I am using this diagram for my control panel.

http://www.pjmuth.org/beerstuff/imag...2451-5500w.jpg

The only difference is I have two syl-2352 PID's from Auber. I don't have power to my element outlet for my HLT. I have 120v on both leads on the input side of the contactor but only get a little over 1 volt on the output sides. My BK contactor works fine and I have power all the way to the outlet. I also hear a click when I turn on the power to my BK but nothing when I turn on the HLT. I hooked up the switch for my BK to the contactor and still nothing so I know it is not the switch. I checked continuity from my SSR's to the PID's and that is fine so I know it is not a connection there. Any ideas?

 
Reply With Quote
Old 03-24-2013, 11:00 PM   #2
lschiavo
HBT_LIFETIMESUPPORTER.png
 
lschiavo's Avatar
Recipes 
 
Sep 2009
Surrounded by Yoopers
Posts: 4,722
Liked 1101 Times on 746 Posts


Check the voltage across the contactor coil. You may have a bad neutral connection. You may have a bad coil or something other than a 120V coil.

 
Reply With Quote
Old 03-24-2013, 11:13 PM   #3
BWN
Recipes 
 
Dec 2010
Dexter, NY
Posts: 702
Liked 20 Times on 19 Posts


I just checked and I have 120v across the coil. I know the neutral is good because I have the neutral to the good contactor jumpered from this one. I just checked the sticker on the sides of the contactors and they are the same.

 
Reply With Quote
Old 03-24-2013, 11:17 PM   #4
WAORGANY
HBT_LIFETIMESUPPORTER.png
 
WAORGANY's Avatar
Recipes 
 
Apr 2010
Northern NY, NY
Posts: 476
Liked 14 Times on 12 Posts


Quote:
Originally Posted by BWN View Post
I just checked and I have 120v across the coil. I know the neutral is good because I have the neutral to the good contactor jumpered from this one. I just checked the sticker on the sides of the contactors and they are the same.
You can have my PID and we will call it good! Thats wild its not working..
__________________
RLTW!

 
Reply With Quote
Old 03-24-2013, 11:19 PM   #5
WAORGANY
HBT_LIFETIMESUPPORTER.png
 
WAORGANY's Avatar
Recipes 
 
Apr 2010
Northern NY, NY
Posts: 476
Liked 14 Times on 12 Posts


Quote:
Originally Posted by BWN View Post
I just checked and I have 120v across the coil. I know the neutral is good because I have the neutral to the good contactor jumpered from this one. I just checked the sticker on the sides of the contactors and they are the same.
Let me know if you need anything or want to come over and look at mine but I am sure they are wired about the same.
__________________
RLTW!

 
Reply With Quote
Old 03-24-2013, 11:19 PM   #6
lschiavo
HBT_LIFETIMESUPPORTER.png
 
lschiavo's Avatar
Recipes 
 
Sep 2009
Surrounded by Yoopers
Posts: 4,722
Liked 1101 Times on 746 Posts


Sounds like it may be a bad coil. You could disconnect both and compare readings with an ohm meter.

 
Reply With Quote
Old 03-24-2013, 11:22 PM   #7
BWN
Recipes 
 
Dec 2010
Dexter, NY
Posts: 702
Liked 20 Times on 19 Posts


Quote:
Originally Posted by WAORGANY View Post
Let me know if you need anything or want to come over and look at mine but I am sure they are wired about the same.
I'm pretty sure it is wired right. I have it wired exactly like the other one and I just double checked the diagram and it is correct. If it is a bad contactor I don't mind replacing it I just want to make sure it isn't something else?

 
Reply With Quote
Old 03-24-2013, 11:25 PM   #8
BWN
Recipes 
 
Dec 2010
Dexter, NY
Posts: 702
Liked 20 Times on 19 Posts


Quote:
Originally Posted by lschiavo View Post
Sounds like it may be a bad coil. You could disconnect both and compare readings with an ohm meter.
Are you saying disconnect the hot and the neutral on both coils and measure the ohms? Then compare them to each other.

 
Reply With Quote
Old 03-24-2013, 11:42 PM   #9
lschiavo
HBT_LIFETIMESUPPORTER.png
 
lschiavo's Avatar
Recipes 
 
Sep 2009
Surrounded by Yoopers
Posts: 4,722
Liked 1101 Times on 746 Posts


Quote:
Originally Posted by BWN View Post
Are you saying disconnect the hot and the neutral on both coils and measure the ohms? Then compare them to each other.
Yes. They should measure close to each other.

Also, try to work the contactor manually. Usually you can push in the contacts with a screwdriver or something. It may just be hung up. I've seen new ones do that before.

 
Reply With Quote
Old 03-24-2013, 11:50 PM   #10
BWN
Recipes 
 
Dec 2010
Dexter, NY
Posts: 702
Liked 20 Times on 19 Posts


I got 330 on the good one and OL on the bad one. I'm not sure I can push it in manually. I'll look and see.

 
Reply With Quote
Reply
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
Working hard, or hardly working? bwirthlin Drunken Ramblings and Mindless Mumbling 19 02-14-2014 05:56 AM
Is it working? Noz03 Cider Forum 11 08-14-2013 09:39 PM
it is working well! Kemah All Grain & Partial Mash Brewing 2 03-04-2012 10:09 PM
Working out ABV renshaw Beginners Beer Brewing Forum 6 06-15-2011 10:09 PM
Something I've been working on.... Dude Label Display & Discussion 9 02-19-2007 05:57 PM


Forum Jump