Melted Heating Element

Discussion in 'Electric Brewing' started by EdK, Mar 6, 2016.

 

  1. #1
    EdK

    Well-Known Member

    Posted Mar 6, 2016
    So brew day comes and my RIMS heating element fails. I turn to direct fire my MT instead but continue to use the pump and monitor temp via the probe of the RIMS tube (as well as for a whirlpool after the boil). That was a couple weeks ago and today I set out to open up the tube and and replace if needed.

    What I find has me quite concerned. I pull the element out and it has basically melted and it snapped into pieces easily (see image). I do recall that the switch was flipped before any recirculating was even happening - I'm not sure how long it ran dry but as soon as I saw, I flipped it off. This is likely when it happened.

    My first thought is if it is possible that this thing could have leached any toxic metals into the brew. Has anyone had this happen? I thought I read they are made of copper and covered in magnesium oxide and nickle or some such.

    [​IMG]
     
    IslandLizard likes this.
  2. #2
    BrunDog

    Sponsor  

    Posted Mar 7, 2016
    What's wrong? I don't see anything!?! :drunk::drunk::drunk:

    Holy hats that thing's smoked!!

    Regarding your beer, its probably alright, though it might have a musty/smoky/acridish taste.
     
  3. #3
    Stillraining

    Well-Known Member

    Posted Mar 7, 2016
    All I can think of is how lucky you are your not looking similarly..:eek:
     
    Hello and AkBrew907 like this.
  4. #4
    cod3ck

    Well-Known Member

    Posted Mar 7, 2016
    Shouldn't a breaker have flipped somewhere along the melting process?
     
  5. #5
    dyqik

    Well-Known Member

    Posted Mar 7, 2016
    Probably not. The resistance of the element would likely have gone up as it heated up and burnt out, so the current draw would have dropped. Breakers only respond to overcurrent situations.
     
  6. #6
    BrunDog

    Sponsor  

    Posted Mar 7, 2016
    I wonder where it fell apart. Did cold liquid hit it after it was heated?
     
  7. #7
    EdK

    Well-Known Member

    Posted Mar 7, 2016
    I suppose? Not cold water but mash temp when I finally started the recirc of the mash and of course the rest of the brew day, including whirlpooling after boil and finally a decent amount of time recirculating with hot water/PBW. Then it's been in the unheated shed for 2 weeks where temps dropped below freezing so whatever was exposed and may have still been wet had that stress put on it as well.

    What's inside these elements anyway? It's very brittle and breaks apart easily.

    Full disclosure, though I've used the RIMS box for many a brew day it was always my brew partner that was the techy equipment guy. So I know how to run the box (and the flipped switch was very much an accident to run it dry), but I didn't do the wiring myself nor did I procure the element. Unfortunately, he isn't available to brew so much anymore so I need to get more versed in this stuff - not a bad thing at all though.

    Now that I'm looking at it, it's a 120v, 2000 Watt element and it's U-shaped so high density, right? After reading through the RIMS for dummies thread, it sounds like a low or ultra low density element would be a safer route.
     
  8. #8
    ChocolateMaltyBalls

    Well-Known Member

    Posted Mar 7, 2016
    What was the watt density?

    When it comes to terrible things that could happen during brew day that's not too bad, I'm sure your GFI would have saved you from current leak. At least your RIMS didn't turn into a pipe bomb.
     
  9. #9
    EdK

    Well-Known Member

    Posted Mar 7, 2016
    Yes, indeed. See above for explanation (I edited while you were posting), I believe the it was HD wattage.

    Thank god for no pipe bomb.

    So to move away from HD, I could go with one of these lower wattage elements and it should still be able to perform okay, right?

    120-1500-LD
    120-1500-ELD

    I wouldn't have to do anything different as far as wiring goes inside the box?
     
  10. #10
    dyqik

    Well-Known Member

    Posted Mar 7, 2016
    Don't go with either of those elements - they aren't all stainless (bases will likely rust), and they aren't really LWD (I have the second one, from before the all stainless ones became available, and I really need to take my RIMS tube apart to replace it). You're better off going with an all stainless 5500W 240V element run at 120V (for 1375W at ULWD) if it will fit in your tube, or a LWD 1500W 120V all stainless element if it won't fit.

