Are these e-stop buttons NO or NC? Can someone explain to me the concept?

From what I am thinking is that I would use a normally open contact, and when pressed it lets current leak out the ground, therefore tripping the GFCI in the panel. Or am I completely off base here?


smoothlarryhughes is offline
 
Reply With Quote
Old 06-16-2013, 07:50 PM   #12
P-J
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
Recipes 
 
Join Date: Mar 2010
Location: Charlotte, NC
Posts: 3,335
Liked 294 Times on 231 Posts
Likes Given: 496

Default

Quote:
Originally Posted by smoothlarryhughes View Post
Are these e-stop buttons NO or NC? Can someone explain to me the concept?

From what I am thinking is that I would use a normally open contact, and when pressed it lets current leak out the ground, therefore tripping the GFCI in the panel. Or am I completely off base here?
You have it exactly correct.!


P-J is offline
 
Reply With Quote
Old 06-16-2013, 08:28 PM   #13
jeffmeh
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
jeffmeh's Avatar
Recipes 
 
Join Date: Feb 2009
Posts: 2,021
Liked 180 Times on 153 Posts
Likes Given: 24

Default

So the implication here is that for the e-stop, "normal" means "button up" and "not-normal" means "button down," yes? That would be consistent with a push-button, but a bit counterintuitive to me, as "activated" state implies to me "not normal." Incidentally, Automation Direct sells this illuminated e-stop http://www.automationdirect.com/adc/...d/GCX3226-120L that only includes a NC contact block, which only confuses me further.

Do I have it right in the first sentence? Am I missing something here? Thanks.
jeffmeh is offline
 
Reply With Quote
Old 06-16-2013, 09:20 PM   #14
P-J
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
Recipes 
 
Join Date: Mar 2010
Location: Charlotte, NC
Posts: 3,335
Liked 294 Times on 231 Posts
Likes Given: 496

Default

Quote:
Originally Posted by jeffmeh View Post
So the implication here is that for the e-stop, "normal" means "button up" and "not-normal" means "button down," yes? That would be consistent with a push-button, but a bit counterintuitive to me, as "activated" state implies to me "not normal." Incidentally, Automation Direct sells this illuminated e-stop http://www.automationdirect.com/adc/...d/GCX3226-120L that only includes a NC contact block, which only confuses me further.

Do I have it right in the first sentence? Am I missing something here? Thanks.
???

What?

A N/O switch has a open contact when NOT activated.!

Illuminated? What to Hell for????

Confused... You betcha...
P-J is offline
 
Reply With Quote
Old 06-16-2013, 11:27 PM   #15
jeffmeh
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
jeffmeh's Avatar
Recipes 
 
Join Date: Feb 2009
Posts: 2,021
Liked 180 Times on 153 Posts
Likes Given: 24

Default

So a NO pushbutton switch is open when the button is up, and closed when the button is down (activated).

A NO e-stop is open when the button is down, and closed when the button is up (activated)? So "normal" in the case of the e-stop is "button down," while "normal" in the case of the pushbutton is "button up?"

Yes, I was quite confused, but the illumination is a red herring.
jeffmeh is offline
 
Reply With Quote
Old 06-16-2013, 11:58 PM   #16
P-J
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
Recipes 
 
Join Date: Mar 2010
Location: Charlotte, NC
Posts: 3,335
Liked 294 Times on 231 Posts
Likes Given: 496

Default

Quote:
Originally Posted by jeffmeh View Post
So a NO pushbutton switch is open when the button is up, and closed when the button is down (activated).

A NO e-stop is open when the button is down, and closed when the button is up (activated)? So "normal" in the case of the e-stop is "button down," while "normal" in the case of the pushbutton is "button up?"

Yes, I was quite confused, but the illumination is a red herring.
Sorry. Your logic is twisted..

N/O = contact is open when the switch is at rest.

N/C = contact is closed when the switch is at rest (not - activated). (I just edited my error - thanks Kevin)

An illuminated switch for this application significantly complicates the application. Don't go there...
P-J is offline
 
Reply With Quote
Old 06-17-2013, 12:15 PM   #17
BadNewsBrewery
Basement Brewer
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
BadNewsBrewery's Avatar
Recipes 
 
Join Date: Oct 2012
Location: Severn, MD
Posts: 1,245
Liked 128 Times on 102 Posts
Likes Given: 65

Default

Quote:
Originally Posted by jeffmeh View Post
So a NO pushbutton switch is open when the button is up, and closed when the button is down (activated).
Correct.

