Old 07-14-2013, 02:48 AM   #1
Mojzis
Recipes 
 
Jan 2012
Rochester, NY
Posts: 1,269
Liked 152 Times on 107 Posts



Hi everyone. I would like to ask the experts some questions. I'm not very knowledgeable of wiring besides some basic lighting and outlets.

I purchased a DIY controller for my 240v 5500 camco element. It consists of a potentiometer, SS relay, aluminum heat sink and box. I bought 15ft of water resistant 10/3 wire (same as listed on the electric brewery). I want to make a simple controller to keep the boil regulated.

I found a diagram online and wired it up. I'll attach pictures in another post. I rent so I don't have the ability to install a 240v outlet. Instead I'm hoping to use the dryer outlet which is 240. I picked up a plug to fit the dryer outlet but I ran into an issue. The wire I bought has a white, black and green which I believe are two hots and a ground. The dryer outlet has a red, black and white. Red and black are hot and white is neutral?

Am I out of luck? Or can I still use this outlet?

Thanks in advance.

 
Reply With Quote
Old 07-14-2013, 02:55 AM   #2
Mojzis
Recipes 
 
Jan 2012
Rochester, NY
Posts: 1,269
Liked 152 Times on 107 Posts


Click image for larger version

Name:	image-840744971.jpg
Views:	231
Size:	41.3 KB
ID:	134988



Click image for larger version

Name:	image-3533052412.jpg
Views:	234
Size:	41.4 KB
ID:	134989



Click image for larger version

Name:	image-3468150368.jpg
Views:	232
Size:	47.1 KB
ID:	134990





P.s- did I wire this up right?

 
Reply With Quote
Old 07-14-2013, 03:27 AM   #3
stlbeer
Senior Member
HBT_SUPPORTER.png
 
stlbeer's Avatar
Recipes 
 
Jan 2008
Fenton, MO
Posts: 1,013
Liked 46 Times on 45 Posts


Use a multimeter to properly determine which wire is which. In 220v only there is no neutral. Most likely black and red are the 2 legs of 110v and the white is ground. Confirm this by looking at the breaker panel and using a multimeter.
__________________
My RIMS eBrewery build

 
Reply With Quote
Old 07-14-2013, 03:45 AM   #4
sils13
Recipes 
 
Jul 2010
Cedar Rapids, IA
Posts: 144
Liked 8 Times on 6 Posts


if im looking at that rite you need to double check it. for 220 you need both legs there is no neutral. its just a 3 wire system to hots and a ground if your ssr is like any of the other ones ive seen you have your neutral hooked up to the input to acually switch the ssr it wont hurt anything it just wont work check out theelectricbrewery.com and do some really good reading it will be extremely helpfull and be carefull 220 doesnt like to let go of you if u get caught up in it. good luck and be safe.

 
Reply With Quote
Old 07-14-2013, 07:40 AM   #5
jeffmeh
HBT_SUPPORTER.png
 
jeffmeh's Avatar
Recipes 
 
Feb 2009
Posts: 2,160
Liked 211 Times on 181 Posts


If it is an older dryer outlet it is most likely wired with H-H-N, as you described, and the N is bonded to the dryer chassis. This is no longer allowed, but existing work is grandfathered in.

You should definitely ground your brewery panel and have a GFCI, and the easiest way to do it is with a GFCI spa panel bringing in H-H-N and bringing out H-H-N-G. There have been many heated discussions around this approach, but it certainly works and is far better than no GFCI at all. http://www.homebrewtalk.com/f170/3-w...-again-372667/

 
Reply With Quote
Old 07-15-2013, 03:51 PM   #6
Mojzis
Recipes 
 
Jan 2012
Rochester, NY
Posts: 1,269
Liked 152 Times on 107 Posts


Thanks everyone. I'll look into checking the outlet to see which is which as far as hots/ground. As far as grounding the panel, I don't have a panel. It's just a small plastic box with the SSR in it. The way I have it wired up is that the aluminum sink and kettle will be grounded. I don't have a gfci available and won't be able to install one just yet. I was hoping to make use of the dryer/stove outlets for a little while as I don't have a permanent or eve semi permanent residence. When permanent residence is acquired i'll install the better outlet, plug, etc.

 
Reply With Quote
Old 07-15-2013, 04:00 PM   #7
jeffmeh
HBT_SUPPORTER.png
 
jeffmeh's Avatar
Recipes 
 
Feb 2009
Posts: 2,160
Liked 211 Times on 181 Posts


Quote:
Originally Posted by Mojzis View Post
Thanks everyone. I'll look into checking the outlet to see which is which as far as hots/ground. As far as grounding the panel, I don't have a panel. It's just a small plastic box with the SSR in it. The way I have it wired up is that the aluminum sink and kettle will be grounded. I don't have a gfci available and won't be able to install one just yet. I was hoping to make use of the dryer/stove outlets for a little while as I don't have a permanent or eve semi permanent residence. When permanent residence is acquired i'll install the better outlet, plug, etc.
I strongly urge you to incorporate a GFCI as a critical safety feature. It is likely that a GFCI spa panel will not only protect your life, but will also solve your neutral vs. ground problems.

 
Reply With Quote
Old 07-15-2013, 04:08 PM   #8
Mojzis
Recipes 
 
Jan 2012
Rochester, NY
Posts: 1,269
Liked 152 Times on 107 Posts


Do you have a link for a build or a how-to with parts?

 
Reply With Quote
Old 07-15-2013, 04:41 PM   #9
Lopsy
Recipes 
 
Mar 2013
Posts: 94
Liked 11 Times on 9 Posts


GFCI is not an option.


Install it or don't brew electric.

2
People Like This 
Reply With Quote
Old 07-15-2013, 04:46 PM   #10
Mojzis
Recipes 
 
Jan 2012
Rochester, NY
Posts: 1,269
Liked 152 Times on 107 Posts


Quote:
Originally Posted by Lopsy View Post
GFCI is not an option.


Install it or don't brew electric.
It was already stated that I should use a spa panel with GFCI incorporated. I am seeking assistance on how to do this.

If you have nothing new, helpful or constructive to add please refrain from commenting. Thanks.

 
Reply With Quote
Reply
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help Wiring 240V Heating Element rack04 Electric Brewing 23 08-15-2012 11:45 AM
240v LED wiring - need fuses/resistors? DustBow Electric Brewing 4 07-14-2012 12:47 AM
Ranco wiring 240V beer_master Brew Stands 4 07-04-2011 12:27 PM
wiring a 240V heater to a Kettle CanadianNorth Electric Brewing 9 03-31-2011 11:01 PM
Need 240v Wiring Confirmation lustrum Brew Stands 5 09-13-2010 12:54 PM


Forum Jump