this isn't exactly brewing related, but was brought to light by my recent addition of a 30A gfci breaker in my main breaker box.

The load center is a Square D QO20M which is probably at least 25 years old. It is a single neutral/ground bar setup at which the previous owner/DIY specialist took the liberty of adding some circuits to. They have doubled up 14ga grounds, which from what I read is OK. The problem I saw is they have also combined grounds and neutral's under the same lug in the bar. I know this is not to code, and I'm also pretty sure its not safe.

My question is, what is the best course of action? The label in the box says grounding kit PK9GTA can be added if necessary.

While that may be an option, I was wondering if cutting the main and simply removing all the neutrals and grounds and then attaching them properly (2 grounds per lug / 1 neutral) would work? There appear to be enough spots to attach all the runs for each circuit.

Again, sorry its not really brewing related, but I think its important before moving forward with my setup.



 
Reply With Quote
Old 11-27-2013, 02:47 PM   #2
The10mmKid
Recipes 
 
Jul 2013
Home of the Wright Brothers
Posts: 845
Liked 100 Times on 73 Posts


If it was mine, I'd move as many as three or four grounds under each screw.

Might be too late(wires too short), but we will 'braid' four at a time and get them under one screw.

One neutral per screw.

Try to make a couple open spots for the future.

Also, try to use the larger holes last.

'da Kid



 
Reply With Quote
Old 11-27-2013, 02:51 PM   #3
Strecker25
Recipes 
 
Jan 2011
Rochester, NY
Posts: 200
Liked 6 Times on 4 Posts


So no reason to add the ground bar? That seems like it would be significantly more work, since all the knockouts are on the top near the current neutral bar, and like you said the wires are probably cut too short to make it to the bottom for the new bar.

I think I'll just take a day and combine/move them. In the meantime, any immediate risk of how it is set up? All the lugs are tight and none of the wires seem like they could easily come loose.

Thanks for the reply.

 
Reply With Quote
Old 11-27-2013, 06:20 PM   #4
The10mmKid
Recipes 
 
Jul 2013
Home of the Wright Brothers
Posts: 845
Liked 100 Times on 73 Posts


Panels have been wired the way you described for decades.

Problems started showing up when we would wire two branch circuits with a common neutral. Very common in the kitchen where multiple circuits are required.

'da Kid

 
Reply With Quote
Old 11-27-2013, 08:35 PM   #5
Strecker25
Recipes 
 
Jan 2011
Rochester, NY
Posts: 200
Liked 6 Times on 4 Posts


Gotcha, thanks for the clarification. Ill pick a day and clean it up.

cheers

 
Reply With Quote
Old 11-30-2013, 12:30 AM   #6
kenh
Registered User
Recipes 
 
Oct 2013
Posts: 256
Liked 20 Times on 16 Posts


Quote:
Originally Posted by Strecker25 View Post
this isn't exactly brewing related, but was brought to light by my recent addition of a 30A gfci breaker in my main breaker box.

The load center is a Square D QO20M which is probably at least 25 years old. It is a single neutral/ground bar setup at which the previous owner/DIY specialist took the liberty of adding some circuits to. They have doubled up 14ga grounds, which from what I read is OK. The problem I saw is they have also combined grounds and neutral's under the same lug in the bar. I know this is not to code, and I'm also pretty sure its not safe.

My question is, what is the best course of action? The label in the box says grounding kit PK9GTA can be added if necessary.

While that may be an option, I was wondering if cutting the main and simply removing all the neutrals and grounds and then attaching them properly (2 grounds per lug / 1 neutral) would work? There appear to be enough spots to attach all the runs for each circuit.

Again, sorry its not really brewing related, but I think its important before moving forward with my setup.
If it's the main power panel into the house it does not matter. The ground and neutral are bonded together anyways. In other words they are the exact same circuit. And most houses only have a main panel.



 
Reply With Quote
Reply
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
Chugger center inlet adapter question jmwils1 Equipment/Sanitation 13 11-10-2012 05:12 PM
Temperature Controller Inductive Load Question EFaden Kegerators & Keezers 2 10-18-2010 08:39 PM
March pump center inlet question jwright Equipment/Sanitation 2 10-24-2009 12:38 PM
Adding a remote load center for Electric kettle Gussymo Equipment/Sanitation 3 12-17-2008 05:36 PM
Question on Center Keg Height StankAle Bottling/Kegging 8 05-15-2008 07:49 PM


Forum Jump