    Brew Hardware ULWD 5500W 240V element for 18" RIMS tube (might just fit in a 12" RIMS tube with your Triclover adapter in the photo - I thinks it's 12.75" long)
    Brew Hardware Short 1500W LWD for 12" RIMS tube.
     
    EdK likes this.
  11. #11
    EdK

    Well-Known Member

    Posted Mar 7, 2016
    Thank you! Yes, stainless would make more sense.

    I don't have the unit (its of the RIMS in a toolbox variety) in front of me, but I do have a ruler and I'm thinking it's probably the 18 inch tube. That said, is the idea of using the 240v element because it's longer and will have more contact with the wort in the tube?
     
  12. #12
    EdK

    Well-Known Member

    Posted Mar 7, 2016
    Also, the wiring to the element never seemed to be enclosed in a safe manner in my opinion. My friend simply wrapped the wiring in a lot of electrical tape (which in the image had already been removed). I think I would like to grab a plastic junction box to make a better cover.

    Is there any special way the two should be mated - can I simply cut a hole, place the tri clover adapter on the outside and thread the element from the inside of the box?
     
  13. #13
    dyqik

    Well-Known Member

    Posted Mar 7, 2016
    Sort of - running the long 240V element on 120V means it has 1/4 of the power it would have at 240V, so you've got the power spread out over a large area. More contact with the wort probably also means that the element runs cooler and closer in temperature to the wort. The power density is low enough that you can even accidentally run the 240V elements on 120V dry and they won't burn out (reportedly you can also do this carefully with the 240V 5500W ripple elements on 240V to burn off scorched wort).

    A plastic or metal junction box is one option (have a look at The Electric Brewery for one way to do that - you'll replace the kettle and locknut with the Triclover adapter.

    Another is a pre-made element adapter - either the Brew Hardware Hot Pod or one of the other ones that are out there. I have one of these on my RIMS tube.

    A third that I've seen is using a CPVC reducer JB-welded over the element connections. This seems a bit dodgy as it doesn't give an easy option to connect a ground to the element.
     
    EdK likes this.
  14. #14
    EdK

    Well-Known Member

    Posted Mar 7, 2016
    That hot pod is a nice affordable option. So basically I would use my tri clover adapter in place of the lock nut as seen in this install - https://youtu.be/5QjkXWE1QI8?t=5m19s

    And I'd be grounding inside the pod and no longer on the nut itself.
     
  15. #15
    IslandLizard

    Progressive Brewing Staff Member  

    Posted Mar 7, 2016
    The compromised element's "heating" wires, carrying 240V, were exposed to wort or water. That should have kicked in the GFCI! That's what those are for.

    Maybe the OP isn't using one?
     
  16. #16
    EdK

    Well-Known Member

    Posted Mar 7, 2016
    120V heating element in this case. If I remember correctly, I had it plugged into a CFCI in my kitchen but after I realized it wasn't working, tried another non-CFCI outlet in the next room. I can't say how long it was firing dry until I noticed the switch was in the ON position but it sounds like a cheap HD wattage element can burn out quite fast under those conditions.

    I just wish I had enough smarts to turn everything off, unplug, and check the element. Had I seen it was totally crapped out, I had two options I suppose. Run to Home Depot and replace or simply leave it out and cap off the RIMS tube and direct fire like I wound up doing anyway. Of course I just left it in there and ran my damn wort through it all day.

    I had already doughed in and a bit of panic struck when I started recirculating and the temperature kept falling. I never assumed it burnt out like this, just that something else was malfunctioning so it took entirely too long just to diagnose and decide to direct fire.
     
    IslandLizard likes this.
  17. #17
    mainiac

    Not a Masshole!  

    Posted Mar 7, 2016
    I have one of these in my 8 gallon kettle that provides assistance to my induction cooktop in boiling. I've used it in many brew sessions over the past year, and had no issues whatsoever. It is stainless steel resistored, and LWD.

    http://bostonheatingsupply.com/SP10868LH.aspx
     
  18. #18
    kayakman

    Member

    Posted Mar 7, 2016
    The element failed because it ran dry. Low density design or stainless sheath would not have prevented this. Basically the element sheath melts, any moisture that is introduced to the magnesium oxide powder within the element will cause an electrical short to the sheath and will also expand splitting the sheath as shown. GFCI protection would have tripped the circuit but would not have prevented element failure.
     
