Has anyone added a 30a breaker to the 50a GFI spa panel? - Page 3 - Home Brew Forums
Register Now For Free!

Home Brew Forums > Home Brewing Beer > Electric Brewing > Has anyone added a 30a breaker to the 50a GFI spa panel?

Reply
 
Thread Tools
Old 03-15-2013, 01:30 PM   #21
Homercidal
Licensed Sensual Massage Therapist.
HBT_MODERATOR.png
 
Homercidal's Avatar
Recipes 
 
Feb 2008
Reed City, MI
Posts: 31,709
Liked 5106 Times on 3453 Posts


Quote:
Originally Posted by P-J View Post
This 2 POLE 30A B CURVE breaker is well suited for mounting in the Spa Panel. It is a UL1077 device that functions as needed for this application without issues or problems. Plus - it is DIN rail mountable & for $17.50 it is a great deal.
I like that. So I could add this to my spa panel and run a 30A feed from the 50A GFI already in the panel??

 
Reply With Quote
Old 03-15-2013, 01:46 PM   #22
P-J
HBT_LIFETIMESUPPORTER.png
Recipes 
 
Mar 2010
Charlotte, NC
Posts: 3,336
Liked 302 Times on 235 Posts


Quote:
Originally Posted by Homercidal View Post
I like that. So I could add this to my spa panel and run a 30A feed from the 50A GFI already in the panel??
Exactly. It will work very well.

 
Reply With Quote
Old 03-15-2013, 02:35 PM   #23
Walker
I use secondaries. :p
HBT_LIFETIMESUPPORTER.png
 
Walker's Avatar
Recipes 
 
Sep 2005
Cary, NC
Posts: 10,987
Liked 101 Times on 89 Posts


Educate me. I'm not really familiar with UL ratings, so what is the difference between UL489 and UL1077?

I'm trying to google it, but not really finding much.

edit: nevermind. If I change my search to "UL489 vs UL1077" I get some info.
__________________
Ground Fault Brewing Co.

 
Reply With Quote
Old 03-15-2013, 03:06 PM   #24
jeffmeh
HBT_SUPPORTER.png
 
jeffmeh's Avatar
Recipes 
 
Feb 2009
Posts: 2,160
Liked 211 Times on 181 Posts


Quote:
Originally Posted by Walker View Post
Educate me. I'm not really familiar with UL ratings, so what is the difference between UL489 and UL1077?

I'm trying to google it, but not really finding much.

edit: nevermind. If I change my search to "UL489 vs UL1077" I get some info.
There is a comparison in this document, in case anyone else is interested. http://www.automationdirect.com/stat...ppprot1p3p.pdf

Short answer: UL489 for branch circuit protection, UL1077 for supplementary protection.

So for this application can we consider it supplementary protection because we already have a breaker in the main panel providing branch circuit protection? That would make sense to me.

 
Reply With Quote
Old 03-15-2013, 03:10 PM   #25
jeffmeh
HBT_SUPPORTER.png
 
jeffmeh's Avatar
Recipes 
 
Feb 2009
Posts: 2,160
Liked 211 Times on 181 Posts


This would enable using 10awg and 30a rated receptacles and plugs, from the 50a receptacle, to the 50a GFI spa panel with the supplementary 30a breaker, to the control panel, to the heating elements. I would expect that to be significantly less expensive than having to use 6awg and 50a rated receptacles and plugs.

Edit: And easier to work with....

 
Reply With Quote
Old 03-15-2013, 03:15 PM   #26
P-J
HBT_LIFETIMESUPPORTER.png
Recipes 
 
Mar 2010
Charlotte, NC
Posts: 3,336
Liked 302 Times on 235 Posts


Quote:
Originally Posted by jeffmeh View Post
There is a comparison in this document, in case anyone else is interested. http://www.automationdirect.com/stat...ppprot1p3p.pdf

Short answer: UL489 for branch circuit protection, UL1077 for supplementary protection.

So for this application can we consider it supplementary protection because we already have a breaker in the main panel providing branch circuit protection? That would make sense to me.
That is it exactly.

The breakers mounted within the controller or within the Spa Panel are placed for device protection.

