Using a STC-1000 I set up a side by side fridge as a fermenter. I wired it so that when the temp was above the setpoint, the compressor would kick on and a computer fan would draw air in from the freezer side. Below the setpoint, a ceramic heater and a circulating fan would kick on.

I was able to lager one batch of beer, but afterwards, the fridge stopped working completely. I'm pretty sure this setup burned out the compressor. because the controller only has one setpoint, the heating and cooling temp swings overshot the setpoint frequently resulting in the compressor running a lot.

Has anybody had any issues like this? Any suggestions to fix it? I'm considering a second STC-1000 in order to introduce a second setpoint. Alternately, a better temp controller that has two setpoints.

Thanks for any feedback!
Andy

 
Reply With Quote
Old 12-17-2013, 09:06 AM   #2
FatDragon
HBT_LIFETIMESUPPORTER.png
 
FatDragon's Avatar
Recipes 
 
Aug 2013
Wuhan, China
Posts: 1,605
Liked 403 Times on 283 Posts


You can set a deviation on the STC-1000 so the heating/cooling functions don't turn on within a certain range of your set temperature. By default I believe mine was set to 0.5C, so if I'm set to 17.5 the heater turns on at 17 and the cooler at 18. I don't recall offhand which of the functions controls this, but you can set it way wider than mine is set.

Another option would be removing the heater from your setup - that way your temps won't swing as much, meaning less compressor time.
__________________
Feel free to correct me if I'm wrong. It's been known to happen.

Primary: Soon...
Secondary: Next Winter Quad
Bottled: November 2014 RIS, Next Winter Barleywine, Rye Saison, Bitter Beer Face APA, Inaugural Third Time's a Charm Gose, Oatmeal Porter
Bottle Aging: Bochet, Baby Bochet, Osmanthus Mead
Coming Up: Doppelbock (if it ever gets cold enough to ferment a lager this winter...), Durian Hefeweizen, Hopbursted Vienna APA, Passion Fruit Gose

Wynne-R Likes This 
Reply With Quote
Old 12-17-2013, 09:19 AM   #3
mojo2008
HBT_SUPPORTER.png
 
mojo2008's Avatar
Recipes 
 
May 2010
Herndon, VA
Posts: 64
Liked 4 Times on 4 Posts


Thanks for the information. I didn't realize you could adjust the setpoint accuracy on the controller.

As for the heater, I probably could remove it from the system during most of the year. The fridge is in the garage and it typically doesn't get much cooler than 50 degrees or so in the winter.

 
Reply With Quote
Old 12-17-2013, 01:20 PM   #4
smertz001
HBT_LIFETIMESUPPORTER.png
 
smertz001's Avatar
Recipes 
 
Feb 2013
Houston, TX
Posts: 41
Liked 2 Times on 2 Posts


Before blaming the compressor I would check the relay connected to it. I thought my compressor went, and it turned out to be a $30 relay instead after checking closer and testing.
A video on testing compressor and relay.

ChrisfromAbby Likes This 
Reply With Quote
Old 12-17-2013, 01:29 PM   #5
IslandLizard
Progressive Brewing
HBT_LIFETIMESUPPORTER.png
 
IslandLizard's Avatar
Recipes 
 
Jan 2013
Pasadena, MD
Posts: 7,004
Liked 1247 Times on 1066 Posts


+1^

Did you set the cooling delay at 10 minutes (the max)? That curbs excessive wear on the compressor and relay.

 
Reply With Quote
Old 12-17-2013, 02:20 PM   #6
raouliii
HBT_SUPPORTER.png
 
raouliii's Avatar
Recipes 
 
Aug 2011
Ponchatoula, LA
Posts: 1,015
Liked 118 Times on 102 Posts


In the Setup menu, F1 represents the set temperature; F2 represents the difference value. When the measured temperature is equal to the set temp + the diff temp, the cooling relay closes. When the measured temp drops to the set temp, the cooling relay opens. Vice versa for heating.