  19. #19
    BrunDog

    Sponsor  

    Posted Mar 7, 2016
    This is one area where RIMS is inferior to HERMs (though I personally think it's superior otherwise). You need to build in a safety to make sure the element is not run dry. On my BCS controlled rig, using ladder logic, the element cannot be powered unless there is positive flow through the tube. Not just liquid but flow. It uses a flowmeter but there are inexpensive flow switches that anyone can incorporate.
     
  20. #20
    EdK

    Well-Known Member

    Posted Mar 8, 2016
    Totally makes sense when you look at it. Seems like there are two copper-looking "drops" at the main braking point. Maybe I was able to shut it off before more melting happened but the magnesium oxide was already exposed in some way.

    Looked into the inside, didn't seem like any of it actually dripped onto the tube itself. Potentially adding some magnesium to the beer doesn't sound so bad.
     
  21. #21
    ChocolateMaltyBalls

    Well-Known Member

    Posted Mar 8, 2016
    The lower the watt density the more time you have before melt down, some folks will dry fire their ripple elements to clean them. I've dry fired mine a few times when I forgot to turn off the HLT during sparge. It's still working fine
     
  22. #22
    cod3ck

    Well-Known Member

    Posted Mar 8, 2016


    I would think even if it wasn't GFCI, the breaker on the box would still trip from pulling too much current to the equipment?!

    Either the circuit must have still been able to complete or something wasn't grounded properly?

    I'm not calling anyone out, just seems curious how this went down. And scary/dangerous for that matter...
     
  23. #23
    BeardedBrews

    Well-Known Member

    Posted Mar 8, 2016
    If you use the basic pot, https://www.brewhardware.com/product_p/hotpod-ewl.htm then you need to ground your existing TC Flange nut and the metal pod cover. If you don't do that, then the rest of the rims tube and control box won't be protected from short circuit.

    It would be more clean to use the integrated TC version https://www.brewhardware.com/product_p/etc.htm so you just attach the ground to the all in one deal.
     
  24. #24
    EdK

    Well-Known Member

    Posted Mar 8, 2016
    Something other than the element to the adaptor nut? It has a nut where the ground wire was attached. Hard to see in the pic, but it was still attached. Could there be an issue with the outlet?

    Yeah, I saw that other TC one. Not sure when it would be in stock again. If I did use the basic pot, how would this ground be accomplished?

    Here is what I'm working with:
    [​IMG]
     
  25. #25
    dyqik

    Well-Known Member

    Posted Mar 8, 2016
    I think that it's pretty unlikely. A heating element burning up in air like this one did is likely to fail open, not short (short would require that the two ends of the element, which are separated by at least half an inch at the base, came into low resistance contact), which means no excessive current and no breaker trip.

    Wort or water isn't a very good conductor, and the contact to the wort/water is through a thin wire, so later adding wort after the element has burnt out also doesn't mean that enough current will be shorted to trip the breaker. It also looks like this element burnt out a little distance up the element, so there's also some resistance in the wires to that point.

    My bet is that the circuit wasn't complete enough to pass enough current to ground to trip the GFCI (if indeed it didn't trip the GFCI at all after the burn out and with wort in the tube - I'm not so sure from the OP's posts about moving from a GFCI to non-GFCI circuit). <WAG*> The open ends of the wires could possibly be so oxidized by overheating in air </WAG> that there's too much resistance from wire to wort to ground to pass the 5mA to ground that the GFCI needs to trip. You'd need about 40 kOhms or more from hot to ground through the wort for that to be the case.

    *WAG = Wild Ass Guess
     
  26. #26
    BrunDog

    Sponsor  

    Posted Mar 8, 2016
    Remember that these elements were not made for this purpose. They were meant to me submerged in a large volume of water full time where the convective fluid currents alone would keep their temperatures limited. They were not meant to be trapped in a small tube and possibly dry fired. A dry fired element will eventually burn up and open circuit - not short out nor ground fault. If by some miracle the heating were stopped at the right time to expose a conductor, then water/wort were added, it should fault to ground, but that conduction exposure is highly unlikely.
     
