Default SSR size

I'm putting together a 110v dual element ebiab system on 20a circuits. I've read a lot of the threads on similar systems and I've noticed that most of them are using 40a ssr's. What is the reason for using 40a ssr's on a 20a system wouldn't the 25a ssr (ssr) be enough?

Thanks for the help


mnherky is offline
 
Reply With Quote
Old 03-29-2013, 01:29 PM   #2
BadNewsBrewery
Basement Brewer
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
BadNewsBrewery's Avatar
Recipes 
 
Join Date: Oct 2012
Location: Severn, MD
Posts: 1,248
Liked 129 Times on 103 Posts
Likes Given: 65

Default

The reasoning is the heat generated. SSRs produce a lot of heat as a biproduct of switching the power output. A 40A SSR will have larger components capable of handling heavier loads. Running it at 50% capacity will generate significantly less heat than running a 25A SSR at 80% load.
-Kevin


__________________
Building a Bad News Brewery - eHERMS

2014 - 70gal
2015:
10gal American Pale Ale
5gal Wee Heavy
10gal Irish Red
10gal Hefeweizen
2gal Mead

Keg 1: Apfelwein
Keg 2: Irish Red
Keg 3: Hefeweizen
Fermenting: 1gal Joe's Ancient Orange Mead & 1gal Traditional Mead
BadNewsBrewery is offline
 
Reply With Quote
Old 03-29-2013, 01:41 PM   #3
tphjr
Registered User
Feedback Score: 0 reviews
Recipes 
 
Join Date: Mar 2013
Posts: 69
Liked 5 Times on 5 Posts

Default

Quote:
Originally Posted by BadNewsBrewery View Post
The reasoning is the heat generated. SSRs produce a lot of heat as a biproduct of switching the power output. A 40A SSR will have larger components capable of handling heavier loads. Running it at 50% capacity will generate significantly less heat than running a 25A SSR at 80% load.
-Kevin
Not true - a SSR will dissipate about 1 watt of heat per amp passed through. And the heat generated by a 40 Amp SSR will be the same as the heat generated by a 25 Amp SSR. You will need the same size heat sink for 20 Amps regardless of the SSR you use.

The difference is the 40 Amp SSR contains a TRIAC capable of handling 40 Amps while a 25 Amp has a TRIAC capable of handling 25 Amps. A 25 Amp SSR will work fine.
tphjr is offline
 
Reply With Quote
Old 03-29-2013, 05:23 PM   #4
AllanMar
Feedback Score: 0 reviews
Recipes 
 
Join Date: Jun 2008
Location: Canada
Posts: 192
Liked 6 Times on 6 Posts

Default

Quote:
Originally Posted by tphjr View Post
Not true - a SSR will dissipate about 1 watt of heat per amp passed through. And the heat generated by a 40 Amp SSR will be the same as the heat generated by a 25 Amp SSR. You will need the same size heat sink for 20 Amps regardless of the SSR you use.

The difference is the 40 Amp SSR contains a TRIAC capable of handling 40 Amps while a 25 Amp has a TRIAC capable of handling 25 Amps. A 25 Amp SSR will work fine.
Partially true, but as previously posted a 40A SSR will be designed to dissipate more heat (as it was designed to run up to 40A), which means it will run cooler at 20A then a 25A SSR will, and hence will provide longer life/more reliable usage (W/degC rating). A 20A ssr will have a higher junction temperature at 20A then a 40A SSR @ 20A (the heatsink point is right though). I almost always see SSR's over sized in commercial designs for this same reason. If your going to use a high quality ($$$) SSR then you could get away with a 20A one, if your planning to use the cheaper ones most homebrewer's do then I would defiantly oversize.
AllanMar is offline
 
Reply With Quote
Old 03-29-2013, 05:34 PM   #5
LandoLincoln
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
LandoLincoln's Avatar
Recipes 
 
Join Date: Feb 2011
Location: Joliet, IL
Posts: 2,831
Liked 998 Times on 527 Posts
Likes Given: 26

Default

The 40a will probably last you longer, and there's very little price difference.
__________________
www.jolietbrewersguild.org
LandoLincoln is offline
 
