Propane tank froze regulator - Home Brew Forums

Register Now!
Home Brew Forums > Home Brewing Beer > Equipment/Sanitation > Propane tank froze regulator

Reply
 
Thread Tools
Old 10-14-2008, 09:42 PM   #1
ShortSnoutBrewing
Kwanesum Chinook Illahee
HBT_LIFETIMESUPPORTER.png
 
ShortSnoutBrewing's Avatar
Recipes 
 
Oct 2007
Portland, OR
Posts: 3,213
Liked 19 Times on 17 Posts



SO I was brewing this past weekend. Saturday morning I got up and took a few propane tanks to the gas station to be filled. I have your normal everyday tank, then one about twice the size that is ubber old. Small one worked fine for heating my strike water etc. While I was doing that, the large one started to hiss and gas was coming out. It was sitting in the sun for a few hours and thought that was it so I moved it in the shade, it stopped.

Well, I hooked it up to my burner to start my boil. Within about 5 minutes the regulator was frosted over. I knew this was not good, so I turned off the gas, disconnected then attached the smaller tank and completed my boil.

I know this isn't good/right, but what is it? Water in the tank somehow? Over filled tank??

Now, I just filled this sucker at close to $30. Is there anything I can do that won't involve loosing it all?

 
Reply With Quote
Old 10-14-2008, 09:48 PM   #2
McKBrew
 
McKBrew's Avatar
Recipes 
 
Oct 2006
Hayden, Idaho
Posts: 8,204
Liked 35 Times on 30 Posts


I googled this and there are about 1500 different "reasons" for why it occurs and just about as many recommendations on what to do. They all seem to contradict eachother, so I'm just going to wait for one of our resident "gas geeks" to give me a detailed technical explanation and then for someone else to put it in laymans terms. I remember last year at Brewtopia's holiday party that it got down to freezing and the big gas heat lamps would go out and keep having to be restarted.
__________________
Make Beer, Not War.

 
Reply With Quote
Old 10-14-2008, 10:15 PM   #3
kladue
Senior Member
HBT_LIFETIMESUPPORTER.png
Recipes 
 
Dec 2006
Turner, Oregon, Oregon most of the time now
Posts: 2,305
Liked 53 Times on 47 Posts


The second guess, over filled tank, the relief valve opening while not in use meant that tank had no room for propane liquid to expand. The tank was sending liquid propane into the regulator where it was trying to turn into gas again and it needs heat to change from liquid to gas. Same process that chills the tank only on a much smaller and colder scale as the surface area of the regulator is so small. As to using the tank, keep the flow down for about 30 minutes and enough propane should be burned off to correct the problem of liquid propane entering the regulator.


 
Reply With Quote
Old 10-14-2008, 10:20 PM   #4
ShortSnoutBrewing
Kwanesum Chinook Illahee
HBT_LIFETIMESUPPORTER.png
 
ShortSnoutBrewing's Avatar
Recipes 
 
Oct 2007
Portland, OR
Posts: 3,213
Liked 19 Times on 17 Posts


Solution?
0

 
Reply With Quote
Old 10-14-2008, 11:00 PM   #5
BigKahuna
Senior Member
HBT_LIFETIMESUPPORTER.png
 
BigKahuna's Avatar
Recipes 
 
Feb 2008
Eastern Colorado
Posts: 5,971
Liked 52 Times on 45 Posts


Pour hot water over the regulator. It's just the condensation freezing on the outside of the regulator body due to high humidity and super cold propane inside the tank. Not a big deal, but hot water will clear it up if you need it to.
__________________
Seriously. I'm here for BEER
It's Not The Size Of Your Rig That Counts....It's How Often You Use It.

 
Reply With Quote
Old 10-15-2008, 12:52 AM   #6
ShortSnoutBrewing
Kwanesum Chinook Illahee
HBT_LIFETIMESUPPORTER.png
 
ShortSnoutBrewing's Avatar
Recipes 
 
Oct 2007
Portland, OR
Posts: 3,213
Liked 19 Times on 17 Posts


So I'm assuming it will stop once the propane level drops to an acceptable level?

 
Reply With Quote
Old 10-15-2008, 12:58 AM   #7
Parker36
 
Parker36's Avatar
Recipes 
 
Sep 2007
Lesotho
Posts: 4,742
Liked 22 Times on 20 Posts


Your tank isnt on its side is it?

 
Reply With Quote
Old 10-15-2008, 01:09 AM   #8
ShortSnoutBrewing
Kwanesum Chinook Illahee
HBT_LIFETIMESUPPORTER.png
 
ShortSnoutBrewing's Avatar
Recipes 
 
Oct 2007
Portland, OR
Posts: 3,213
Liked 19 Times on 17 Posts


Nope. Don't think I could stop it from rolling away if it was.

 
Reply With Quote
Old 10-15-2008, 01:16 AM   #9
eschatz
 
eschatz's Avatar
Recipes 
 
Dec 2007
Terre Haute, IN
Posts: 3,434
Liked 35 Times on 19 Posts


Yeah, I've heard about that happening if you have too many ports that are pulling too much propane from the tank. I don't exactly understand it. But hope that helps you.
__________________
play the bass, brew the beer

What's tappening? :D

 
Reply With Quote
Old 10-15-2008, 02:13 AM   #10
DutchK9
 
DutchK9's Avatar
Recipes 
 
May 2008
Springfield, Illinois
Posts: 368
Liked 2 Times on 2 Posts


Have you put it on a scale to see if it is overfilled?
__________________
Up Next
Selection Premium-Chablis, Selection Premium-Pettite Sirah, Selection Premium-Ruisseaublanc
Primary
Guinnesss Extra Stout Clone
Secondary
Bottled & Kegged
Guinnesss Extra Stout Clone, Bass Ale Clone, Midwest English Bitter, Muntons Nut Brown Ale, Coopers Pilsener, Northern Bock, Apfelwein, Select Premium-Merlot, Select Premium-Borolo, Select Premium-Valpolicella, Northern Nut Brown Ale
Gone
Midwest Sierra Nevada Pale Ale, Midwest Hanks Hefeweizen

 
Reply With Quote


Reply
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
20# CO2 tank for Nitrogen tank and regulator gruversm Equipment/Sanitation 1 03-09-2009 08:13 AM
Propane regulator help indianaroller Equipment/Sanitation 3 03-02-2009 08:21 PM
propane tank grrtt78 Equipment/Sanitation 15 03-03-2007 05:17 PM
Propane Regulator for 300,000 btu? JoeRags Equipment/Sanitation 5 01-29-2007 08:43 PM
propane tank Born Brewing Co. All Grain & Partial Mash Brewing 13 08-10-2005 02:09 AM


Forum Jump