Old 04-30-2013, 02:52 AM   #11
Spiny-Norman
Recipes 
 
Feb 2013
Posts: 11
Liked 4 Times on 2 Posts


Quote:
Originally Posted by Dave1096 View Post
That clamp is called a romex clamp, and your problem is not fixed by loosening the clamp. When that clamp was originally over-tightened the sharp metal edges on it cut through the insulation and grounded-out either your hot or your neutral. When your electrician loosened the clamp he broke that short to ground, but the problem still exists and is a serious safety issue. I can't believe your electrician didn't mention this to you because this is a pretty easy issue to troubleshoot. Replace that run of wire, don't over-tighten the clamp, and you're good.
Trut so pure.
Looks like some damage was done to the wire insulation. In a high load situation this could cause arcing. Arcing lights fires. Bad bad bad.

 
Reply With Quote
Old 04-30-2013, 02:59 AM   #12
Spiny-Norman
Recipes 
 
Feb 2013
Posts: 11
Liked 4 Times on 2 Posts


Oh. and ground fault won't always protect from arcing. Arc fault breakers do that but are only required in bedrooms.
I guess that's because that's where all the sparks are? :-)

sleewok Likes This 
Reply With Quote
Old 05-14-2013, 10:51 AM   #13
NewBrewB
HBT_LIFETIMESUPPORTER.png
 
NewBrewB's Avatar
Recipes 
 
Dec 2009
Pace, FL
Posts: 818
Liked 39 Times on 33 Posts


Quote:
Originally Posted by Dave1096 View Post
That clamp is called a romex clamp, and your problem is not fixed by loosening the clamp. When that clamp was originally over-tightened the sharp metal edges on it cut through the insulation and grounded-out either your hot or your neutral. When your electrician loosened the clamp he broke that short to ground, but the problem still exists and is a serious safety issue. I can't believe your electrician didn't mention this to you because this is a pretty easy issue to troubleshoot. Replace that run of wire, don't over-tighten the clamp, and you're good.
Wanted to follow-up. I did replace the orange wire to the 30A outlet. Afterwards, I peeled-back the insulation where the romex clamp had pinched it to see and of course Dave1096 was absolutely correct. The neutral had pinched through the insulation and was grounding to the romex clamp.

Would this have started a house fire? I'm glad I will never know.

Thanks for the fast feedback guys.

__________________
And now you see that Evil will always triumph, because Good is dumb!

 
Reply With Quote
Old 05-14-2013, 07:41 PM   #14
Dave1096
Recipes 
 
Mar 2013
Philly, PA
Posts: 522
Liked 136 Times on 93 Posts


Quote:
Originally Posted by NewBrewB View Post
Wanted to follow-up. I did replace the orange wire to the 30A outlet. Afterwards, I peeled-back the insulation where the romex clamp had pinched it to see and of course Dave1096 was absolutely correct. The neutral had pinched through the insulation and was grounding to the romex clamp.

Would this have started a house fire? I'm glad I will never know.

Thanks for the fast feedback guys.

No problem. I'm just glad you got a serious safety issue taken care of. To answer your question: Would it have started a house fire? Possibly. Electrical fires are typically caused by overheating of high-resistance connections (loose or broken connections). Even though the copper in the neutral wire wasn't physically touching the metal anymore once you loosened the clamp it was still close enough for the energy to jump through the air (arc) if there was enough potential there. Just as Spiny-Norman said, the insulation between the neutral and the grounded metal being compromised could easily have lead to arcing...which could easily have lead to a fire. Good work by you getting this taken care of. I would fire my electrician, though, if I were you.

P-J Likes This 
Reply With Quote
Old 05-14-2013, 08:37 PM   #15
jeffmeh
HBT_SUPPORTER.png
 
jeffmeh's Avatar
Recipes 
 
Feb 2009
Posts: 2,140
Liked 209 Times on 179 Posts


Quote:
Originally Posted by Dave1096 View Post
Good work by you getting this taken care of. I would fire my electrician, though, if I were you.
I couldn't agree more. He made an extremely incompetent decision to just loosen the clamp and walk away. It should have been obvious to him that some insulation must have been compromised if the GFCI was tripping before but not after loosening the clamp.

P-J Likes This 
Reply With Quote


Reply
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
Brewery Reset FullDraw General Beer Discussion 1 02-06-2013 06:34 PM
Does transplanting reset hop age? sensibull Hops Growing 6 09-23-2011 03:11 AM
Beersmith Reset Lost My Recipes. Help!!! Redweasel Brewing Software 26 11-15-2009 05:05 AM
Does stuck fermentation reset time to bottle? redawg77 Beginners Beer Brewing Forum 3 07-31-2008 11:13 PM


Forum Jump