 
Reply With Quote
Old 03-15-2013, 03:24 PM   #27
Walker
I use secondaries. :p
HBT_LIFETIMESUPPORTER.png
 
Walker's Avatar
Recipes 
 
Sep 2005
Cary, NC
Posts: 10,987
Liked 101 Times on 89 Posts


Here's the most concise thing I found. (Not saying it's correct, but it is clear and concise):

taken from here, emphasis added by me: http://forums.mikeholt.com/showthread.php?t=66983

Quote:
UL489 breakers can be used to meet the requirements of NEC branch circuit protective devices. UL1077 devices can be used as a supplement to a UL489 device. If the circuit wiring leaves the control cabinet it must be protected, somewhere upstream, by a UL489 device. If the circuit does not leave the control cabinet a UL1077 device may be applicable.
In this situation, the wiring is going to leave the cabinet (the spa panel). That requires a UL489 device somewhere upstream. If the main GFCI breaker in the spa panel is a UL489 device (which it should be based on what I was reading), then a UL1077 device is fine to use to drop the current to 30A before leaving the spa panel.

Or did I get that wrong?
__________________
Ground Fault Brewing Co.

 
Reply With Quote
Old 03-15-2013, 03:36 PM   #28
P-J
HBT_LIFETIMESUPPORTER.png
Recipes 
 
Mar 2010
Charlotte, NC
Posts: 3,336
Liked 302 Times on 235 Posts


Quote:
Originally Posted by Walker View Post
...
Or did I get that wrong?
You have it right. I do have one diversion on the whole thing though. The power feed to the Spa Panel and the controller terminates with a outlet where the Spa Panel &/or the controller plugs into. With that said, the NEC rules really ended at the outlet.

Just saying...

 
Reply With Quote
Old 03-15-2013, 03:37 PM   #29
AllanMar
Recipes 
 
Jun 2008
Canada
Posts: 190
Liked 6 Times on 6 Posts


Quote:
Originally Posted by P-J View Post
That is it exactly.

The breakers mounted within the controller or within the Spa Panel are placed for device protection.
If your going to drop the wire size from the GFCI panel (50A breaker) it needs to be UL489. As mentioned above UL489 is to meet NEC requirement. NEC requires a 30A overcurrent protector for your 10gauge wire from the modified GFCI, a UL1077 device does NOT satisfy this requirement.

As mentioned UL1077 is supplemental protection, meaning you already have some other protection. If you are dropping to 30A with the supplemental protection you have NO primary protection at 30A. This is like saying you can use UL1077 breakers off your bus bar's in your panel because you have the 100/200A main breaker....

This is a very common mistake and I see it done in industry alot as well (and fails panel certification)

If you want to do it cheap, what about a Fused disconnect they sell for Air conditioners/etc?

EDIT: Yes, NEC ends at outlet but then UL panel specifications are supposed to take over (in industry), but as most people don't usually have access or desire to follow they stick with the NEC. Certaintly you can do whatever you want we are not building industrial panels here. So if you don't follow it thats your choice, but that doesnt change the facts.

EDIT2: Why not something like this, with a small peice of 6AWG wire and a short conduit to connect the two panels. Physically bigger, but cheap. http://www.homedepot.com/p/t/2021064...0h&R=202106492 Modifying the GFCI panel is also likely a bit of an issue.... You can usually also get single breaker panels/disconnects cheaply as well (http://www.homedepot.com/p/t/1001778...2w&R=100177812), and you could throw a regular 30A breaker in it (still going to be a bit more money though)

 
Reply With Quote
Old 03-15-2013, 03:45 PM   #30
P-J
HBT_LIFETIMESUPPORTER.png
Recipes 
 
Mar 2010
Charlotte, NC
Posts: 3,336
Liked 302 Times on 235 Posts


Whatever...

 
Reply With Quote
Reply
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
breaker bracket from sub panel Robhansen Electric Brewing 6 10-03-2012 12:54 PM
Spa Panel vs GFI Breaker? rack04 Electric Brewing 24 09-03-2012 04:34 PM
GE Spa Panel Breaker sdugre Electric Brewing 9 07-18-2011 07:22 PM
Panel GFCI Breaker IrregularPulse Electric Brewing 13 03-23-2011 08:43 PM
Take a Look at my Breaker Panel... ScubaSteve Electric Brewing 21 02-08-2011 07:42 PM


Forum Jump