Reply With Quote
Old 04-01-2013, 08:52 PM   #6
inda_bebe
Feedback Score: 0 reviews
Recipes 
 
Join Date: Jan 2012
Location: orange, ca
Posts: 195
Liked 3 Times on 3 Posts
Likes Given: 3

Default

will 2 120v elements work on 1 40a SSR?
inda_bebe is offline
 
Reply With Quote
Old 04-01-2013, 10:55 PM   #7
MX1
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
MX1's Avatar
Recipes 
 
Join Date: May 2008
Location: Colorado Springs, CO
Posts: 1,146
Liked 72 Times on 58 Posts
Likes Given: 101

Default



I use this one!
__________________
"The ART of brewing Beer, is the ACT of brewing Beer"
https://txbrewing.wordpress.com

Ferm 1: Irish Red Ale
Ferm 2:

On Deck: American Wheat

Keg 1: Un-Common
Keg 2: Switchback Stout

Total Gallons brewed (2015) - 10
MX1 is offline
highland_brewer Likes This 
Reply With Quote
Old 04-01-2013, 11:17 PM   #8
Monster Mash
Feedback Score: 0 reviews
Recipes 
 
Join Date: Apr 2006
Location: Castaic, CA
Posts: 1,323
Liked 88 Times on 69 Posts
Likes Given: 12

Default

Quote:
Originally Posted by inda_bebe View Post
will 2 120v elements work on 1 40a SSR?
It depends on the wattage of the elements, not the voltage.
__________________
My 1BBL Brewery Pics
Monster Mash is offline
 
Reply With Quote
Old 04-01-2013, 11:27 PM   #9
passedpawn
Waste Allocation Load Lifter - Earth Class
HBT_MODERATOR.png
Feedback Score: 1 reviews
 
passedpawn's Avatar
Recipes 
 
Join Date: Apr 2009
Location: ☼ Clearwater, FL ☼
Posts: 22,419
Liked 5023 Times on 2994 Posts
Likes Given: 4201

Default

Quote:
Originally Posted by tphjr View Post
Not true - a SSR will dissipate about 1 watt of heat per amp passed through. And the heat generated by a 40 Amp SSR will be the same as the heat generated by a 25 Amp SSR. You will need the same size heat sink for 20 Amps regardless of the SSR you use.

The difference is the 40 Amp SSR contains a TRIAC capable of handling 40 Amps while a 25 Amp has a TRIAC capable of handling 25 Amps. A 25 Amp SSR will work fine.
Hmmm. So, if you run 40A through the 25A triac, what happens?
__________________
- Andrew
passedpawn is offline
 
Reply With Quote
Old 04-01-2013, 11:31 PM   #10
JayMac
Feedback Score: 0 reviews
Recipes 
 
Join Date: Jun 2012
Location: Guelph, Ontario
Posts: 271
Liked 11 Times on 10 Posts
Likes Given: 5

Default

Quote:
Originally Posted by Monster Mash View Post
It depends on the wattage of the elements, not the voltage.
True, but the highest wattage in a 120V element is 2000W. Two of those draw 33.3A. That's well below the SSR's rating. To my knowledge, that's the highest power you can get at 120V (even two 6000W 240V element at 120V won't draw that much current).

So to answer your question, that should work fine.


JayMac is offline
 
Reply With Quote
Reply


Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
Kettle size versus heater element size Hound Electric Brewing 6 03-21-2013 11:29 PM
Batch size vs. fermenter size question. vetbrewer Beginners Beer Brewing Forum 3 10-06-2012 06:52 PM
What size freezer??? 5 Tall Quarters (possibly a couple slim 1/6) to keep size down? gtpeebs1 Bottling/Kegging 6 01-29-2012 01:07 AM
yeast starter size vs. batch size biestie General Beer Discussion 3 04-05-2011 01:00 AM
Size of Batch to Size of Fermenter For Blow Off Method and Dry Hopping AirBronto General Beer Discussion 9 02-19-2010 02:39 PM


Forum Jump

Newest Threads

LATEST SPONSOR DEALS