Quote:
Originally Posted by HappyLoon View Post
Hey Kal,

Currently we only have a 220v outlet there, but I think it's a 30amp connection. Is it as simple as swapping it out for a 240v if the amperage is high enough?

To be honest none of us are that knowledgeable about the wiring, we had someone else do it. We did notice everything takes a bit longer to work though, especially the pumps. Would that be the reason?

I also noticed the amazon link on your site is to a 250v outlet. I'm guessing 250v is Ok?
The outlet rating is only that, what it's rated to handle as a maximum. Your household voltage is dependent on many things, mostly due to the load on your local substation. What you get is what you get.


__________________
Primary: Altbier
Secondary: What sorcery is this?
Bottled: RIS, Wee Heavy, Oaked Wee Heavy
Kegged: Cider, New England DIPA, Hibiscus Ginger Saison

 
Reply With Quote
Old 11-29-2012, 03:20 AM   #13
cdubbaya
Recipes 
 
Oct 2010
Bloomington, MN
Posts: 475
Liked 40 Times on 34 Posts


Quote:
Originally Posted by foos-n-brew
Hey HappyLoon - nice Foos table! From the looks of the rubber bands on the men it looks like you even practice.

Are you in MN by any chance?

Nice brewery too. That's what I hope to end up with.
Haha yeah we play quite a bit, those rubber bands are holding a few guys together, they still have lots of punch left! And yes we're in Minneapolis.
__________________
"To Thine Own Self Be Brew" -Shakesbeer

Honey Double IPA

 
Reply With Quote
Old 11-29-2012, 03:23 AM   #14
cdubbaya
Recipes 
 
Oct 2010
Bloomington, MN
Posts: 475
Liked 40 Times on 34 Posts


Quote:
Originally Posted by Stephonovich

The outlet rating is only that, what it's rated to handle as a maximum. Your household voltage is dependent on many things, mostly due to the load on your local substation. What you get is what you get.
Thanks for the response. Pardon my ignorance, but is there any way to draw more power from the outlet? It's actually a commercial building so there are many things drawing power. Not sure if that matters or not, but we would love to pull closer to 230-235v with a 240v outlet.
__________________
"To Thine Own Self Be Brew" -Shakesbeer

Honey Double IPA

 
Reply With Quote
Old 11-29-2012, 03:52 AM   #15
foos-n-brew
Recipes 
 
Nov 2011
Posts: 48
Liked 1 Times on 1 Posts


HappyLoon - do you ever go to Mort's or high Five (used to be Primetime) and play Foos? Check out minnesotafoosball.com sometime. A few of us are home brewers too. I'm gatekeeper on that site.

Happy brewing!

 
Reply With Quote
Old 11-29-2012, 04:13 AM   #16
cdubbaya
Recipes 
 
Oct 2010
Bloomington, MN
Posts: 475
Liked 40 Times on 34 Posts


Quote:
Originally Posted by foos-n-brew
HappyLoon - do you ever go to Mort's or high Five (used to be Primetime) and play Foos? Check out minnesotafoosball.com sometime. A few of us are home brewers too. I'm gatekeeper on that site.

Happy brewing!
I've been to morts once with some coworkers, it's a sweet place, but too tough for my level of skill. I'll check out the site, I was wondering where all the Minnesota foosers are. In North Dakota, where I went I school, everyone played it seemed.
__________________
"To Thine Own Self Be Brew" -Shakesbeer

Honey Double IPA

 
Reply With Quote
Old 11-29-2012, 03:07 PM   #17
kal
HBT_SUPPORTER.png
 
kal's Avatar
Recipes 
 
Nov 2006
Ottawa, Canada
Posts: 2,507
Liked 347 Times on 224 Posts


220V is odd. It's not usually available in the US. Are you running this in some sort of commercial environment where 208V 3-phase was available and they wired up one phase? That would make sense and explain why your pictures show 208-211V on the

When connected to two phases of a 208V 3-phase system, the heating element (designed for single phase 240V) will only produce 75% of its rated heating effect. So your 5500W elements are in effect behaving like 4125W elements. Everything will work fine, it'll just take longer to heat.

