I have recently set up a TET-612 PID controller attached to a Honeywell VR8300a gas valve to control the mash temp on my brew stand. I have gone through the PID setup to the best of my ability (granted, that might not be much ability ) and all is well except for 2 issues.

1) Autotune has to be enabled on the PID for the system to work. Otherwise the valve will click but never open and ignite. This is really more of an observation than an issue but....

2) The real issue.. autotune stops running every 15 mins or so. It's impossible to walk away during the mash as autotune will randomly stop working and will need to be restarted. This also happens on a friends sabco brewmagic system so I am hoping its a setup issue.

Is there anything I can do to make autotune constant so that I don't have to continuously monitor it? I admit that I don't fully understand what autotune does, but as long as I can get it to stay on that is all that I care about.

Thanks for any input you can give.

 
Reply With Quote
Old 12-27-2012, 11:01 PM   #2
tophmck
Recipes 
 
Oct 2009
Madison, WI
Posts: 193
Liked 4 Times on 4 Posts


I don't have any experience with this controller, but it sounds like you're using it in PID mode. Since you're using a gas valve, it should be in relay output mode. The manual is pretty cryptic, but I think you want outy=0.

 
Reply With Quote
Old 12-27-2012, 11:14 PM   #3
BetterSense
Recipes 
 
Jul 2011
Richardson, Texas
Posts: 1,025
Liked 56 Times on 45 Posts


Actual PID is in most situations not even appropriate for brewing purposes. Simple thermostatic control is what you want.

Auto-tuning is not something that you use normally. It's a routine that you can run, and the PID controller software will 'learn' your system so that it can optimize overshoot etc.

 
Reply With Quote
Old 12-28-2012, 02:32 AM   #4
JonClayton
Recipes 
 
Dec 2009
Anderson, South Carolina
Posts: 239
Liked 1 Times on 1 Posts


Thanks everyone. I will experiment with changing the Outy setting tomorrow. I am pretty sure I left it as default value 2. BetterSense, thanks for clarifying that for me. I thought from my understanding that autotune was only so that it could learn the system but then it confused me that it would only control the valve with AT turned on. Hopefully the settings change clears things up.

If I can get this going and receive my new false bottom from Jaybird I think i'll be in business.

 
Reply With Quote
Old 12-28-2012, 04:04 PM   #5
JonClayton
Recipes 
 
Dec 2009
Anderson, South Carolina
Posts: 239
Liked 1 Times on 1 Posts


No dice setting outy to 0. When set to 0 the gas valve does not open (or even click) to light the burner. Any other thoughts?

Thanks!

 
Reply With Quote
Old 12-28-2012, 05:55 PM   #6
tophmck
Recipes 
 
Oct 2009
Madison, WI
Posts: 193
Liked 4 Times on 4 Posts


Which terminals do you have the gas valve hooked up to? And what are your settings for AH1 and AL1?

 
Reply With Quote
Old 12-29-2012, 05:00 PM   #7
JonClayton
Recipes 
 
Dec 2009
Anderson, South Carolina
Posts: 239
Liked 1 Times on 1 Posts


Top, good question. A friend wired up the controller for me. I will check it out when I am home this evening and report back.

 
Reply With Quote
Old 12-29-2012, 06:40 PM   #8
tophmck
Recipes 
 
Oct 2009
Madison, WI
Posts: 193
Liked 4 Times on 4 Posts


Quote:
Originally Posted by JonClayton View Post
Top, good question. A friend wired up the controller for me. I will check it out when I am home this evening and report back.
OK. From the behavior you describe above, my guess is that the gas valve is currently hooked up as if it were an SSR (terminals 6 and 7). But the manual says that for outy=0 mode, "Relay J1 and J2 as Alarm outputs; SSR Disabled, normally used for upper/lower limits alarm trigger control". In other words, you want to hook up the gas valve to J1 (terminals 4 and 5 see the attached terminal assignments below).

Also, it sounds like you might be trying to set your desired temperature using SV. But you're using the J1 relay to fire your burner (effectively the burner is a low temp alarm), so you need to use AL1 and AH1 to set the desired temperature. Note that AH1 is the temperature you want the burner to fire at and AL1 is the temperature at which it should turn off. (See the attached Figure 5 below.) Note that AL1 must be higher than AH1.

So, just as an example, if you want to maintain a mash temp of 152, you might try setting AH1 to 151 and AL1 to 153.

Good luck!
Click image for larger version

Name:	Screen Shot 2012-12-29 at 12.17.53 PM.png
Views:	295
Size:	103.5 KB
ID:	90925   Click image for larger version

Name:	Screen Shot 2012-12-29 at 12.18.26 PM.jpg
Views:	303
Size:	37.3 KB
ID:	90926  

 
Reply With Quote
Old 12-29-2012, 07:02 PM   #9
whoaru99
Recipes 
 
Oct 2012
Posts: 1,765
Liked 142 Times on 118 Posts


Quote:
Originally Posted by BetterSense View Post
Actual PID is in most situations not even appropriate for brewing purposes. Simple thermostatic control is what you want.

Auto-tuning is not something that you use normally. It's a routine that you can run, and the PID controller software will 'learn' your system so that it can optimize overshoot etc.
Yeah, and maybe it's your point but I'm thinking auto tune doesn't work for simple on/off control?
__________________
Drinking: Store Bought
Kegged: nothing at present

 
Reply With Quote
Old 12-30-2012, 04:18 AM   #10
crane
Recipes 
 
Sep 2011
San Diego, CA
Posts: 712
Liked 104 Times on 87 Posts


Quote:
Originally Posted by whoaru99

Yeah, and maybe it's your point but I'm thinking auto tune doesn't work for simple on/off control?
Auto tune is used to calculate the gain coefficients for the PID control algorithm, so you are correct it doesn't work for simple on/off control.

 
Reply With Quote
Reply
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
HOW TO: Manually Tune a PID CodeRage Brew Stands 9 01-06-2017 07:16 PM
Auber 2352 Auto tune issue frankstoneline Electric Brewing 6 11-21-2011 07:26 AM
Wanted: Auto/Semi-Auto All-Grain System (So. Cal) ocluke For Sale 4 10-08-2010 08:18 PM
IBU tune in ChickenSoop Beginners Beer Brewing Forum 11 01-12-2009 07:57 PM
Name That Tune! Cheesefood General Chit Chat 14 04-07-2007 01:18 AM


Forum Jump