Quote:
Originally Posted by jeffmeh View Post
A NO e-stop is open when the button is down, and closed when the button is up (activated)? So "normal" in the case of the e-stop is "button down," while "normal" in the case of the pushbutton is "button up?"
False. The NO e-stop is open when the button is up (normal condition for the switch), and closed when you mash the button down (activated). Unless you have some weird push-button switch that when you push it, it goes up. The switch you showed (the illuminated one) has a NC block, so it wouldn't work for the GFCI trip method. You could use that button for the power-flow through to the contactor method - normal condition, power flows through to the contactor coil. Mash the button, the NC block opens, power no longer flows to contactor coil, panel turns off.

Quote:
Originally Posted by jeffmeh View Post
Yes, I was quite confused, but the illumination is a red herring.
As the switch listed only have a NC block, you'd basically have the switch illuminated when normal (not activated), and turned off when activated (pushed down) - you'd have to install a NO block if you wanted to have the light turn on when activated, but if you went with the GFCI flip method, there'd be no power to illuminate the light anyways.

Quote:
Originally Posted by P-J View Post
N/O = contact is open when the switch is at rest.

N/C = contact is closed when the switch is activated.
I think the N/C logic is backwards. N/O is open when switch is at rest (closed when switch is activated). N/C is closed when at rest (open when activated). The description above would be the same switch, which is a N/O contact block.

-Kevin
__________________
Building a Bad News Brewery - eHERMS

2014 - 70gal
2015:
10gal American Pale Ale
5gal Wee Heavy
10gal Irish Red
10gal Hefeweizen
2gal Mead

Keg 1: Apfelwein
Keg 2: Irish Red
Keg 3: Hefeweizen
Fermenting: 1gal Joe's Ancient Orange Mead & 1gal Traditional Mead
BadNewsBrewery is offline
 
Reply With Quote
Old 06-17-2013, 03:00 PM   #18
jeffmeh
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
jeffmeh's Avatar
Recipes 
 
Join Date: Feb 2009
Posts: 2,021
Liked 180 Times on 153 Posts
Likes Given: 24

Default

Thanks Kevin. So according to your definition above, "normal" position for an e-stop is button up. If I use the NC e-stop switch listed to switch a NO, DPST contactor, it would illuminate and close the contactor when the button is up, correct?
jeffmeh is offline
 
Reply With Quote
Old 06-18-2013, 10:30 AM   #19
BadNewsBrewery
Basement Brewer
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
BadNewsBrewery's Avatar
Recipes 
 
Join Date: Oct 2012
Location: Severn, MD
Posts: 1,245
Liked 128 Times on 102 Posts
Likes Given: 65

Default

Quote:
Originally Posted by jeffmeh View Post
Thanks Kevin. So according to your definition above, "normal" position for an e-stop is button up. If I use the NC e-stop switch listed to switch a NO, DPST contactor, it would illuminate and close the contactor when the button is up, correct?
Bingo. Power would flow from your supply via any sort of keyed switch you may or may not use, through the CLOSED switch block (as Normal for an e-stop is 'up' IE not depressed) to your contactor coils. This would in-turn cause your coils to energize, causing the contactor to switch from it's normal at-rest condition of being open, to being a closed and fully functional contactor, thereby allowing the rest of your panel to be powered by your primary supply. In this condition, the e-stop button could also be illuminated.

In this configuration, the EMERGENCY STOP button is not actually being used for any sort of emergency stopping on a regular basis, but is instead simply acting as a large mushroom switch to provide power to your contactor coils. While it goes against the basic fundamentals of using a piece of emergency equipment for routine function, that's more of a SOP issue than an actual functionality issue.

As described above, your panel should function fine.
__________________
Building a Bad News Brewery - eHERMS

2014 - 70gal
2015:
10gal American Pale Ale
5gal Wee Heavy
10gal Irish Red
10gal Hefeweizen
2gal Mead

Keg 1: Apfelwein
Keg 2: Irish Red
Keg 3: Hefeweizen
Fermenting: 1gal Joe's Ancient Orange Mead & 1gal Traditional Mead
BadNewsBrewery is offline
 
Reply With Quote
Old 06-18-2013, 01:24 PM   #20
jeffmeh
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
jeffmeh's Avatar
Recipes 
 
Join Date: Feb 2009
Posts: 2,021
Liked 180 Times on 153 Posts
Likes Given: 24

Default

Thanks again Kevin. My confusion was around which state was considered "normal" for an e-stop. Once knowing that normal is up, all else logically follows.

P.S. One could also consider normal the state of lowest physical energy, i.e., the state the device would fail into, which would be down in the case of a twist-up e-stop. Hence my confusion.



Reason: P.S.
jeffmeh is offline
 
Reply With Quote
Reply


Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
Control Panel PLANNING and BUILD smoothlarryhughes Electric Brewing 24 10-14-2012 04:33 PM
Help with Electric Planning (Spa Panel, Dryer Outlet, Extension Cord) br1dge Electric Brewing 13 01-23-2012 05:00 PM
Electric Control Panel PinupBrewery Electric Brewing 8 05-12-2011 12:41 AM