Does the garage not have another 120v circuit available?


__________________
Welcome to BrewHardware.com. I love you.
New 100% Stainless Steel Heating Elements are IN! ULWD 5500w Ripple, 2000w, 1500w, etc
Chugger Pumps, Pump Kits, Camlocks, Sightglasses, Clear USA made Silicone Tubing, RIMS, Electric Install Parts, etc.
Bobby_M is online now
 
Reply With Quote
Old 01-04-2013, 05:25 PM   #22
ajdelange
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
Recipes 
 
Join Date: Aug 2010
Location: McLean/Ogden, Virginia/Quebec
Posts: 7,764
Liked 1034 Times on 818 Posts
Likes Given: 32

Default

Quote:
Originally Posted by johnp View Post
Thanks for that workaround. I'll ask my electrician about that.
This isn't something I'd expect the average electrician to encounter every day. A typical part would be something like this
http://www.grainger.com/Grainger/ACM...DN6?Pid=search

Note that these are not cheap (over $100). This particular one is rated at 150VA and ought to run a couple of fractional HP pumps but check the pump actual draw.


ajdelange is offline
 
Reply With Quote
Old 01-04-2013, 05:45 PM   #23
GTaylor
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
GTaylor's Avatar
Recipes 
 
Join Date: Sep 2011
Location: Avon, Indiana
Posts: 184
Liked 6 Times on 6 Posts

Default

He mentioned running this outlet through a spa panel in the OP, wouldn't that allow him to have 4 lines coming out and draw the 120 off one of the hot legs and the new neutral?
GTaylor is offline
 
Reply With Quote
Old 01-04-2013, 06:45 PM   #24
Misplaced_Canuck
HBT_LIFETIMESUPPORTER.png
Feedback Score: 1 reviews
 
Misplaced_Canuck's Avatar
Recipes 
 
Join Date: Jan 2011
Location: NE Columbia SC - Formerly, Montreal Canada
Posts: 2,839
Liked 157 Times on 129 Posts
Likes Given: 51

Default

Quote:
Originally Posted by ajdelange View Post
This isn't something I'd expect the average electrician to encounter every day. A typical part would be something like this
http://www.grainger.com/Grainger/ACM...DN6?Pid=search

Note that these are not cheap (over $100). This particular one is rated at 150VA and ought to run a couple of fractional HP pumps but check the pump actual draw.
150VA @ 110V ~= 1.4 Amps. Uber low.

MC
__________________
Quote:
Originally Posted by Misplaced_Canuck
Carbonic bite? Is that like the bubonic plague?
Quote:
Originally Posted by ebstauffer
Needless to say after more than a few drams my mental efficiency matched my mashing efficiency.
Misplaced_Canuck is offline
 
Reply With Quote
Old 01-04-2013, 06:48 PM   #25
jeffmeh
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
jeffmeh's Avatar
Recipes 
 
Join Date: Feb 2009
Posts: 2,015
Liked 178 Times on 151 Posts
Likes Given: 24

Default

Quote:
Originally Posted by GTaylor View Post
He mentioned running this outlet through a spa panel in the OP, wouldn't that allow him to have 4 lines coming out and draw the 120 off one of the hot legs and the new neutral?
He has H-H-G, and the spa panel solution (somewhat controversial, and beaten to death, http://www.homebrewtalk.com/f170/3-w...-again-372667/) is with H-H-N in.
jeffmeh is offline
 
Reply With Quote
Old 01-04-2013, 06:57 PM   #26
danb35
Feedback Score: 0 reviews
Recipes 
 
Join Date: May 2012
Location: Hartsville, SC
Posts: 131
Liked 20 Times on 14 Posts
Likes Given: 1

Default

Quote:
Originally Posted by GTaylor View Post
He mentioned running this outlet through a spa panel in the OP, wouldn't that allow him to have 4 lines coming out and draw the 120 off one of the hot legs and the new neutral?
A spa panel won't (can't) create a new neutral if there isn't one coming into it.
danb35 is offline
 
