I know there is a lot of information out there and I have tried to read as much as possible as I can as I have formulated my plan to convert my current keggle (serves as both HLT and boil kettle) into an electric kettle.

I am currently renting and will be for the foreseeable future so I have decided to go with the spa panel approach since I will be able to take it with me. My basement has an older 3 prong dryer on a non-GFCI 30A breaker. My plan is to run 10/3 soow from the dryer outlet to the spa panel to put my brewing operation under GFCI protection. From there, I'm still deciding on what kind of controller to use (its going to be simple) to control the element. I'm going to be buying the 5500W element kit from the electric brewery.

Can anyone see any fatal flaws in my plan to plug my spa panel into the existing dryer outlet and then plug in the controller/element into an outlet I will put in the panel as many others have.

As far as the pump goes, I'm not worried about that because I have an outdoor GFCI plug that is part of the townhouse for that.

Thanks for taking the time to tell me this won't work or it sounds reasonable.

 
Reply With Quote
Old 09-26-2013, 11:45 AM   #2
BadNewsBrewery
 
BadNewsBrewery's Avatar
Recipes 
 
Oct 2012
Severn, MD
Posts: 1,244
Liked 129 Times on 103 Posts


Your plan is solid so long as you only run 240v - don't try to dual run 120/240 as you need a 4 wire dryer plug to safely / properly do that.
__________________
Building a Bad News Brewery - eHERMS

2014 - 70gal
2015 - 72gal

2
People Like This 
Reply With Quote
Old 09-26-2013, 06:06 PM   #3
TheBrewinator
HBT_SUPPORTER.png
Recipes 
 
Nov 2010
Milwaukee, WI
Posts: 294
Liked 15 Times on 11 Posts


Thanks for the reply. So if I have read correctly I will have a H + H + N coming from my dryer outlet to the panel and I'd just install a 3 prong plug post-breaker using only those three instead of adding the 4th wire like in the spa panel wiring for dummies thread?

 
Reply With Quote
Old 09-28-2013, 01:34 PM   #4
dcbw
HBT_LIFETIMESUPPORTER.png
Recipes 
 
Feb 2012
Minneapolis, MN
Posts: 285
Liked 29 Times on 24 Posts


You kinda need a ground. Otherwise the spa panel won't do it's job and you will die. Did you have a plan on how the control panel and spa panel would get grounded if you're only running 10/3 from the dryer outlet? You might want to double check what is coming out of the dryer to see whether you're missing the ground or the neutral. Missing ground can kill you. Missing neutral will make the Electric Brewery control panel not work.

passedpawn Likes This 
Reply With Quote
Old 09-28-2013, 01:38 PM   #5
Black
Recipes 
 
Dec 2012
Jonquiere, Canada
Posts: 157
Liked 12 Times on 11 Posts


I don't know if your PIDS can work on 240 volts. I think mine do. However, your pumps will have to be connected to a 120 volts outlet somewhere else if you can't have a neutral wire in your dryer outlet. But you got a fix for that. That's about the only problem I see with having only H H GND in the outlet.

Also, your main relay will need to have a 240 volts coil. Check for that as some of them are 120volts.

If you have any questions on the wiring, PM me it will be a pleasure to help you out !

Cheers !


Black

 
Reply With Quote
Old 09-28-2013, 02:09 PM   #6
P-J
HBT_LIFETIMESUPPORTER.png
Recipes 
 
Mar 2010
Charlotte, NC
Posts: 3,336
Liked 302 Times on 235 Posts


Quote:
Originally Posted by BadNewsBrewery View Post
Your plan is solid so long as you only run 240v - don't try to dual run 120/240 as you need a 4 wire dryer plug to safely / properly do that.
Sorry but your statement is not accurate. Clothes dryers set up with a 3 prong (3 wire) power cord are being supplied with the 240V hot legs and neutral. The dryer contains both 240V and 120V devices within it. When the dryer is setup the neutral line is additionally bonded to the dryer frame to provide equipment ground.

The use of the spa panel provides a method to supply GFCI protected power to the brewery.

