Old 09-18-2012, 03:47 AM   #1
lorglath
HBT_SUPPORTER.png
 
lorglath's Avatar
Recipes 
 
Sep 2011
Minneapolis, MINNESOTA
Posts: 224
Liked 7 Times on 6 Posts



So I stopped by a garage sale and it had a locking 3 wire plug along with roughly 10 feet of 10 gauge 3 conductor wire. They were reasonably priced and I thought they would work perfect for hooking up to the heating element in my brewing system I am planning.

Question:
After looking closer, it seems these devices are rated for 125V @30A, and have a slightly different orientation of the locking pin.

Link on Amazon to what I bought: link

Link on Amazon to the 3 prong 30A 240V plug: link

is there honestly anything different internally that would make the 125V not capable to carry 125V on two separate wires thus making 250V? The wire itself is insulated and no big deal there. Just wanted to see if I shouldn't worry or if there is something I am missing



 
Reply With Quote
Old 09-18-2012, 03:54 AM   #2
Sublimis
Recipes 
 
Sep 2012
Colorado Springs, CO
Posts: 82
Liked 1 Times on 1 Posts


Quote:
Originally Posted by lorglath View Post
is there honestly anything different internally that would make the 125V not capable to carry 125V on two separate wires thus making 250V? The wire itself is insulated and no big deal there. Just wanted to see if I shouldn't worry or if there is something I am missing
NO. They configure these devices so that when you have a ton of receptacles or cord caps on a job or any location, you cant plug a 125A device in a 240v device or visa versa causing a potential hazard.



 
Reply With Quote
Old 09-18-2012, 04:16 AM   #3
lorglath
HBT_SUPPORTER.png
 
lorglath's Avatar
Recipes 
 
Sep 2011
Minneapolis, MINNESOTA
Posts: 224
Liked 7 Times on 6 Posts


but if the other end is connected to a brew kettle and the only mating connector within a city block is my brew panel for the heating element, is that really a big deal?

 
Reply With Quote
Old 09-18-2012, 04:34 AM   #4
Sublimis
Recipes 
 
Sep 2012
Colorado Springs, CO
Posts: 82
Liked 1 Times on 1 Posts


Its your call if you know that you're the only one using this connection and don't see any mixup then... If it was me I would take a white piece of phase tape wrap it around the cord caps and write "240v" on them or I would just get different cord caps in all but thats the Master Electrician in me.

Cheers

 
Reply With Quote
Old 09-18-2012, 01:48 PM   #5
lorglath
HBT_SUPPORTER.png
 
lorglath's Avatar
Recipes 
 
Sep 2011
Minneapolis, MINNESOTA
Posts: 224
Liked 7 Times on 6 Posts


Thanks for the input Sublimis! Your reason about many cords being at a job site does make sense that they would distinguish plugs via physical ability to plug them in.



 
Reply With Quote
Reply
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
20 amp plug question Homer Electric Brewing 5 02-26-2012 04:14 AM
60a plug question Mpavlik22 Electric Brewing 1 12-23-2011 09:30 PM
Electrical Dilemma NEMA 10-30P, NEMA 10-50R and 40A circuit breaker BroFratBrew Electric Brewing 1 12-14-2011 08:19 PM
NEMA Plugs wegz15 Electric Brewing 10 03-22-2011 06:02 AM
2kw heater element plug question devilishprune Electric Brewing 8 10-30-2010 07:24 PM


Forum Jump