Reply With Quote
Old 01-04-2013, 07:33 PM   #27
ajdelange
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
Recipes 
 
Join Date: Aug 2010
Location: McLean/Ogden, Virginia/Quebec
Posts: 7,764
Liked 1034 Times on 818 Posts
Likes Given: 32

Default

Quote:
Originally Posted by Misplaced_Canuck View Post
150VA @ 110V ~= 1.4 Amps. Uber low.
Not really. I said it ought to run a couple based on 746/25 = 30 watts but 115*1.4 = 161 VA (these are the nameplate numbers for the 1/25 HP March pumps used by most of us). Either these things are incredibly reactive or incredibly inefficient or a bit of both.

Just checked: under load at 122 V a 1/25 HP March Pump draws 1.29 A rms for 157 VA but the power consumed is only 93 Watts so that's 93/122 = 0.76 Amp resistive and 1.29 - 0.76 = 0.53 amp reactive for a power factor of 0.59.

Also the efficiency is 30/93 = 32%.

I'm bit surprised but that's what the numbers show.

Given that OP would probably get by with a 150 KVA transformer if all he wanted to run was a single pump but would have to go to a larger transformer if he wanted a second pump or additional 120 V loads.
ajdelange is offline
 
Reply With Quote
Old 01-04-2013, 07:41 PM   #28
johnp
Feedback Score: 0 reviews
Recipes 
 
Join Date: Jun 2010
Location: SD
Posts: 137
Liked 7 Times on 7 Posts
Likes Given: 10

Default

Quote:
Originally Posted by Bobby_M View Post
Does the garage not have another 120v circuit available?
I do have 120 in the garage.
johnp is offline
 
Reply With Quote
Old 01-04-2013, 07:42 PM   #29
johnp
Feedback Score: 0 reviews
Recipes 
 
Join Date: Jun 2010
Location: SD
Posts: 137
Liked 7 Times on 7 Posts
Likes Given: 10

Default

Quote:
Originally Posted by ajdelange View Post
Not really. I said it ought to run a couple based on 746/25 = 30 watts but 115*1.4 = 161 VA (these are the nameplate numbers for the 1/25 HP March pumps used by most of us). Either these things are incredibly reactive or incredibly inefficient or a bit of both.

Just checked: under load at 122 V a 1/25 HP March Pump draws 1.29 A rms for 157 VA but the power consumed is only 93 Watts so that's 93/122 = 0.76 Amp resistive and 1.29 - 0.76 = 0.53 amp reactive for a power factor of 0.59.

Also the efficiency is 30/93 = 32%.

I'm bit surprised but that's what the numbers show.

Given that OP would probably get by with a 150 KVA transformer if all he wanted to run was a single pump but would have to go to a larger transformer if he wanted a second pump or additional 120 V loads.
I just bought a single chugger pump from bobby, I'm assuming it would draw a similar load.
johnp is offline
 
Reply With Quote
Old 01-04-2013, 08:00 PM   #30
ajdelange
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
Recipes 
 
Join Date: Aug 2010
Location: McLean/Ogden, Virginia/Quebec
Posts: 7,764
Liked 1034 Times on 818 Posts
Likes Given: 32

Default

If it's a 1/25 HP probably something pretty close but there ought to be a nameplate on it with actual numbers.


ajdelange is offline
 
Reply With Quote
Reply


Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help with wires ( pics inside ) Thehopguy Beginners Beer Brewing Forum 6 07-20-2011 01:55 AM
Pics Inside Westvleteren tagz General Beer Discussion 11 05-10-2011 04:03 PM
Still going, pics and Q's inside kryznic Beginners Beer Brewing Forum 6 03-25-2010 10:11 PM
MLT Build.. Few pics inside TimSTi Kettles, Mash Tuns, & Hot Liquor Tanks 5 02-02-2009 04:33 AM
Brewday! Pics inside jdoiv All Grain & Partial Mash Brewing 14 04-18-2007 04:18 AM


Forum Jump

Newest Threads

LATEST SPONSOR DEALS