No problem.

atoughram Likes This 
Reply With Quote
Old 09-28-2013, 03:26 PM   #7
TheBrewinator
HBT_SUPPORTER.png
Recipes 
 
Nov 2010
Milwaukee, WI
Posts: 294
Liked 15 Times on 11 Posts


I'm just trying to figure out how to GFCI protect a 240v line to power the element. I will not be buying a control panel, just the element kit. My pump is plugging into a separate outlet that I have on my patio already. I guess I'll either just stick with propane and hope the association doesn't have a fit or drop 200 bucks or so on an industrial 30A 240v GFCI extension cord and plug my element into that.

Thanks for the replies all, I really appreciate the help.

Edit: To further illustrate what I'm trying to do, here is a picture of the "rig" I built before I moved and had to put brewing on hold. I took an old AV cart (the kind that teachers used to push overhead projectors on back before schools got all this fancy technology), cut a hole in it for my burner since I was set up for propane. This cart conveniently has a cord and outlets that will plug into an outdoor 120v 15A GFCI outlet on my patio that will protect anything I plug into it (namely my chugger pump and any possible controller to control power to the element).
Click image for larger version

Name:	IMAG0184 (2).jpg
Views:	517
Size:	327.9 KB
ID:	150812  

 
Reply With Quote
Old 10-01-2013, 11:23 AM   #8
BadNewsBrewery
 
BadNewsBrewery's Avatar
Recipes 
 
Oct 2012
Severn, MD
Posts: 1,244
Liked 129 Times on 103 Posts


Quote:
Originally Posted by P-J View Post
Sorry but your statement is not accurate. Clothes dryers set up with a 3 prong (3 wire) power cord are being supplied with the 240V hot legs and neutral. The dryer contains both 240V and 120V devices within it. When the dryer is setup the neutral line is additionally bonded to the dryer frame to provide equipment ground.

The use of the spa panel provides a method to supply GFCI protected power to the brewery.

No problem.
My point is that he COULD do it, but the safest / current code method would be to have a dedicated ground which would require a 4 wire setup. There are plenty of ways to make it work, but wouldn't the safest / 'proper-est' way to do it require a dedicated ground and not a shared ground/neutral?
__________________
Building a Bad News Brewery - eHERMS

2014 - 70gal
2015 - 72gal

raouliii Likes This 
Reply With Quote
Old 10-01-2013, 02:54 PM   #9
TheBrewinator
HBT_SUPPORTER.png
Recipes 
 
Nov 2010
Milwaukee, WI
Posts: 294
Liked 15 Times on 11 Posts


With all the 3 wire vs 4 wire, here is a simple question. Would something like this put in line from the dryer outlet to the element work?

http://www.ebay.com/itm/Inline-GFCI-...item4ac918f396

 
Reply With Quote
Old 10-01-2013, 04:10 PM   #10
The10mmKid
 
The10mmKid's Avatar
Recipes 
 
Jul 2013
Home of the Wright Brothers
Posts: 842
Liked 101 Times on 74 Posts


OP, you will be fine with your plan.

GFCI protection DOES NOT REQUIRE A GROUND . . . . . period.

The device works by comparing current flow among the monitored lines.
If ~5mA comes up missing, it will trip.

Everyone is needlessly worrying about the grounds . . . . . .

Use your GFCI and test it monthly as is instructed; but rarely complied with.

'da Kid

 
Reply With Quote
Reply
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
Why switch to electric? Islandboy85 Electric Brewing 35 01-12-2012 03:53 AM
Time To Switch To Electric ?'s Ki-ri-n Electric Brewing 3 05-12-2011 11:31 PM
Electric HLT planning help tnbrewer371 Electric Brewing 9 03-25-2011 03:09 AM
The Electric Brewery switch question milldoggy Electric Brewing 1 12-20-2010 09:05 PM
Wiring of a 2 pole switch in an electric HLT bf514921 Kettles, Mash Tuns & Hot Liquor Tanks 6 02-19-2010 02:47 AM


Forum Jump