Default PID Calibration Troubleshooting

Finally have everything wired up, but I am having troubles setting up my PID. I have a 1/16 DIN PID Temperature Controller (SSR control output) (SYL-2352) wired to a Liquid tight RTD sensor, 4 in, 1/4 NPT Thread (PT100-L100NPT). I tired following Kal's PID settings but I get a weird flashing message when I try to accomplish the first step of setting the Sn to 21. It flashes "-343", then "or AL", and then "100". I am pretty positive my 3 wires are wired correctly.

I was hoping someone could help walk me through this as I am lost with this thing!


Chris7687 is offline
 
Reply With Quote
Old 04-30-2013, 01:01 PM   #2
Chris7687
Feedback Score: 0 reviews
Recipes 
 
Join Date: Jan 2012
Location: Palm Beach Gardens, FL
Posts: 485
Liked 11 Times on 9 Posts
Likes Given: 23

Default

Bump


Chris7687 is offline
 
Reply With Quote
Old 04-30-2013, 04:25 PM   #3
kal
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
kal's Avatar
Recipes 
 
Join Date: Nov 2006
Location: Ottawa, Canada
Posts: 2,306
Liked 254 Times on 172 Posts
Likes Given: 6

Default

You likely have an intermittent problem in your wiring, inside the PID, or in the temp probe.

SYL-2352 manual is here:

http://auberins.com/images/Manual/Ma...sion%203.4.pdf

Quote:
8. Error Message and trouble shooting
8.1 Display orAL

This is an input error message. The possible reasons are: the sensor is not
connected correctly; the input setting is wrong type; or the sensor is defective.
In this case, the instrument terminates its control function automatically, and
the output value is fixed according to the parameter OUTL. If this happens
when using thermocouple sensor, you can short terminal 4 and 5 with a copper
wire. If the display shows ambient temperature, the thermocouple is defective.
If it still displays orAL, check the input setting, Sn, to make sure it is set to the
right thermocouple type. If the Sn setting is correct, the controller is defective.
For RTD sensors, check the input setting first because most controllers are
shipped with the input set for thermocouples. Then check the wiring. The two
red wires should be connected to terminals 3 and 4. The clear wire should be
connected to terminal 5.
Use the PID settings outlined here: http://www.theelectricbrewery.com/control-panel-setup

Kal
kal is offline
 
Reply With Quote
Old 05-01-2013, 05:31 PM   #4
Chris7687
Feedback Score: 0 reviews
Recipes 
 
Join Date: Jan 2012
Location: Palm Beach Gardens, FL
Posts: 485
Liked 11 Times on 9 Posts
Likes Given: 23

Default

Had my wires switched on the PID. Thanks for all the great support you have provided Kal. Couldn't have even imagined doing this without the support you provided via your website.
Chris7687 is offline
 
Reply With Quote
Old 05-01-2013, 11:21 PM   #5
Chris7687
Feedback Score: 0 reviews
Recipes 
 
Join Date: Jan 2012
Location: Palm Beach Gardens, FL
Posts: 485
Liked 11 Times on 9 Posts
Likes Given: 23

Default

Kal - During my auto tuning, my PID stopped at 204. It wouldn't go past it even after letting it sit for an hour. I turned it off. Hoping a "reboot" might help it out. Any suggestions? It had a very small boil to it, if you could even call it that. It definitely was nothing I would expect for a 100% rolling boil, so I cdon't think believe 8 degrees off on the pB set could be the issue.
Chris7687 is offline
 
Reply With Quote
Old 05-02-2013, 12:50 AM   #6
kal
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
kal's Avatar
Recipes 
 
Join Date: Nov 2006
Location: Ottawa, Canada
Posts: 2,306
Liked 254 Times on 172 Posts
Likes Given: 6

Default

I'm not entirely sure what you're up to but normally auto-tuning is done in auto-mode on the PID for allowing it to hold temp (usually around mash temp). You wouldn't auto-tune a PID run in manual mode for tuning.