In every system there will be undershoot of cooling and overshoot of heating. IMO, it is best to determine what these values are for your system, operating in steady state, and establish an F2 value that is greater than both the undershoot and overshoot values. This will keep the cooling and heating functions from constantly fighting one another. If undershoot or overshoot are unacceptably large values, redesign may be necessary. A simple change in probe placement may help.
__________________
On Tap:
LeftOvers Amber
Rearranger IPA - Chinook, Simcoe, Cascade
Ponchy Pale Ale - Millennium and Willamette
NippleRub Ultra (Light Lager w/Mexican Lager yeast)

In the Chamber:
Nothing

Next Up:
A Light Lager

 
Reply With Quote
Old 12-18-2013, 01:24 AM   #7
acidrain
Recipes 
 
Jul 2012
Seattle, Washington
Posts: 2,104
Liked 183 Times on 158 Posts


Did you have the temp probe taped and insulated on the fermentation vessel? A thermowell into the beer would be even better. If you just had the temp probe in the air, it will way overshoot.
__________________
Keg #1: Brown Bomber Bourbon/Oak Vanilla Porter
Keg #2: The Bollocks ESB
Keg #3 Lawnmower APA
Fermenter: Empty
Bottled: Mjolnir Mead, Lazy Daze Hefe.

 
Reply With Quote
Old 12-18-2013, 02:13 AM   #8
cgrivois
Recipes 
 
May 2012
willow spring, nc
Posts: 247
Liked 19 Times on 15 Posts


The first heater i had was causing my system to overshoot on the heating side, causing the compressor to run more. I replace the heater with one of my wifes scented wax deals that only has a 40 watt bulb and I vary rarely overshoot on the heat now. In fact the compressor rarely comes on especialy since its in the garage and it has been cold lately. The first one heated the air inside of the fridge too fast causing it to over shoot. Long story short, go with the lowest power heat source that you can.

 
Reply With Quote
Old 12-18-2013, 02:15 AM   #9
FuzzeWuzze
I Love DIY
HBT_SUPPORTER.png
 
FuzzeWuzze's Avatar
Recipes 
 
Jun 2012
Newberg, Oregon
Posts: 3,121
Liked 435 Times on 318 Posts


Quote:
Originally Posted by acidrain View Post
Did you have the temp probe taped and insulated on the fermentation vessel? A thermowell into the beer would be even better. If you just had the temp probe in the air, it will way overshoot.
You have that backwards, in the thermowell the freezer will kick on for a long time because it will take it a long time to move the beer even half a degree...by then your freezer is at 0F.

If your using a STC-1000 and not something like BrewPi with a PID controller your best bet is to measure the AIR temperature inside of your chamber and set it a few degree's below your expected fermentation temperature.

You should only really use a thermowell if you have a PID mechanism that will compensate for overshoot and shut the freezer off early so that your freezer coasts in to the set temperature.

For example this is what my BrewPi setup results in using nothing but a Lasko personal ceramic heater and a thermowell in my 8 gallon bucket, its about 30-45 in the garage where the freezer is. The worst temperature swings were after fermentation ended on the 15th and it was still overcompensating only about .5F as it figured out the new settings it needed.


Your beer will always be pulled towards ambient, if you set your chamber to 62, the beer will get to 62, start fermenting and be around 64-65 most likely, this can be monitored with a separate probe or just one of those thermometer stickers you stick to the side of carboy/buckets. It should only take a few brews to figure out what this delta is and set your chamber accordingly.

To keep your freezer at 62 it should only have to turn on every once in a while...honestly i wouldnt use both a heater and a cooler. If its too cold(which it likely is by now in VA) just use the heater instead of having them combat eachother. Save the cooling for spring/summer.

iaefebs Likes This 
Reply With Quote
Old 12-18-2013, 02:23 AM   #10
cgrivois
Recipes 
 
May 2012
willow spring, nc
Posts: 247
Liked 19 Times on 15 Posts


My probe is in a thermawell and I my temp doesnt coast more than the .3C the controller is set too. As mentioned above I used the smallest heat source I could. I also placed an aditional 5 gal bucket of water in the fridge for some thermal mass.

 
Reply With Quote
Reply
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
What's More Accurate? smangold Fermentation & Yeast 2 12-18-2012 02:34 PM
Which temp is accurate cd38 Fermentation & Yeast 8 07-24-2012 08:32 PM
Accurate OG readings dropjaw83 Beginners Beer Brewing Forum 5 07-02-2012 02:58 AM
How Accurate? FishinDave07 Brewing Software 1 04-24-2008 12:14 PM
Accurate FG AnOldUR Beginners Beer Brewing Forum 3 04-29-2007 10:50 PM


Forum Jump