Default Some questions about going electric

Hello all,

Im finally getting back into brewing after a year long hiatus and Id like to retire the propane burner and switch to electric brewing. Were installing a new water heater this weekend and I thought it might be a good time to also rough-in the required power cable from the main breaker panel to the new brewery location.

Which brings me to my questions:

Is 10/3 cable the most common type of cable that will cover most electric brewing needs?

Our main electric panel does have enough room for a 30-amp GFCI breaker but is there any benefit to installing a sub-panel for the brewery instead? I know some people install sub-panels because there is no room in the main breaker panel but Im curious if there are other good reasons for using a sub-panel.

My brewery is very basic. I plan to use my existing 10-gallon boil kettle with a 4500 watt (or lower) ULWD heating element and maybe a pump or two. I brew BIAB so I wont need dual heating elements for a boil kettle + mash tun, etc.

I know I still have a lot of research to do on this but was hoping to at least get a cable run from the breaker box to the brewery while we have the basement all torn up for the water heater installation. I wont attach the brewery cable to the breaker panel or install any receptacles until Ive had a chance to research these items more.

Thanks!


Seven is offline
 
Reply With Quote
Old 09-29-2013, 07:31 PM   #2
Bobby_M
Vendor and Brewer
HBT_SPONSOR.png
Vendor Ads 
Feedback Score: 4 reviews
 
Bobby_M's Avatar
Recipes 
 
Join Date: Aug 2006
Location: Whitehouse Station, NJ
Posts: 22,821
Liked 1340 Times on 878 Posts
Likes Given: 35

Default

Price out a 30a GFCI breaker for your panel and compare that against a regular 2pole 30a +$50 (the cost of a spa panel with GFCI installed). Most of the time, the spa panel is cheaper. You want to run 10/4 to your brew area if you plan to tap off it for any 120v components. If not, you'll have to run pumps and other stuff off another 120v circuit nearby. In other words, you'll need a neutral conductor for 120v.


__________________
Welcome to BrewHardware.com. I love you.
New 100% Stainless Steel Heating Elements are IN! ULWD 5500w Ripple, 2000w, 1500w, etc
Chugger Pumps, Pump Kits, Camlocks, Sightglasses, Clear USA made Silicone Tubing, RIMS, Electric Install Parts, etc.
Bobby_M is offline
 
Reply With Quote
Old 09-29-2013, 09:28 PM   #3
jesserizzo
Feedback Score: 0 reviews
Recipes 
 
Join Date: Jun 2012
Location: Kansas City, Missouri
Posts: 87
Liked 12 Times on 10 Posts
Likes Given: 2

Default

Definitely do 10/4 cable (usually labeled as 10/3 with ground). The price difference is almost non-existent, and then you'll have that extra conductor there if you decide you want it.
jesserizzo is offline
 
Reply With Quote
Old 09-29-2013, 09:40 PM   #4
AnOldUR
fer-men-TAY-shuhn
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
 
AnOldUR's Avatar
Recipes 
 
Join Date: Mar 2007
Location: New Jersey
Posts: 6,816
Liked 764 Times on 558 Posts
Likes Given: 621

Default

Brewing (and drinking) so can't (won't) look for link, but saw something recently about running 10-3 to a dryer outlet from a spa panel and using the ground as the neutral past the spa panel being good.

__________________
Sent from my POS computer because I refuse to own a smartphone!
AnOldUR is offline
 
Reply With Quote
Old 09-29-2013, 11:21 PM   #5
jeffmeh
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
jeffmeh's Avatar
Recipes 
 
Join Date: Feb 2009
Posts: 2,021
Liked 180 Times on 153 Posts
Likes Given: 24

Default

Quote:
Originally Posted by AnOldUR View Post
Brewing (and drinking) so can't (won't) look for link, but saw something recently about running 10-3 to a dryer outlet from a spa panel and using the ground as the neutral past the spa panel being good.

