I ran into a small hitch in my RIMS plan. My brewing area is only on a 15A circuit. I pulled an outlet and it is 14gauge wire, not 12 so I guess I'm stuck with 15A.

I assume it's ok to use a higher rated element at lower voltage. I'm thinking about using this element http://bostonheatingsupply.com/SP10869ML.aspx

it's a 240V 4500W element. based on my calculations it should be 1125W at 120V and only pull ~9.5A.

Any forseeable problems with this?

 
Reply With Quote
Old 11-06-2012, 01:25 AM   #2
Junkster
Recipes 
 
Feb 2011
North Central, Ohio
Posts: 509
Liked 31 Times on 22 Posts


Nope...

 
Reply With Quote
Old 11-06-2012, 02:35 AM   #3
Bobby_M
Vendor and Brewer
HBT_SPONSOR.png
 
Bobby_M's Avatar
Recipes 
 
Aug 2006
Whitehouse Station, NJ
Posts: 23,330
Liked 1765 Times on 1122 Posts


Why not just use a 1500 watt element? 1500/120= 12.5 amps.
__________________
Welcome to BrewHardware.com. I love you.
New Stirplates are IN!
Chugger Pumps, Pump Kits, Camlocks, Sightglasses, Clear USA made Silicone Tubing, RIMS, Electric Install Parts, etc.

 
Reply With Quote
Old 11-06-2012, 04:41 AM   #4
annoyingrob
Recipes 
 
Sep 2011
Calgary, AB
Posts: 74
Liked 6 Times on 5 Posts


Maybe he wants to be able to utilize the higher output in the future when he has 240v available, and doesn't want to buy two different elements?

Or maybe he's being ambitious and wiring it up to 240v/120v so he has two settings......

 
Reply With Quote
Old 11-09-2012, 02:07 AM   #5
RyanW
Recipes 
 
Apr 2009
Grand Rapids, MI
Posts: 8

Quote:
Why not just use a 1500 watt element? 1500/120= 12.5 amps.
Well I'm trying to stay under 80% of the circuit breaker rating. 80% of 15 is 12. Using the 1500W element wouldn't leave room for a pump.

 
Reply With Quote
Old 11-09-2012, 02:11 AM   #6
Bobby_M
Vendor and Brewer
HBT_SPONSOR.png
 
Bobby_M's Avatar
Recipes 
 
Aug 2006
Whitehouse Station, NJ
Posts: 23,330
Liked 1765 Times on 1122 Posts


You'd run a 1800 watt hair dryer on a 15amp circuit right?
__________________
Welcome to BrewHardware.com. I love you.
New Stirplates are IN!
Chugger Pumps, Pump Kits, Camlocks, Sightglasses, Clear USA made Silicone Tubing, RIMS, Electric Install Parts, etc.

 
Reply With Quote
Old 11-09-2012, 02:34 AM   #7
RyanW
Recipes 
 
Apr 2009
Grand Rapids, MI
Posts: 8

My bathroom circuits are all 20A. The kitchen are also 20A so my toaster and coffee maker are safe.

 
Reply With Quote
Old 11-11-2012, 05:29 AM   #8
thargrav
Registered User
Recipes 
 
Dec 2009
Huntsville, Alabama
Posts: 821
Liked 38 Times on 35 Posts


Quote:
Originally Posted by RyanW View Post
Well I'm trying to stay under 80% of the circuit breaker rating. 80% of 15 is 12. Using the 1500W element wouldn't leave room for a pump.
Why do so many assume you can't run a breaker at more than 80% of it's rating? A 15 Amp breaker is rated at 15 Amps, not 80% of 15 Amps and there is nothing wrong with loading it to 15 Amps.

A 1500 Watt element draws 12.5 Amps leaving plenty of capacity for your pump. You can even run a 1650 Watt element (13.75 Amps) and have plenty left over for your pump.

 
Reply With Quote
Old 11-11-2012, 05:35 AM   #9
whoaru99
Recipes 
 
Oct 2012
Posts: 1,760
Liked 140 Times on 117 Posts


Quote:
Originally Posted by Bobby_M View Post
You'd run a 1800 watt hair dryer on a 15amp circuit right?
Yes, you would for like 5 minutes, if you had lots of hair.
__________________
Drinking: Store Bought
Kegged: Cream Ale

 
Reply With Quote
Old 11-11-2012, 05:41 AM   #10
whoaru99
Recipes 
 
Oct 2012
Posts: 1,760
Liked 140 Times on 117 Posts


Quote:
Originally Posted by thargrav View Post
Why do so many assume you can't run a breaker at more than 80% of it's rating? A 15 Amp breaker is rated at 15 Amps, not 80% of 15 Amps and there is nothing wrong with loading it to 15 Amps.

A 1500 Watt element draws 12.5 Amps leaving plenty of capacity for your pump. You can even run a 1650 Watt element (13.75 Amps) and have plenty left over for your pump.

Seems I recall seeing that the 80% thing is for continuous loads, 3 hours or more.

But, yes, without regards to any code that may or may not apply, breakers are typically capable of holding 100% load indefinitely and some overload depending on amount and duration.
__________________
Drinking: Store Bought
Kegged: Cream Ale

 
Reply With Quote
Reply
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
Switch element from 240v to 120v brewsme Electric Brewing 5 07-21-2012 04:29 AM
Amps from 120v element on 240v circuit scottland Electric Brewing 3 05-21-2012 11:22 PM
Switch for running element at 120v OR 240V? thelorax121 Electric Brewing 14 05-10-2011 11:37 PM
Strange issue with 240v legs. 120v on both, no 240v Brewmoor Electric Brewing 5 12-03-2010 07:15 PM
Need advice- Using 240V water heater element for 120V? MTEXX Brew Stands 7 10-29-2009 03:20 PM


Forum Jump