Hey Folks!

I picked up an Eaton 50amp GFCI BR Type Spa Panel and I am having a hell of a time deciphering the wiring schematic. If I'm reading this correct, line in comes into the panel on the left side of the breaker and line out goes out the right side of the breaker? The ground and common will be self explanatory if I can figure out the line in/out.


Click image for larger version

Name:	image-3937295502.jpg
Views:	541
Size:	38.7 KB
ID:	157195   Click image for larger version

Name:	image-3917368797.jpg
Views:	393
Size:	37.2 KB
ID:	157196  
__________________
Blind Pirate Brewing Co.
Plundering Brain Cells Since 2010
Wrecked is offline
cank Likes This 
Reply With Quote
Old 10-31-2013, 02:04 AM   #2
whoaru99
Feedback Score: 0 reviews
Recipes 
 
Join Date: Oct 2012
Posts: 1,644
Liked 129 Times on 106 Posts
Likes Given: 17

Default

The two supply/incoming "hot" wires go to those two big screw lugs on the left and right sides of the cross, so to speak. The two hot wires to the load go to the screw lugs on the bottom of the breakers.


__________________
Drinking: Nuttin'... ran out of home brew..
Primary: Scottish Wee Heavy
Primary: Craptastic Cream Ale
whoaru99 is offline
 
Reply With Quote
Old 10-31-2013, 02:10 AM   #3
Wrecked
Feedback Score: 0 reviews
Recipes 
 
Join Date: Apr 2010
Location: West Texas
Posts: 112
Liked 3 Times on 3 Posts
Likes Given: 5

Default

Quote:
Originally Posted by whoaru99
The two supply/incoming "hot" wires go to those two big screw lugs on the left and right sides of the cross, so to speak. The two hot wires to the load go to the screw lugs on the bottom of the breakers.
I knew it was gonna be simple like that! I swear the schematic was like reading Greek for me. Thanks whoaru99!
__________________
Blind Pirate Brewing Co.
Plundering Brain Cells Since 2010
Wrecked is offline
 
Reply With Quote
Old 10-31-2013, 02:24 AM   #4
ryan_george
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
Recipes 
 
Join Date: Jul 2009
Location: Fergus, Ontario
Posts: 232
Liked 21 Times on 15 Posts
Likes Given: 6

Default

It's usually safe to assume that the "line in" terminals will be permanently mounted to the enclosure, where the "line outs" will be off of the breakers.
ryan_george is offline
noremorse1 Likes This 
Reply With Quote
Old 10-31-2013, 11:25 AM   #5
raouliii
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
raouliii's Avatar
Recipes 
 
Join Date: Aug 2011
Location: Ponchatoula, LA
Posts: 872
Liked 78 Times on 70 Posts
Likes Given: 128

Default

And the load neutral should attach to the lug on the breaker, not the neutral bus bar in the upper right.
__________________
On Tap:
Second Amendment Amber
Nada
Ponchy Pale Ale - Falconer's Flight
NippleRub Ultra

In the Chamber:
Rearranger IPA

Next Up:
NippleRub Ultra (Light Lager w/Mexican Lager yeast)
raouliii is offline
stlbeer Likes This 
Reply With Quote
Old 10-31-2013, 06:47 PM   #6
Wrecked
Feedback Score: 0 reviews
Recipes 
 
Join Date: Apr 2010
Location: West Texas
Posts: 112
Liked 3 Times on 3 Posts
Likes Given: 5

Default

Quote:
Originally Posted by raouliii
And the load neutral should attach to the lug on the breaker, not the neutral bus bar in the upper right.
Yep, found this out the hard way. Kudos to Dennis at High Gravity for walking me through it.
__________________
Blind Pirate Brewing Co.
Plundering Brain Cells Since 2010
Wrecked is offline
 
Reply With Quote
Old 11-02-2013, 11:45 PM   #7
cank
HBT_LIFETIMESUPPORTER.png
Feedback Score: 4 reviews
Recipes 
 
Join Date: Nov 2012
Location: Jonesboro, Arkansas
Posts: 558
Liked 35 Times on 31 Posts
Likes Given: 18

Default

Wrecked:
At least you asked. I wasn't thinking and wired it backwards (line-in to terminals on the bottom of the breaker and the load cord to my panel off of the spa panel lugs.
Somehow it all worked but when I went to test the GFCI, I fried it and let out the magic smoke...

Once I wired it up correctly the same breaker functions but not as GFCI. Now I need to figure out if I want to replace the breaker or just get another spa panel.


cank is online now
 
Reply With Quote
Reply


Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
Spa Panel Wiring chrismac676 Electric Brewing 4 09-23-2012 04:02 PM
control panel - how's my wiring? NoCornOrRice Electric Brewing 8 12-23-2011 09:55 PM
panel to spa panel wiring buffalobrewer Electric Brewing 4 11-28-2010 11:06 PM
Spa Panel with GFI Wiring interplexr Brew Stands 11 09-12-2010 05:01 PM
Control panel wiring help NinjaJoe Brew Stands 6 03-26-2010 02:58 AM


Forum Jump

Newest Threads

LATEST SPONSOR DEALS