Coldbreak Brewing Giveaway - Open to All!

Home Brew Forums > Home Brewing Beer > Electric Brewing > Help with wiring my elements
Reply
 
Thread Tools
Old 12-02-2013, 04:47 PM   #1
thefost
Feedback Score: 0 reviews
Recipes 
 
Join Date: Jun 2013
Posts: 331
Liked 59 Times on 42 Posts
Likes Given: 15

Default Help with wiring my elements

I'm planning out the basic wiring of my new electric rig and could use some help!

My setup will utilize 3 120V 1500W elements connected to 3 separate 20A breakers (actually it will use 5, but only 3 at a time - lets keep this simple for now). The distance from the outlets will be 50ft, 50ft, and 100ft.

Here's a quick drawing of what I had in mind for the cheapest safe setup, but could really use your input before I burn my apartment down =)


Click image for larger version

Name:	Electricity.jpg
Views:	213
Size:	40.7 KB
ID:	163742  
thefost is offline
 
Reply With Quote
Old 12-02-2013, 04:59 PM   #2
brew_ny
Social_Misfit
HBT_LIFETIMESUPPORTER.png
Feedback Score: 4 reviews
 
brew_ny's Avatar
Recipes 
 
Join Date: Apr 2013
Location: Charleston Four Corners, New York
Posts: 3,751
Liked 626 Times on 440 Posts
Likes Given: 1929

Default

your 110 foot run with 14 gauge wire drawing 1500 watts maybe too much draw

I woulld have to check a calculator to be sure

12 more then likely would be better

and on the 50 foot run maybe use the 14

all the best

S_M


__________________
Quote:
Originally Posted by Yooper View Post
A well made beer doesn't need time to age out off flavors, and you don't create off-flavors in the first place.
Quote:
Originally Posted by 1977Brewer View Post
I'ma make a beer. It'll have barley. Hops too. I'll like it, my wife will hate it.
"Bread, work, or lead!"

710 Brewing We go to sleep errly and wake up errly
brew_ny is offline
 
Reply With Quote
Old 12-02-2013, 08:58 PM   #3
neild5
HBT_SUPPORTER.png
Feedback Score: 0 reviews
Recipes 
 
Join Date: Apr 2010
Location: Forest Park, Illinois
Posts: 97
Liked 14 Times on 12 Posts
Likes Given: 23

Default

20 amp circuit needs 12 ga wire as a minimum. You want the heating to happen in the elements not the wire.
neild5 is offline
brew_ny Likes This 
Reply With Quote
Old 12-02-2013, 09:20 PM   #4
thefost
Feedback Score: 0 reviews
Recipes 
 
Join Date: Jun 2013
Posts: 331
Liked 59 Times on 42 Posts
Likes Given: 15

Default

Thanks, I will definitely up the cable gauge

Quote:
Originally Posted by neild5 View Post
20 amp circuit needs 12 ga wire as a minimum. You want the heating to happen in the elements not the wire.
Is there a reason why I'd want 12 gauge instead of 14 gauge for the 50ft extension cords? Both cords would be rated to 15A 1875 watts, so I'm not sure why 12 gauge would be an improvement for this length.
thefost is offline
 
Reply With Quote
Old 12-02-2013, 10:11 PM   #5
brew_ny
Social_Misfit
HBT_LIFETIMESUPPORTER.png
Feedback Score: 4 reviews
 
brew_ny's Avatar
Recipes 
 
Join Date: Apr 2013
Location: Charleston Four Corners, New York
Posts: 3,751
Liked 626 Times on 440 Posts
Likes Given: 1929

Default

here is the easy answer, thinner the wire the more resistance the thicker the wire less resistance

over a 50 foot or a 100 foot run you have more power loss with a thinner wire

when you pull lots of power over an extension cord an it fells hot to the touch that is resistance

1500 watts at 110 volts is about 14 amp so you are maxing you wire out

a 15 amp rated wire is better using 10 amps, me when I want to run something drawing 14 amps on 110 with a 100 foot cord I use a 10 gauge extension cord

the advice given is for safety, burning your place to the ground to brew beer would suck ass

good luck and be safe

S_M
__________________
Quote:
Originally Posted by Yooper View Post
A well made beer doesn't need time to age out off flavors, and you don't create off-flavors in the first place.
Quote:
Originally Posted by 1977Brewer View Post
I'ma make a beer. It'll have barley. Hops too. I'll like it, my wife will hate it.
"Bread, work, or lead!"