See the Auto-tuning instructions I provide here: http://www.theelectricbrewery.com/control-panel-setup

Kal
kal is offline
 
Reply With Quote
Old 05-02-2013, 11:58 AM   #7
Chris7687
Feedback Score: 0 reviews
Recipes 
 
Join Date: Jan 2012
Location: Palm Beach Gardens, FL
Posts: 485
Liked 11 Times on 9 Posts
Likes Given: 23

Default

Hey Kal, sorry about my post as it was kind of scatter brained. Here is my situation, I am using my kettle in for BIAB. So in essence I am combining all three kettles into one, as I am sure you know this. I went ahead and programmed my PID to your specs for the default settings, but since I am using my kettle to heat up the water all the way to boil I had to combine some of the settings. I made the PID's A-M mode 0, but when I ran the auto-tuning it was in Auto mode. I said 100% because I am assuming when it's in auto mode the element is firing at 100% power. The water at 204 on my PID had a minor boil to it, so what I meant was even if I thought it was stuck at 204 but really it was 212 (miscalculated my pB adjustment) it was still a very weak boil.

I am assuming that either the PID in A-M mode 2 or it just had a brain fart which caused it to stop at 204. I can't get to it again until Monday.
Chris7687 is offline
 
Reply With Quote
Old 05-02-2013, 12:53 PM   #8
kal
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
kal's Avatar
Recipes 
 
Join Date: Nov 2006
Location: Ottawa, Canada
Posts: 2,306
Liked 254 Times on 172 Posts
Likes Given: 6

Default

When the element is on it's always firing at 100% power. A PID can't fire an element at 50% power. It's either on or off.

To control how vigorous a boil is, duty cycle is used in manual mode. This means setting the PID to 50% in manual mode the element will be on at 100% power for 1 second, then complete off for 1 second. The "average" is 50%.

I don't understand why you're at 204F, but just to be sure: Don't do your auto-tune at boiling temperatures. Put the PID into automatic mode, set it to something around mash temp (say 154F), fill the kettle with cold water, start heating, and then start the auto-tune when the temperarature is about 10 degrees below the set point (~144F). It won't go to up to 204F. If it does, something is set wrong or wired wrong.

Good luck!

Kal
kal is offline
stlbeer Likes This 
Reply With Quote
Old 05-02-2013, 03:06 PM   #9
Chris7687
Feedback Score: 0 reviews
Recipes 
 
Join Date: Jan 2012
Location: Palm Beach Gardens, FL
Posts: 485
Liked 11 Times on 9 Posts
Likes Given: 23

Default

Quote:
Originally Posted by kal View Post
I don't understand why you're at 204F, but just to be sure: Don't do your auto-tune at boiling temperatures. Put the PID into automatic mode, set it to something around mash temp (say 154F), fill the kettle with cold water, start heating, and then start the auto-tune when the temperarature is about 10 degrees below the set point (~144F). It won't go to up to 204F. If it does, something is set wrong or wired wrong.
Something must be set wrong (hoping not wired wrong) because I set it to auto tune at 144 and it ran all the way up to 204.
Chris7687 is offline
 
Reply With Quote
Old 05-02-2013, 03:13 PM   #10
kal
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
kal's Avatar
Recipes 
 
Join Date: Nov 2006
Location: Ottawa, Canada
Posts: 2,306
Liked 254 Times on 172 Posts
Likes Given: 6

Default

Yup. Sounds like something is set wrong or wired wrong. Could also be something defective.

Try a simple test: Set the PID to AUTO mode and set it to around 100F and try to heat some cold water to that temp. Without having done auto-tuning it should get to that temp and stay pretty close. Auto-tuning just makes it more accurate.

If you go more than a degree or two above (and keep rising) something is not right and odds are that the element is firing continuously.

If the little "OUT" light on the PID is always on once you go past that 100F set point then the problem is in the PID settings, the PID is defective, or you're not actually in AUTO mode (hit the A/M button - the A-M light should be OFF when in AUTO mode).

Check the SSR light. If it doesn't go on/off in unision with the PID "OUT" light but stays on all the time (or is always off) then you've wired incorrectly or the SSR is defective (always on).

Good luck!

Kal


kal is offline
 
Reply With Quote
Reply


Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
Thermometer calibration - how do YOU do it? frazier All Grain & Partial Mash Brewing 17 04-06-2011 12:55 PM
MLT calibration Blindguardian Equipment/Sanitation 2 10-13-2010 12:59 PM
refracto calibration help moosetav Equipment/Sanitation 3 01-07-2010 03:08 AM
Thermometer calibration? Beavdowg General Techniques 15 08-20-2009 09:25 PM
Equipment Calibration WeHeavy General Beer Discussion 3 11-05-2008 05:14 AM


Forum Jump

Newest Threads

LATEST SPONSOR DEALS