Old 11-15-2012, 05:52 PM   #31
kickz28
Recipes 
 
Jul 2010
Ottawa
Posts: 52
Liked 2 Times on 2 Posts


Quote:
Originally Posted by CoalCracker View Post
No, the wiring is different. Compare the schematics with the white papers that came with the PID.



All powered up. Came out great!
Looks great! Can't wait to start working on mine!

 
Reply With Quote
Old 11-15-2012, 08:32 PM   #32
hatrickwah
Sponsor
HBT_SPONSOR.png
Recipes 
 
Nov 2010
UP, Michigan
Posts: 263
Liked 6 Times on 5 Posts


Quote:
Originally Posted by CoalCracker View Post
No, the wiring is different. Compare the schematics with the white papers that came with the PID.



All powered up. Came out great!
Looks sharp CoalCracker.
__________________
Keeping busy brewing & building.

Electric Brewing Supply

My e-Brewery | Keezer Build & Tap Tower Refurbish |Glycol System

 
Reply With Quote
Old 11-15-2012, 10:03 PM   #33
TwoDogBrew
Recipes 
 
Jun 2012
Raleigh, NC
Posts: 153
Liked 11 Times on 11 Posts


Quote:
Originally Posted by CoalCracker View Post
No, the wiring is different. Compare the schematics with the white papers that came with the PID.



All powered up. Came out great!
Can you give me an idea have the total cost of the panel..I want to do some comparisons

 
Reply With Quote
Old 11-20-2012, 11:02 PM   #34
Itsott
Recipes 
 
May 2012
Headland, Alabama
Posts: 254
Liked 16 Times on 14 Posts


Id also like to know some cost quotes.

 
Reply With Quote
Old 11-29-2012, 03:56 PM   #35
CoalCracker
Recipes 
 
Sep 2009
Macungie, Pa
Posts: 1,688
Liked 106 Times on 65 Posts


Kit cost:180.00
Enclosure:100.00
2 x PID: 91.00
Labels: 30.00
Paint: 12.00ish.
HeatSink: 18.00

This is all approximate but will get you fairly close.
__________________
coalcrackerbrewing.blogspot.com
Vintage Kegerator Build
1 BBL Tippy Dump

 
Reply With Quote
Old 12-30-2012, 02:09 PM   #36
movet22
HBT_SUPPORTER.png
 
movet22's Avatar
Recipes 
 
Sep 2011
Haddon Heights, NJ
Posts: 196
Liked 10 Times on 6 Posts


maybe a dumb question, but what are the white 'status' lights for?

 
Reply With Quote
Old 12-31-2012, 03:05 PM   #37
CoalCracker
Recipes 
 
Sep 2009
Macungie, Pa
Posts: 1,688
Liked 106 Times on 65 Posts


They show the status of the PID. If the PID kicks on, you have a light.
__________________
coalcrackerbrewing.blogspot.com
Vintage Kegerator Build
1 BBL Tippy Dump

 
Reply With Quote
Old 12-31-2012, 03:13 PM   #38
passedpawn
Waste Allocation Load Lifter - Earth Class
HBT_ADMIN.png
 
passedpawn's Avatar
Recipes 
 
Apr 2009
☼ Clearwater, FL ☼
Posts: 25,821
Liked 6690 Times on 3954 Posts


Quote:
Originally Posted by movet22 View Post
maybe a dumb question, but what are the white 'status' lights for?
Quote:
Originally Posted by CoalCracker View Post
They show the status of the PID. If the PID kicks on, you have a light.
Right, sort of. The white LEDs are wired directly to the element 240VAC power, but they ONLY light if the selector switch has selected element through it's respective contactor. Otherwise, though the PID is driving the SSR, the white LED won't come on.

There isn't any indicator showing the PID output (except for on the face of the PID).

Splitting hairs here, sorry.
__________________
- Andrew

 
Reply With Quote
Old 12-31-2012, 03:53 PM   #39
movet22
HBT_SUPPORTER.png
 
movet22's Avatar
Recipes 
 
Sep 2011
Haddon Heights, NJ
Posts: 196
Liked 10 Times on 6 Posts


Quote:
Originally Posted by passedpawn View Post
Right, sort of. The white LEDs are wired directly to the element 240VAC power, but they ONLY light if the selector switch has selected element through it's respective contactor. Otherwise, though the PID is driving the SSR, the white LED won't come on.

There isn't any indicator showing the PID output (except for on the face of the PID).

Splitting hairs here, sorry.
This is an example of why I am taking years to understand this before I attempt it myself. I am still confused.

I am certainly no electrician, so I apologize for the convoluted question below:

I understand that the yellow light goes on to indicate which element has been selected. Furthermore, I understand that the temp set on the PID will cause that number to be maintained by the element, which may result in some on-then-off-then-on again element power.... All of that being said, does the white light turn on to signify that the element is indeed being used by the PID at the moment? (And thus not illuminated when the temp has been set and the element need not be running?)

 
Reply With Quote
Old 12-31-2012, 04:10 PM   #40
passedpawn
Waste Allocation Load Lifter - Earth Class
HBT_ADMIN.png
 
passedpawn's Avatar
Recipes 
 
Apr 2009
☼ Clearwater, FL ☼
Posts: 25,821
Liked 6690 Times on 3954 Posts


Quote:
Originally Posted by movet22 View Post
does the white light turn on to signify that the element is indeed being used by the PID at the moment? (And thus not illuminated when the temp has been set and the element need not be running?)
Disclaimer: I'm just describing what I see in the schematic, linked above. I don't have this control panel (I built my own several years ago).

The white LED indicates that the element is actually getting power. So, yes to your question. But consider this scenario: you've selected Element #1 with the selector switch; PID #2 is set to 200F. What happens with the LEDs (yellow, white) for Element #2? Do they indicated what PID #2 is doing?

The answer is that PID #2 doesn't have any idea that Element #2 cannot get power. PID #2 will continue to drive SSR #2 in order to turn on Element #2, but Contactor #2 is disabled. Thus, neither the yellow or white LEDs for #2 every come on, even though the PID #2 is happily doing it's job.

You can't really figure any of this out if you don't understand the schematic.
__________________
- Andrew

 
Reply With Quote