Yes, you can do that, but you don't really have a true ground. It's a good solution if you are working with an existing H-H-N dryer outlet, but if you have an opportunity to provide H-H-N-G all the way from the breaker panel that is a far better solution. We have actually beaten this to death, lol.
jeffmeh is offline
 
Reply With Quote
Old 09-30-2013, 03:47 PM   #6
Seven
Feedback Score: 0 reviews
Recipes 
 
Join Date: Jan 2011
Location: Pittsburgh, PA
Posts: 1,540
Liked 156 Times on 79 Posts
Likes Given: 112

Default

I'll get 10/4 cable (3 plus ground) next time I'm at the hardware store. I also checked breaker prices at Home Depot and the 30 amp GFCI breakers are around $80 each... so that might be why some people choose to install spa panels that already have GFCI included.

Thanks for the info everyone. I'm sure I'll have more questions as the new e-brewery build progresses...
Seven is offline
 
Reply With Quote
Old 09-30-2013, 09:03 PM   #7
kal
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
kal's Avatar
Recipes 
 
Join Date: Nov 2006
Location: Ottawa, Canada
Posts: 2,306
Liked 254 Times on 172 Posts
Likes Given: 6

Default

If you're pulling wire for the brewery outlet, you may want to consider pulling 6/4 instead of 10/4 in case you ever want to upgrade to larger batches and use a 50A control panel (ie: run two elements at once as is commonly done).

This is what I did. I pulled 6/4 (50A) to my brewery but then installed a 30A breaker and a 30A wall receptacle because my control panel is 30A.

The price difference between 6/4 and 10/4 is negligible when you consider everything else you're going to pay for.

Kal
kal is offline
 
Reply With Quote
Old 10-01-2013, 02:34 PM   #8
Seven
Feedback Score: 0 reviews
Recipes 
 
Join Date: Jan 2011
Location: Pittsburgh, PA
Posts: 1,540
Liked 156 Times on 79 Posts
Likes Given: 112

Default

@Kal

Thanks for the suggestion. I'll check on 6/4 cable when I'm at the hardware store.
Seven is offline
 
Reply With Quote
Old 11-23-2014, 10:22 PM   #9
Seven
Feedback Score: 0 reviews
Recipes 
 
Join Date: Jan 2011
Location: Pittsburgh, PA
Posts: 1,540
Liked 156 Times on 79 Posts
Likes Given: 112

Default

So lets say that I wanted to pick up this project again after 13 months of delays...

Is this the correct cable to run in my basement from the main electrical service panel to the planned brewing area? I do like the idea of running the 6/3 cable to allow for future growth.

6-3 Indoor Non-Metallic Jacket Wire (with ground)

With this breaker for my main service panel?

Murray 50-Amp Ground Fault Circuit Breaker
Seven is offline
 
Reply With Quote
Old 11-23-2014, 10:36 PM   #10
bbohanon
Feedback Score: 0 reviews
Recipes 
 
Join Date: Jul 2013
Posts: 475
Liked 115 Times on 85 Posts
Likes Given: 15

Default

Quote:
Originally Posted by kal View Post
If you're pulling wire for the brewery outlet, you may want to consider pulling 6/4 instead of 10/4 in case you ever want to upgrade to larger batches and use a 50A control panel (ie: run two elements at once as is commonly done).

This is what I did. I pulled 6/4 (50A) to my brewery but then installed a 30A breaker and a 30A wall receptacle because my control panel is 30A.

The price difference between 6/4 and 10/4 is negligible when you consider everything else you're going to pay for.

Kal
This +100..

I ran a 6/4(Its actually 6/3 plus a ground wire) 50amp 240v feeder to my brew shed as well as I plan on making darn sure I am putting that feeder cable in and I am digging that trench only ONCE with plenty of power for anything I need to use for brewing, heat and A/C, computer, TV , etc. power-wise. Better to be ready for anything rather than regretting not running enough power when you started out.


bbohanon is offline
 
Reply With Quote
Reply


Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
Questions for Electric Build NathanSPowell Brew Stands 0 11-18-2012 04:31 PM
Electric HLT questions wilfonzo Electric Brewing 6 02-13-2012 07:26 PM
electric brewing questions??? Schnitzengiggle Brew Stands 5 03-17-2010 01:34 AM
Electric HLT questions nostalgia Equipment/Sanitation 32 01-27-2010 02:51 AM
Electric MLT & HLT questions missing link Equipment/Sanitation 4 01-16-2008 10:41 PM


Forum Jump

Newest Threads

LATEST SPONSOR DEALS