House is only 120v! - Home Brew Forums
Home Brew Forums > Home Brewing Beer > Electric Brewing > House is only 120v!
Cool Brewing Giveaway - Supporting Membership Drive & Discount

Reply
 
Thread Tools
Old 08-25-2012, 07:55 PM   #1
benbradford
Recipes 
 
May 2007
Denver, Colorado
Posts: 1,007
Liked 33 Times on 29 Posts



I just got everything that I need to add a 240v sub panel, and discovered I might have a problem.

There are only 2 wires coming in from the meter.

1 goes to the nuetral bar, and the other goes to the right side of the breaker bar, but then is jumped to the left side of the breaker bar. The breakers only use the left or right side with the exception of a space in the bottom that could be a two pole breaker spot that attaches to both the left and the right.

Struggling with the fact that this house was probably built in the 20's and may only have 120.

There is no 2 pole breakers on the panel.

The dryer is a stacked 120v.

Gas everthing.

I could take a picture, but would be a pain to make it helpful(pull breakers)..


__________________
I think it's too bad that everybody's decided to turn on drugs, I don't think drugs are the problem. Crime is the problem. Cops are the problem. Money's the problem. But drugs are just drugs.
Jerry Garcia

 
Reply With Quote
Old 08-25-2012, 08:13 PM   #2
Bobby_M
Vendor and Brewer
HBT_SPONSOR.png
 
Bobby_M's Avatar
Recipes 
 
Aug 2006
Whitehouse Station, NJ
Posts: 22,980
Liked 1586 Times on 1023 Posts


Is there a main breaker? If so, what is the amperage?

Sounds like it's time to get some service upgrade quotes.


__________________
Welcome to BrewHardware.com. I love you.
BIAB Large Mesh False Bottoms and SS HERMS COILS are IN!!
Chugger Pumps, Pump Kits, Camlocks, Sightglasses, Clear USA made Silicone Tubing, RIMS, Electric Install Parts, etc.

 
Reply With Quote
Old 08-25-2012, 08:14 PM   #3
benbradford
Recipes 
 
May 2007
Denver, Colorado
Posts: 1,007
Liked 33 Times on 29 Posts


It's funny.... no main breaker.
__________________
I think it's too bad that everybody's decided to turn on drugs, I don't think drugs are the problem. Crime is the problem. Cops are the problem. Money's the problem. But drugs are just drugs.
Jerry Garcia

 
Reply With Quote
Old 08-25-2012, 09:17 PM   #4
P-J
HBT_LIFETIMESUPPORTER.png
Recipes 
 
Mar 2010
Charlotte, NC
Posts: 3,337
Liked 300 Times on 235 Posts


If the house was built in the 20's, it is more than likely that the entire house was wired using "knob & tubing" method being done at that time. If so: Set yourself up for a complete home wiring job. If I were in you situation, I'd call the power company for assistance, recommendations and help.

Wish we were closer, I'd help. Been through that before when I was a pre-teen. (Long, long story.)

P-J

 
Reply With Quote
Old 08-25-2012, 09:27 PM   #5
benbradford
Recipes 
 
May 2007
Denver, Colorado
Posts: 1,007
Liked 33 Times on 29 Posts


It is actually rewired already, with nice new armored cable all thoughout... It is just the circuit box is 120 service i believe... I will add a picture of the wiring schematic that is being used for the panel.
Click image for larger version

Name:	a1.jpg
Views:	609
Size:	49.1 KB
ID:	73186  
__________________
I think it's too bad that everybody's decided to turn on drugs, I don't think drugs are the problem. Crime is the problem. Cops are the problem. Money's the problem. But drugs are just drugs.
Jerry Garcia

 
Reply With Quote
Old 08-25-2012, 09:29 PM   #6
Hammy71
Senior Member
HBT_SUPPORTER.png
 
Hammy71's Avatar
Recipes 
 
Sep 2008
, Maryland, The Tax Me State
Posts: 5,863
Liked 520 Times on 395 Posts


Yeah, at the very least a service change is in order. Ask around for an electrical contractor you can trust. Won't be cheap, but will be worth it. More for the safety aspect than the brewing. A 125 capacity ain't much these days.

 
Reply With Quote
Old 08-26-2012, 07:09 PM   #7
benbradford
Recipes 
 
May 2007
Denver, Colorado
Posts: 1,007
Liked 33 Times on 29 Posts


Can't do a service change... I rent!

I have no problem removing this when I leave, so patching a couple of small holes is no issue.

Here is a picture of the current box. Any ideas about how I can simply add a sub panel that will power 3 2500w 120v elements? 5 would be better, but 3 will work.
Click image for larger version

Name:	box.jpg
Views:	569
Size:	49.8 KB
ID:	73304  
__________________
I think it's too bad that everybody's decided to turn on drugs, I don't think drugs are the problem. Crime is the problem. Cops are the problem. Money's the problem. But drugs are just drugs.
Jerry Garcia

 
Reply With Quote
Old 08-26-2012, 08:08 PM   #8
drewmedic23
Recipes 
 
Aug 2012
Jackson, NJ
Posts: 252
Liked 9 Times on 9 Posts


I may be shooting in the dark here but it could be worth the try to get your landlord to upgrade the service...if you play the safety card you might have some luck

 
Reply With Quote
Old 08-26-2012, 09:07 PM   #9
benbradford
Recipes 
 
May 2007
Denver, Colorado
Posts: 1,007
Liked 33 Times on 29 Posts


I would rather not involve him... Not hiding anything, just easier I find to keep it simple.
__________________
I think it's too bad that everybody's decided to turn on drugs, I don't think drugs are the problem. Crime is the problem. Cops are the problem. Money's the problem. But drugs are just drugs.
Jerry Garcia

 
Reply With Quote
Old 08-26-2012, 10:45 PM   #10
wilserbrewer
BIAB Expert Tailor
HBT_SPONSOR.png
 
wilserbrewer's Avatar
Recipes 
 
May 2007
Jersey Shore, Jersey
Posts: 9,239
Liked 1255 Times on 959 Posts


Quote:
Originally Posted by benbradford View Post
Any ideas about how I can simply add a sub panel that will power 3 2500w 120v elements? 5 would be better, but 3 will work.
Holy crap you think big! 5 elements at 2500w each is 12,500w What size batches are you looking to do, 50 gal.??? 4000w will do 10 gallon batches.



 
Reply With Quote
Reply
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
120v 5 gal questions movet22 Electric Brewing 26 10-10-2011 11:35 AM
can someone help with 120v? agezzi Electric Brewing 58 08-15-2011 11:12 AM
heating element and regular 120V house outlet iamatuna Electric Brewing 4 03-11-2011 02:35 PM
120V wiring help magnj Electric Brewing 1 02-20-2011 09:19 PM
120v Switches CoalCracker Electric Brewing 7 10-15-2010 08:53 PM


Forum Jump