  27. #27
    BeardedBrews

    Well-Known Member

    Posted Mar 8, 2016
    Regarding the ground wire. I believe the BH element pod can have the "grounding lug" reversed so that the ground wire attaches on the outside of pod. If that is the case, then simply run a jumper between the pod lug and the element flange/nut lug. The TC will connect the element flange to the RIMS tube.


    Important testing:
    Once you wire this up, get a multi-meter and check the resistance between the ground pin on the cord you plug into the wall, and every other piece of metal that you can see/touch in your RIMS box.

    You want to make sure that the ground from that wire coming into the box is securely connected to any switches that have grounding screws, any SSRs that should be grounded on their bases, connected to the ground wire for the element cord coming back out of the box, and for good measure you can connect it to any of the screws inside the box that hold things together :D


    Like BrunDog said, it would take an unlikely set of circumstances for the element to have burned out and then short across to the RIMS tube. The worst case would have meant that the outside of your RIMS tube was electrically "hot". No matter what, keep the RIMS kit on a GFCI outlet all the time. That way there is something to automatically cut the power for you if you accidentally take 120v to the fingers.

    -B

    U8eJLKo.jpg
     
  28. #28
    EdK

    Well-Known Member

    Posted Mar 8, 2016
    Thank you! I did snap a pic when I took the other.

    I see the ground wire is coming in from the power supply (right lower hole), running through the ON/OFF power switch, and back out to the element (right upper hole).

    The wiring is a bit everywhere so I'll take a closer look. Do you know a schematic that would match this layout?

    [​IMG]
     
  29. #29
    BeardedBrews

    Well-Known Member

    Posted Mar 8, 2016
    You are pretty close to this:
    http://www.pjmuth.org/beerstuff/images/Auberin-wiring1-a4-2000w-BIAB-120V-A.jpg

    You may not have some of the switches (Element Power, E-Stop, PID Power) but you can get the general idea just by following the wires.


    Everything inside there looks very clean, and it will be easy to test your ground connections since they are all on that nice bus bar. Just check each one to the ground on the wall plug, and if those are working, you should be good to go.
     
    EdK likes this.
  30. #30
    EdK

    Well-Known Member

    Posted Mar 9, 2016
    Looks like they are back in and you are right, the cleaner connections are worth an extra $15, I'd say. I went ahead and ordered that and this element - https://www.brewhardware.com/product_p/element1500_long.htm

    I have an 18 in. tube, so there should be no issue with this, right?

    If I'm getting all this right, with a 1500 Watt element and chugger pump running I'm looking at like 14.4 amps (12.5 from the element + 1.9 from the pump). How does the extension cord factor into this? I run this from my kitchen outlet to the shed not far from my back door.

    I'm curious about this though, my GFCI outlet is probably just a 15 amp, right? Wouldn't the old HD element at 2000 Watts/120 volts/16.6 amps trip that just from running normal because it's over the amp allowance? Or is that not exactly how GFCI works? I recall it tripping one at my buddy's house (but there was also a freezer plugged into it). Or maybe the outlet is 20 amp?
     
  31. #31
    BeardedBrews

    Well-Known Member

    Posted Mar 9, 2016
    The GFCI will just protect you from connecting the power directly to a ground like your hand or something (Ground Fault Circuit Interrupter), it doesn't care about the amps. The circuit breaker at the panel is what determines how many amps can go through the line to your outlet. If you have a bigger breaker you will also need bigger wires to carry the power to the outlet. (And an outlet rated to handle the additional power, and a plug that can handle it)

    The wire thickness for an extension cord depends on how long the cord is. You can do 15 amps at 50 feet on 14 gauge wire without losing too much voltage.
     
  32. #32
    ChocolateMaltyBalls

    Well-Known Member

    Posted Mar 9, 2016

    GCFIs do not like fridge/freezer compressors or large pumps.

    Find the breaker that supplies your chosen outlet, if it's 20amp then you're fine. Good idea to turn it off and see what else is on that circuit.
     
  33. #33
    Jaybird

    Sponsor  

    Posted Mar 9, 2016
    I wouldn't build a RIMS without one! Simple, CHEAP and effective. just a simple float switch for $15 would do it.

