. E.g., it does not show the seocnd hot leg, as at that point in the instructions he had yet to connect it.
     
  16. #16
    slakwhere

    Well-Known Member

    Posted Jan 2, 2013
    it doesn't HAVE to have a neutral (240v heating elements don't have a neutral, just 2 hots) ... but it's in your box, it needs to be accounted for.

    [​IMG]
     