I'm not sure why you mean by the pumps taking longer. If you actually have 208V 3-phase power there and the outlet was wired correctly, he/she should have have wired it such as to provide 120V between one of the phases and neutral. This'll power the pump outlets on the control panel. So the pumps should be getting 120V. You can have them verify this with a multimeter placed on the pump receptacle.

I's typically ok to use an outlet (or any electronic device) that is rated to carry higher voltage or current than what you intend to use. The outlets rated to 250V can be used to carry voltages up to 250V. It doesn't have to be 250V.

Kal

 
Reply With Quote
Old 11-29-2012, 07:12 PM   #18
cdubbaya
Recipes 
 
Oct 2010
Bloomington, MN
Posts: 475
Liked 40 Times on 34 Posts


Quote:
Originally Posted by kal View Post
220V is odd. It's not usually available in the US. Are you running this in some sort of commercial environment where 208V 3-phase was available and they wired up one phase? That would make sense and explain why your pictures show 208-211V on the

When connected to two phases of a 208V 3-phase system, the heating element (designed for single phase 240V) will only produce 75% of its rated heating effect. So your 5500W elements are in effect behaving like 4125W elements. Everything will work fine, it'll just take longer to heat.

I'm not sure why you mean by the pumps taking longer. If you actually have 208V 3-phase power there and the outlet was wired correctly, he/she should have have wired it such as to provide 120V between one of the phases and neutral. This'll power the pump outlets on the control panel. So the pumps should be getting 120V. You can have them verify this with a multimeter placed on the pump receptacle.

I's typically ok to use an outlet (or any electronic device) that is rated to carry higher voltage or current than what you intend to use. The outlets rated to 250V can be used to carry voltages up to 250V. It doesn't have to be 250V.

Kal
I'm afraid my ignorance about electrical work is on display here. I just looked, and we do have a 250v/30A outlet wired in, and the fuse is 30A at the breaker as well. It appears to be the same outlet listed in your website.

I guess I'm not sure why the voltage is low, could it be we just don't have enough power to the building?
__________________
"To Thine Own Self Be Brew" -Shakesbeer

Honey Double IPA

 
Reply With Quote
Old 11-29-2012, 07:33 PM   #19
kal
HBT_SUPPORTER.png
 
kal's Avatar
Recipes 
 
Nov 2006
Ottawa, Canada
Posts: 2,507
Liked 347 Times on 224 Posts


Quote:
Originally Posted by HappyLoon View Post
I guess I'm not sure why the voltage is low, could it be we just don't have enough power to the building?
Likely not. While voltage can fluctuate slightly (for example it dips a bit in the summer during the day when everyone runs their A/C units), normally it's only slight. A dip from 240 down to 208 is enormous, into the danger zone for many devices, and would not be wanted or allowed under normal circumstances by any power company. That would be 104V on a 120V line and could damage equipment.

What sort of building is it? Is this s private home or a commercial/industrial location? Homes never have 3-phase 208V power. Commercial/industrial locations sometimes have 3-phase 208V power available to them.

Kal

 
Reply With Quote
Old 11-29-2012, 08:18 PM   #20
cdubbaya
Recipes 
 
Oct 2010
Bloomington, MN
Posts: 475
Liked 40 Times on 34 Posts


Quote:
Originally Posted by kal View Post
What sort of building is it? Is this s private home or a commercial/industrial location? Homes never have 3-phase 208V power. Commercial/industrial locations sometimes have 3-phase 208V power available to them.
Kal
It is a commercial building, but I don't have knowledge of the electrical system. I'll have to talk to the building owner about that.

Is the solution then to wire up the 3-phase 208V, or is that not an option?


__________________
"To Thine Own Self Be Brew" -Shakesbeer

Honey Double IPA

 
Reply With Quote
Reply
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
Hop porn scottland Recipes/Ingredients 14 12-08-2011 06:28 PM
Successful First Brew!!! Brew Porn and Food Porn! Large Pictures!!! talleymonster Extract Brewing 16 07-04-2007 12:16 PM


Forum Jump