710 Brewing We go to sleep errly and wake up errly
brew_ny is offline
 
Reply With Quote
Old 12-02-2013, 11:10 PM   #6
thefost
Feedback Score: 0 reviews
Recipes 
 
Join Date: Jun 2013
Posts: 331
Liked 59 Times on 42 Posts
Likes Given: 15

Default

Thanks NY and agreed, I want to be as safe as possible here =)

I think I see where my confusion is. Both 12 gauge and 14 gauge extension cords are rated to 15A because they use a NEMA 5-15 connector, which is the limiting factor. If I'm getting close to 15A, is it particularly important safety-wise to use a 20A NEMA 5-20 connector instead? If it is I suppose I could chop off the ends of some 12 gauge extension cords and install 5-20 connectors.
thefost is offline
 
Reply With Quote
Old 12-02-2013, 11:21 PM   #7
brew_ny
Social_Misfit
HBT_LIFETIMESUPPORTER.png
Feedback Score: 4 reviews
 
brew_ny's Avatar
Recipes 
 
Join Date: Apr 2013
Location: Charleston Four Corners, New York
Posts: 3,751
Liked 626 Times on 440 Posts
Likes Given: 1929

Default

Quote:
If it is I suppose I could chop off the ends of some 12 gauge extension cords and install 5-20 connectors.
buy wire and build yous own cords they will be much better

those cheap cords are junk, every time you plug something in you add more resistance

if you can, then you can have the connectors you want/need

all the best

S_M
__________________
Quote:
Originally Posted by Yooper View Post
A well made beer doesn't need time to age out off flavors, and you don't create off-flavors in the first place.
Quote:
Originally Posted by 1977Brewer View Post
I'ma make a beer. It'll have barley. Hops too. I'll like it, my wife will hate it.
"Bread, work, or lead!"

710 Brewing We go to sleep errly and wake up errly
brew_ny is offline
 
Reply With Quote
Old 12-02-2013, 11:24 PM   #8
BBBF
Feedback Score: 0 reviews
Recipes 
 
Join Date: Aug 2008
Location: Chicago
Posts: 1,201
Liked 67 Times on 54 Posts
Likes Given: 32

Default

With 20A outlets, you could potentially use a 2000W element. However, I would bet your male AC connector is rated for only 15. If you think you might ever want to use 2000W, I would use a strain relief instead.

http://www.amazon.com/gp/product/B00...?ie=UTF8&psc=1
BBBF is offline
 
Reply With Quote
Old 12-03-2013, 12:05 AM   #9
thefost
Feedback Score: 0 reviews
Recipes 
 
Join Date: Jun 2013
Posts: 331
Liked 59 Times on 42 Posts
Likes Given: 15

Default

Quote:
Originally Posted by BBBF View Post
owever, I would bet your male AC connector is rated for only 15.
Just got home and checked my sockets, they are NEMA 5-15 style. My breakers are definitely 20A though, so Im not sure what the deal is there. I'm definitely limited to 1500W then.
thefost is offline
 
Reply With Quote
Old 12-03-2013, 12:11 AM   #10
brew_ny
Social_Misfit
HBT_LIFETIMESUPPORTER.png
Feedback Score: 4 reviews
 
brew_ny's Avatar
Recipes 
 
Join Date: Apr 2013
Location: Charleston Four Corners, New York
Posts: 3,751
Liked 626 Times on 440 Posts
Likes Given: 1929

Default

Quote:
Originally Posted by BBBF View Post
With 20A outlets, you could potentially use a 2000W element. However, I would bet your male AC connector is rated for only 15. If you think you might ever want to use 2000W, I would use a strain relief instead.

http://www.amazon.com/gp/product/B00...?ie=UTF8&psc=1
how would a strain relief change anything ?


__________________
Quote:
Originally Posted by Yooper View Post
A well made beer doesn't need time to age out off flavors, and you don't create off-flavors in the first place.
Quote:
Originally Posted by 1977Brewer View Post
I'ma make a beer. It'll have barley. Hops too. I'll like it, my wife will hate it.
"Bread, work, or lead!"

710 Brewing We go to sleep errly and wake up errly
brew_ny is offline
 
Reply With Quote
Reply


Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
Elements burgieburgie For Sale 6 11-29-2012 12:16 AM
Keezer Collar Temp Controller Wiring & Fan Wiring Questions. Revvy Kegerators and Keezers 12 09-23-2012 01:21 PM
How many elements? TravelingBrewer22 Electric Brewing 6 12-13-2011 10:00 PM
One PID, Two Elements? Rondacker Electric Brewing 4 05-03-2011 12:37 AM
Do elements HAVE to be LD/ULD? mattd2 Electric Brewing 27 12-13-2010 11:57 PM


Forum Jump

Newest Threads

LATEST SPONSOR DEALS