    Hi All,

    I'm trying to figure out what the contactor in many(/all) of PJs diagrams is for.

    If the SSR is turning on/off in conjunction with the PID, what is the purpose of the contactor?

    I'm sure it is obvious, but I can't seem to wrap my mind around it.

    -chris
     
  2. #2
    jeffmeh

    Well-Known Member

    Posted Nov 30, 2012
    An SSR can leak current, can fail closed (on), and is only controlling one leg of your 240V circuit. The contactor between the SSR and the element is there so that when you set the switch controlling the contactor off, both legs to the element are truly off.
     
  3. #3
    stlbeer

    Senior Member  

    Posted Nov 30, 2012
    Also, the SSR can switch the power off/on at a much higher rate than a contactor can. The two work in conjunction with each other.
     
  4. #4
    goybar

    Well-Known Member

    Posted Dec 1, 2012
    OK, so it really is more of a fail safe or safety item. Not really required but foolish not to use one.
     
  5. #5
    Rarian

    Active Member

    Posted Dec 1, 2012
    Without a contactor in a 240v system your PID would only be able to output between 50%-100% power; one leg would continually be Hot.
     
  6. #6
    milesvdustin

    Well-Known Member

    Posted Dec 1, 2012
    I don't use one. I always make sure the element is under water before I switch it on just in case.
     
  7. #7
    whoaru99

    Well-Known Member

    Posted Dec 1, 2012
    Not sure that matters from a heating standpoint. Even if only one wire is switched the element only has two states...on or off. 0% or 100%.

    From a hazard standpoint it matters through. If only one leg is broken you still have 120V to ground or neutral on the element, potentially a shock hazard.
     
  8. #8
    jgadbois

    Member

    Posted Dec 1, 2012
    I think you are misunderstanding 240v.

    Current flows from one leg thru the element and thru the other leg. If the SSR is off there is no current flow and therefore no power. With the SSR off there is a 120v potential to ground at any point in the circuit which may be what you were thinking.
     
  9. #9
    stlbeer

    Senior Member  

    Posted Dec 2, 2012
    I'd add that when SSR's fail, they usually fail closed - allowing full current to flow through them - regardless of what the control circuit is doing. Since we only need to control 1 leg of a 240v system a contactor is a requirement to ensure the circuit is off.

    Your life is more important than $10 your going to save by not putting in a contactor or the $50 you'll save by not buying the next larger sized panel.
     
  10. #10
    gbrewing

    Well-Known Member

    Posted Dec 2, 2012
    You can also use the contactor as an emergency off for the entire system. The big red mushroom looking button on control panels is usually wired to the power in contactor.

    If things go wrong, you depress the mushroom button and it kills all power instantly.
     
  11. #11
    Handsaw

    Well-Known Member

    Posted Jan 22, 2013
    I've been trying to figure out how the contactor between the SSR and the element is a safety issue. I can see that if the SSR fails closed and the element is out of water then you burn up the element, but I don't see where the contactor is a personal safety issue.
     
  12. #12
    stlbeer

    Senior Member  

    Posted Jan 22, 2013
    What happens when you drain the water out of the tank? To turn off the element you either unplug it, adjust the water pickup so the water level doesn't go below the element, turn off the PID, or turn off the element using a switch (a contactor).

    You decide how safe you want to be. For < $20 this is a no-brainer solution.
     
  13. #13
    BadNewsBrewery

    Well-Known Member

    Posted Jan 22, 2013
    It's a safety issue because when I want my element off, it better be off - not on, or kinda on, or on if the PID thinks it should be on... but OFF. So when I go to clean the element it's not hot or powered up.
     