    Hope the batch turns out man! Whatcha' gonna call it if it does?

    Cheers
    Jay
     
  34. #34
    dyqik

    Well-Known Member

    Posted Mar 9, 2016
    The GFCI outlet only trips if there is a ground fault (short to ground, detected as missing current between the hot and neutral). It has no overcurrent fault detection. That's provided by the breaker in the panel. If this GFCI outlet is in the kitchen, it's plausible that it's on a 20A circuit and breaker, shared with other outlets.

    Even if it isn't, it takes time for breakers to trip from small overcurrents, and the actual current will depend on the exact line voltage anyway - 16.67A at 120V may not trip the breaker very quickly, and if the line voltage is actually closer to 110V, the actual current will be lower - 15.2A at 110V - which might not trip at all.
     
  35. #35
    EdK

    Well-Known Member

    Posted Mar 9, 2016
    Thank you all for the insight.

    It's a BSDA and at this point is only about 2.5 weeks old, so very very young. I've tasted a recent sample and all seems well to me - nothing that gives me the idea of burnt wort or metallic off flavors that I can perceive, so there's a plus. Went down from 1088 to 1014, not too dry which was a concern as the hooplah with the RIMS tube had me wind up mashing a bit lower than target. Going to throw it in kegs this weekend and age for another 4+ months.

    My wife, who now brews with me (but is really more of the official stirrer and disappears when it's time to clean), found a recipe that was supposed to be a sort of St. Bernardus inspired brew. I did a bit of tweaking, mostly just dropped a random Marris Otter addition for a small quantity of Aromatic and adjusted sugar to malt ratios. We were originally going to brew it on Valentine's Day and the name that came to mind as a whole play on St. Bernardus was to call it St. Valentine which of course the wife loved.

    But after this debacle, something with meltdown sounds more fitting. Malt Meltdown
     
  36. #36
    EdK

    Well-Known Member

    Posted Mar 9, 2016
    So basically all I need is the meter, third down on this page - http://www.futurlec.com/Flow_Sensor.shtml - and there is an easy way to wire it into my current box to cut off the element power? Could some sort of red light be installed to indicate when the meter has tripped? I'm likely to be watching the flow like a hawk now, but it still seems like a cheap yet most useful fail safe.

    Or this thing - http://www.amazon.com/dp/B00NWF8L6U/?tag=skimlinks_replacement-20

    Not sure the float would work with the box setup.
     
    Last edited by a moderator: Oct 24, 2018
  37. #37
    Jaybird

    Sponsor  

    Posted Mar 9, 2016
    No I mean in the RIMS tube itself If you could get one to fit. I Don't see any reason why the flow sensor you linked wont work. It is all low voltage so it looks like you would need a Voltage regulator and then it is digital output so you just need to build accordingly. I think I would be using a simple tank style float switch at the top of my RIMS (if I used one) and disrupt the element relay. But my system is simple electrical relay driven. I use all full voltage everything accept my PID's of course..

    Cheers
    Jay
     
  38. #38
    EdK

    Well-Known Member

    Posted Mar 9, 2016
    Thanks, yeah, I think I came across one of the floats you are referring to in the mean time and edited but you had already posted at the same time.
     
  39. #39
    Jaybird

    Sponsor  

    Posted Mar 9, 2016
    Yeah something like that for sure. That one looks like they rated it for DC voltage/current but I think your on the right path for sure. I use a bunch of them in my brewery.

    Cheers
    Jay
     
    EdK likes this.
  40. #40
    EdK

    Well-Known Member

    Posted Mar 15, 2016
    Okay, so the hot pod and element came in today and as I suspected, the wire coming out of the box is not long enough, especially if you want to be able to unclamp the whole unit and remove the long element from the tube.

    Should I just cut out and rewire an outlet into the side of the box? This way I can get another short length of cord with a plug attached to the element and the whole thing becomes much more modular.

    Should this outlet be CFGI or can it just be a standard 15 amp in this case (considering the whole box will be plugged into one in my kitchen).

    I am a little worried about that ridge of the box and if a plate will fit over it (see below). Is there any other options using what's already there?

    [​IMG]
     