I did some rewiring in my control panel and then tested it with my multimeter. At my two 240 vac outlets, I found 235 vac (on) and 0.25 vac (off) and 235 vac (on) and 1.1 vac (off). I was expecting 0.0 vac with the contactors off. I then tested upstream (236 vac) and downstream (0.85 vac)of my main contactor when it was off. Is this kosher or do I have something wrong?


stevehaun is offline
 
Reply With Quote
Old 11-30-2013, 10:46 PM   #2
lschiavo
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
 
lschiavo's Avatar
Recipes 
 
Join Date: Sep 2009
Location: Surrounded by Yoopers
Posts: 4,303
Liked 926 Times on 618 Posts
Likes Given: 709

Default

It may just be the meter. What does it read across your index fingers? Then with the probes shorted? And open air?


lschiavo is offline
 
Reply With Quote
Old 11-30-2013, 10:55 PM   #3
stevehaun
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
Recipes 
 
Join Date: Dec 2006
Location: hudson, wi
Posts: 601
Liked 18 Times on 17 Posts
Likes Given: 46

Default

index finger 0.0
shorted 0.0
air 0.01-0.02
stevehaun is offline
 
Reply With Quote
Old 11-30-2013, 10:59 PM   #4
ajdelange
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
Recipes 
 
Join Date: Aug 2010
Location: McLean/Ogden, Virginia/Quebec
Posts: 7,461
Liked 957 Times on 757 Posts
Likes Given: 26

Default

Even when a contactor is open some current can flow between the open contacts via because of the capacitance between them. As this current is at right angles to the voltage no energy is transferred across an open contactor but if the meter is high impedance (as modern meters are) it may register a small voltage. This is a possible, but not necessarily the, explanation for what you are seeing.
ajdelange is online now
 
Reply With Quote
Old 11-30-2013, 11:21 PM   #5
Begin2Brew
Searching for the perfect beer one at a time
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
 
Begin2Brew's Avatar
Recipes 
 
Join Date: Jan 2011
Location: Antioch, IL
Posts: 742
Liked 59 Times on 56 Posts
Likes Given: 11

Default

Are you going across an SSR by any chance?
__________________
Bill

Ruffled Feathers Brewery
Begin2Brew is online now
 
Reply With Quote
Old 12-01-2013, 12:30 AM   #6
stevehaun
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
Recipes 
 
Join Date: Dec 2006
Location: hudson, wi
Posts: 601
Liked 18 Times on 17 Posts
Likes Given: 46

Default

No. The SSR is between the main contactor and the contactors that control the elements.
stevehaun is offline
 
Reply With Quote
Old 12-01-2013, 12:40 AM   #7
lschiavo
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
 
lschiavo's Avatar
Recipes 
 
Join Date: Sep 2009
Location: Surrounded by Yoopers
Posts: 4,303
Liked 926 Times on 618 Posts
Likes Given: 709

Default

I wouldn't worry about a volt or fraction thereof. It is probably some phenomenon like AJ described. I dislike my digital meter and usually use an old analog one if I am only checking for power and continuity. Watch for auto range too. I scratched my head a few times not realizing my meter was displaying mV.
lschiavo is offline
 
Reply With Quote
Old 12-01-2013, 01:08 AM   #8
passedpawn
Waste Allocation Load Lifter - Earth Class
HBT_MODERATOR.png
Feedback Score: 1 reviews
 
passedpawn's Avatar
Recipes 
 
Join Date: Apr 2009
Location: ☼ Clearwater, FL ☼
Posts: 21,325
Liked 4478 Times on 2704 Posts
Likes Given: 3809

Default

You should not get any leakage through a contactor. I suspect you're reading your own aura. You might be a lightning attractor... be careful out there.

j/k. If you are downstream of the contactor, it might be something simple like a seebeck effect from dissimilar metals. I wouldn't worry about a volt.

AC voltage? Might be what you're picking up from the walls.


__________________
- Andrew
passedpawn is offline
 
Reply With Quote
Reply


Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
Voltage test on PID/SSR Psych Electric Brewing 5 01-21-2013 06:05 PM
Voltage Rating. What exactly does mean? mattrennert Electric Brewing 3 08-11-2012 08:30 PM
Switch at different voltage njbabs Electric Brewing 2 07-13-2011 10:30 PM
Downstream system??? Lost_Sailor15 Bottling/Kegging 1 04-19-2011 11:25 PM
Do SSR's leak voltage while off? Ranger9913 Brew Stands 11 03-24-2010 02:28 PM


Forum Jump

Newest Threads

LATEST SPONSOR DEALS