Hello all,

Is it possible to instal my spa panel in between the breaker box and my dryer outlet(3 wire).

My idea is this:

-Cut the dryer line in between breaker and dryer outlet
-instal spa panel and 4 wire outlet
-then reconnect existing 3 wire outlet inside spa panel.

Before:
Breaker..........3 wire dryer outlet
After:
Breaker.......spa panel w/4wire outlet........3 wire dryer outlet

I would not use dryer and brewery at the same time. (maybe install a switch to prevent accidental use of both)

Thanks.
__________________
Andrew

 
Reply With Quote
Old 11-28-2012, 11:15 PM   #2
whoaru99
Recipes 
 
Oct 2012
Posts: 1,765
Liked 142 Times on 118 Posts


Disclaimer: I am not an electrician by trade, nor do I claim to know the NEC inside and out.

That said, my interpretation of NEC would be that you can only use that 3-wire circuit in its original form. If you modify the circuit itself I think you would have to bring it up to the current 3-wire with equipment ground (4-wire) code.
__________________
Drinking: Store Bought
Kegged: nothing at present

 
Reply With Quote
Old 11-28-2012, 11:15 PM   #3
45_70sharps
 
45_70sharps's Avatar
Recipes 
 
Sep 2012
Raymond, Washington
Posts: 1,807
Liked 172 Times on 141 Posts


It should be possible, but I think you would probably be in violation of code to have both on one circuit.
Putting a switch of some sort in line would probably be a good idea. Draw from both at one time would be more than the breaker and probably the wire was rated for.
__________________
Let's see if I keep this updated!

On tap
Black Butte clone

In secondary
Pumpkin ale

In primary
Honey wit

Up next.. Firestone Union Jack clone

 
Reply With Quote
Old 11-28-2012, 11:35 PM   #4
fbold1
Brew Nut
HBT_SUPPORTER.png
 
fbold1's Avatar
Recipes 
 
Dec 2011
North Coast, Ohio
Posts: 255
Liked 8 Times on 8 Posts


Quote:
Originally Posted by Andrwb33 View Post
Hello all,
My idea is this:

-Cut the dryer line in between breaker and dryer outlet
-instal spa panel and 4 wire outlet
-then reconnect existing 3 wire outlet inside spa panel.

Before:
Breaker..........3 wire dryer outlet
After:
Breaker.......spa panel w/4wire outlet........3 wire dryer outlet

I would not use dryer and brewery at the same time. (maybe install a switch to prevent accidental use of both)

Thanks.
Not a good idea, but if you do, you still need to run a ground wire for the spa panel.
__________________
"Whoever makes a poor beer is transferred to the dung-hill." Edict in the City of Danzig, 11th Century.

 
Reply With Quote
Old 11-29-2012, 01:06 AM   #5
jeffmeh
HBT_SUPPORTER.png
 
jeffmeh's Avatar
Recipes 
 
Feb 2009
Posts: 2,161
Liked 212 Times on 182 Posts


Definitely not a good idea. Out of curiosity, what are you trying to accomplish? The only thing I can think of is that you want to set up your brewing space at some point midway along the wire between the breaker box and the dryer outlet. You would be much better off just using the outlet and plugging the spa panel into it and running off of that. You still only have 2 hots and a ground, so you do not have a neutral to safely run 120V in addition to the 240V.

Lastly, welcome to HBT. I am in North Andover.

 
Reply With Quote
Old 11-29-2012, 02:17 AM   #6
whoaru99
Recipes 
 
Oct 2012
Posts: 1,765
Liked 142 Times on 118 Posts


I'd disagree. A dryer receptacle is almost certainly two hots and neutral, not two hots and ground. The NEMA type of receptacle should tell you this, assuming it's put in to Code.

A 10-XX (XX being the current rating, typically 30 for dryer circuit) would be 120/240V with two hots and neutral. Two hots and ground would be a 6-XX, for 240V only.
__________________
Drinking: Store Bought
Kegged: nothing at present

 
Reply With Quote
Old 11-29-2012, 03:27 PM   #7
jeffmeh
HBT_SUPPORTER.png
 
jeffmeh's Avatar
Recipes 
 
Feb 2009
Posts: 2,161
Liked 212 Times on 182 Posts


Quote:
Originally Posted by whoaru99 View Post
I'd disagree. A dryer receptacle is almost certainly two hots and neutral, not two hots and ground. The NEMA type of receptacle should tell you this, assuming it's put in to Code.

A 10-XX (XX being the current rating, typically 30 for dryer circuit) would be 120/240V with two hots and neutral. Two hots and ground would be a 6-XX, for 240V only.
I suspect you are correct. This is what happens when one knows just enough to be dangerous and posts after a few beers, lol.

Either way, with 3-wires you cannot get both a dedicated neutral and ground, so running both 120V in the panel along with the 240V is not recommended. It would need the fourth wire (the missing ground if 10-XX, or the missing neutral if 6-XX).

 
Reply With Quote
Old 11-29-2012, 06:18 PM   #8
Andrwb33
 
Andrwb33's Avatar
Recipes 
 
Jan 2011
Lawrence, Ma
Posts: 21


Quote:
Originally Posted by jeffmeh View Post
Definitely not a good idea. Out of curiosity, what are you trying to accomplish? The only thing I can think of is that you want to set up your brewing space at some point midway along the wire between the breaker box and the dryer outlet. You would be much better off just using the outlet and plugging the spa panel into it and running off of that. You still only have 2 hots and a ground, so you do not have a neutral to safely run 120V in addition to the 240V.

Lastly, welcome to HBT. I am in North Andover.
Your correct the dryer is on the other side of the basement from the breaker panel. I hope to brew closer to the panel, on top of that the panel is full so I have no more room to run a dedicated brewery outlet.

So my best bet would to just have an electrician rewire a 4 wire outlet at the dryer then plug my spa panel into that for the GFI protection. I like the portability aspect of this. I would just have to make a really long plug for the spa panel.

Now that I'm thinking about it I could skip the spa panel all together and just have the electrician install a GFI protected breaker. (oh boy getting expensive now).

Thanks.

PS Nice to meet someone local. Do you know of any HB clubs in the area?
__________________
Andrew

 
Reply With Quote
Old 11-29-2012, 06:49 PM   #9
jeffmeh
HBT_SUPPORTER.png
 
jeffmeh's Avatar
Recipes 
 
Feb 2009
Posts: 2,161
Liked 212 Times on 182 Posts


I belong to the Merrimack Valley Home Brew Club. We usually meet the first Saturday of the month, and there is a meeting this Saturday. I don't think I will be able to make it, but if you are interested let me know and I will put you in touch with the host. The website is a bit sparse, but is at www.mvhbc.com.

 
Reply With Quote
Reply
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
Why Not Just Plug Into the Dryer Outlet? txstars15 Electric Brewing 9 11-14-2012 12:52 PM
Connecting a Three wire inline GFCI to a 4 wire Outlet? ODI3 Electric Brewing 3 10-10-2012 03:02 PM
4-wire GFCI 220 volt cable with a 3-wire dryer outlet? gshopper Electric Brewing 12 07-17-2012 11:49 PM
Installing a dryer outlet in spa panel bagpiperjosh Electric Brewing 22 04-24-2012 06:19 PM
Help with Electric Planning (Spa Panel, Dryer Outlet, Extension Cord) br1dge Electric Brewing 13 01-23-2012 05:00 PM


Forum Jump