Hi, I have been using my electric 5500w herms rig at home for a year now. It has been working flawlessly. My boss said I could brew at work but they have three phase power there. I guess when you split the power the outlet only gets 208 volts. I know my elements will have less power, but will it slow the pumps or have any other issues? Will the contactors with a 120v coil still latch with 104 volts? I kinda want to know if it will still function the same or will there be problems? Thanks
__________________
Quote:
Originally Posted by Bobby_M View Post
Simcoe smells like 10 cats pissing on a pine tree. It's awesome.

 
Reply With Quote
Old 06-21-2013, 02:41 AM   #2
P-J
HBT_LIFETIMESUPPORTER.png
Recipes 
 
Mar 2010
Charlotte, NC
Posts: 3,337
Liked 301 Times on 235 Posts


With 3 phase power delivered in a Y configuration (208V) the power for 120 volt devices is 120V. Here is an illlustration.


 
Reply With Quote
Old 06-21-2013, 02:51 AM   #3
fbold1
Brew Nut
HBT_SUPPORTER.png
 
fbold1's Avatar
Recipes 
 
Dec 2011
North Coast, Ohio
Posts: 259
Liked 8 Times on 8 Posts


I don't think it will be a problem. It may draw slightly higher current, but it will still be less than 30 amps. Wish I could brew at work, that sounds like you'll be sharing a lot of brew.
__________________
"Whoever makes a poor beer is transferred to the dung-hill." Edict in the City of Danzig, 11th Century.

 
Reply With Quote
Old 06-21-2013, 03:32 AM   #4
JRems
Recipes 
 
Nov 2010
Mahopac, NY
Posts: 2,221
Liked 60 Times on 52 Posts


Quote:
Originally Posted by P-J View Post
With 3 phase power delivered in a Y configuration (208V) the power for 120 volt devices is 120V. Here is an illlustration.

Thanks p-j. I built my panel with your diagram. 3 phase still confuses me. Your diagram looks like a flux capaitor. 120+120=240. I still don't understand where the 208 comes from. As long as it work I don't care.
__________________
Quote:
Originally Posted by Bobby_M View Post
Simcoe smells like 10 cats pissing on a pine tree. It's awesome.

 
Reply With Quote
Old 06-21-2013, 03:37 AM   #5
passedpawn
Waste Allocation Load Lifter - Earth Class
HBT_ADMIN.png
 
passedpawn's Avatar
Recipes 
 
Apr 2009
☼ Clearwater, FL ☼
Posts: 25,852
Liked 6694 Times on 3957 Posts


Quote:
Originally Posted by JRems View Post
Thanks p-j. I built my panel with your diagram. 3 phase still confuses me. Your diagram looks like a flux capaitor. 120+120=240. I still don't understand where the 208 comes from. As long as it work I don't care.
240V*sin(360/3)
__________________
- Andrew

 
Reply With Quote
Old 06-21-2013, 03:46 AM   #6
Stauffbier
HBT_SUPPORTER.png
 
Stauffbier's Avatar
Recipes 
 
Nov 2011
El Paso, TX
Posts: 5,122
Liked 1048 Times on 641 Posts


I don't use 3 phase very often, but I do work with 240V all the time at work. We have a 30 amp, 240V floor sanding machine. I can tell you that every house I work in is different. Voltage ranges from as low as 205V up to 245V and everything in between. My machinery always runs the same in any of those scenarios. I can only assume that your brewing equipment would react the same way. Just my 2 cents....
__________________
Bier war sein letztes wort dann trugen ihn die Englein fort...


 
Reply With Quote
Old 06-21-2013, 09:51 AM   #7
danb35
Recipes 
 
May 2012
Hartsville, SC
Posts: 131
Liked 20 Times on 14 Posts


Quote:
Originally Posted by fbold1 View Post
I don't think it will be a problem. It may draw slightly higher current, but it will still be less than 30 amps.
No, the current draw will be less. The heating element is a purely resistive device. With a resistive circuit, the current draw will be directly proportional to the voltage, and the power consumption will be directly proportional to the square of the voltage. A 240V, 5500W element will output 5500 * (208^2 / 240^2) = 4131 watts with 208 volts input.

 
Reply With Quote
Old 06-21-2013, 10:11 AM   #8
fbold1
Brew Nut
HBT_SUPPORTER.png
 
fbold1's Avatar
Recipes 
 
Dec 2011
North Coast, Ohio
Posts: 259
Liked 8 Times on 8 Posts


Quote:
Originally Posted by danb35 View Post
No, the current draw will be less. The heating element is a purely resistive device. With a resistive circuit, the current draw will be directly proportional to the voltage, and the power consumption will be directly proportional to the square of the voltage. A 240V, 5500W element will output 5500 * (208^2 / 240^2) = 4131 watts with 208 volts input.
Yep, your right, when working with resistive loads compare it to a light bulb, lowering the voltage will result in a dimmer bulb, which means lower efficiency for the heater at 208. Too many years working with motors.
__________________
"Whoever makes a poor beer is transferred to the dung-hill." Edict in the City of Danzig, 11th Century.

 
Reply With Quote
Old 06-21-2013, 12:00 PM   #9
mattd2
Recipes 
 
Sep 2009
Papamoa, New Zealand
Posts: 3,723
Liked 307 Times on 245 Posts


Quote:
Originally Posted by danb35 View Post
No, the current draw will be less. The heating element is a purely resistive device. With a resistive circuit, the current draw will be directly proportional to the voltage, and the power consumption will be directly proportional to the square of the voltage. A 240V, 5500W element will output 5500 * (208^2 / 240^2) = 4131 watts with 208 volts input.
Quote:
Originally Posted by fbold1 View Post
Yep, your right, when working with resistive loads compare it to a light bulb, lowering the voltage will result in a dimmer bulb, which means lower efficiency for the heater at 208. Too many years working with motors.
Thinking about the pumps though, I thought current draw for an inductive load goes up with decreased voltage? The pumps may run hotter but I wouldn't think a small decrease in voltage would be a big issue.
I'll wait to be corrected now

 
Reply With Quote
Old 06-21-2013, 12:08 PM   #10
reynolds5520
HBT_LIFETIMESUPPORTER.png
Recipes 
 
Jan 2010
Western Fingerlakes NY
Posts: 294
Liked 42 Times on 32 Posts


Quote:
Originally Posted by mattd2 View Post
Thinking about the pumps though, I thought current draw for an inductive load goes up with decreased voltage? The pumps may run hotter but I wouldn't think a small decrease in voltage would be a big issue.
I'll wait to be corrected now

The pumps won't see a decreased voltage. They will still be on 120V. From any leg of the three phase service to neutral is 120V.

 
Reply With Quote


Reply
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
240V HLT with PID- Need Help!!!! TahoeRy Electric Brewing 13 12-18-2012 01:10 AM
Can you use L16-30P with 240V ekjohns Electric Brewing 0 09-10-2012 01:46 AM
Auber 40A 240v Contactor - 240v Coil TheAleMaster For Sale 0 08-12-2012 05:10 PM
Strange issue with 240v legs. 120v on both, no 240v Brewmoor Electric Brewing 5 12-03-2010 07:15 PM
3 Pos 240v Switch illin8 Brew Stands 8 05-20-2009 02:07 AM


Forum Jump