Old 08-14-2012, 11:56 AM   #11
rack04
Recipes 
 
Dec 2010
Dallas, TX
Posts: 474
Liked 4 Times on 4 Posts


Quote:
Originally Posted by Dgonza9 View Post
How large are your batches? A propane burners should give you plenty of power, no? Or was that a typo and you're on a stovetop burner?

I'd be a bit nervous with electrical connections in the vicinity of open flames, no? Maybe I'm wrong as my propane days were a number of years ago, but the potted electrical connections are obviously right up against the keggle. JMO.
I am currently doing 10 gallon batches outside on a two burner single tier stand. I have shifted direction and I'm basically trying to find a way of brewing inside to avoid the insane summer heat. I would be doing 5 gallons batches on either 110V 20A GFI which is already available or 220V 30A which would require installation of spa panel.



 
Reply With Quote
Old 08-15-2012, 12:38 AM   #12
rack04
Recipes 
 
Dec 2010
Dallas, TX
Posts: 474
Liked 4 Times on 4 Posts


I have changed direction. My intent is to build a 5 gal batch system (7.5 gal pre boil) BIAB kettle that will work on 120V. I figure I will need 2 120V 2000W heating elements to get this volume to boil. I have 2 GFCI receptacles in my kitchen that are on separate 20A circuits. Since I will be pulling 16.7A per heating element I would like to ensure that everything is rated up to 20A. My GFCI receptacles look like this so I assume this is a 15A GFCI receptacle. There is nothing on the receptacle to indicate what amp it is.



I plan to follow this wiring diagram except I would like individual switches and lights on the heating elements. If someone could help modifying this diagram to have switches and lights I would greatly appreciate it.




 
Reply With Quote
Old 08-15-2012, 12:41 AM   #13
thorongil
Recipes 
 
Aug 2007
Buckeye, Arizona
Posts: 229
Liked 4 Times on 2 Posts


In my experience a 2000W element will barely boil 5.5 gal. I start with 6.5 then drain off 1.5 and boil it on the stovetop. I'll add this back in the last 10 min or so of the boil...
__________________
“Altogether 1420 in the Shire was a marvelous year... The Northfarthing barley was so fine that the beer of 1420 malt was long remembered and became a byword. Indeed a generation later one might hear an old gaffer in an inn, after a good pint of well-earned ale, put down his mug with a sigh: ‘Ah! that was a proper fourteen-twenty, that was!’”

- J.R.R. Tolkien, The Lord of the Rings, The Return of the King

 
Reply With Quote
Old 08-15-2012, 01:12 AM   #14
P-J
HBT_LIFETIMESUPPORTER.png
Recipes 
 
Mar 2010
Charlotte, NC
Posts: 3,337
Liked 301 Times on 235 Posts


Quote:
Originally Posted by rack04 View Post
I have changed direction. My intent is to build a 5 gal batch system (7.5 gal pre boil) BIAB kettle that will work on 120V. I figure I will need 2 120V 2000W heating elements to get this volume to boil. I have 2 GFCI receptacles in my kitchen that are on separate 20A circuits. Since I will be pulling 16.7A per heating element I would like to ensure that everything is rated up to 20A.
...

I plan to follow this wiring diagram except I would like individual switches and lights on the heating elements. If someone could help modifying this diagram to have switches and lights I would greatly appreciate it.
...
I drew and posted a diagram today that will probably fit your request:

Electric Brewing Forum: 110v recirculating ebiab 2.5 gallon batches - post #33

I hope it is a good solution for you.

P-J

 
Reply With Quote
Old 08-15-2012, 01:33 AM   #15
rack04
Recipes 
 
Dec 2010
Dallas, TX
Posts: 474
Liked 4 Times on 4 Posts


Thanks a lot for the wire diagram. Can anyone tell me if the picture of the GFCI receptacle I posted appears to be 15A. The 20A GFCI receptacles and plugs that I have seen have a different plug orientation, ie on prong is perpendicular to the other.

 
Reply With Quote
Old 08-15-2012, 01:41 AM   #16
abarnett
Recipes 
 
Nov 2011
Jenkintown, PA
Posts: 159
Liked 4 Times on 3 Posts


I would agree that those are probably not 20a outlets. And if they're not 20a, your wiring probably only supports 15a, so it won't help to switch just the outlets.

 
Reply With Quote
Old 08-15-2012, 02:11 AM   #17
rack04
Recipes 
 
Dec 2010
Dallas, TX
Posts: 474
Liked 4 Times on 4 Posts


Quote:
Originally Posted by abarnett View Post
I would agree that those are probably not 20a outlets. And if they're not 20a, your wiring probably only supports 15a, so it won't help to switch just the outlets.
The receptacles are connected to 20A breakers so I'm confused. I'll probably take one of the receptacles out and verify if the wiring is 12 gauge or 14 gauge. I may step down to 1500W heating elements to be safe. Anyone know if 2 120V 1500W elements can boil 7.5 gallons?

 
Reply With Quote
Old 08-15-2012, 02:21 AM   #18
P-J
HBT_LIFETIMESUPPORTER.png
Recipes 
 
Mar 2010
Charlotte, NC
Posts: 3,337
Liked 301 Times on 235 Posts


The circuit breaker is 20A - therefore the wire will be 12 gauge. I do not believe you will be at any risk using the system with those GFCI outlets. The only problem I could see is if your refrigerator or another appliance is on the same circuit. That's something easy to check out though.

Just my humble opinion.

P-J

Edit: Here is a 20A outlet layout:



The same plug works with it.

 
Reply With Quote
Old 08-15-2012, 02:24 AM   #19
rack04
Recipes 
 
Dec 2010
Dallas, TX
Posts: 474
Liked 4 Times on 4 Posts


Quote:
Originally Posted by P-J View Post
I drew and posted a diagram today that will probably fit your request:

Electric Brewing Forum: 110v recirculating ebiab 2.5 gallon batches - post #33

I hope it is a good solution for you.

P-J
I looks like a great solution. They only thing I don't need in the diagram is the pump. I'm pretty confident I can figure out how to modify the wiring to take this out. How are the resistors wired into the system?

I assume these resisters would work?

http://www.parts-express.com/pe/show...tnumber=003-1K

And these fuses?

http://www.parts-express.com/pe/show...number=070-612

http://www.parts-express.com/pe/show...number=071-818

 
Reply With Quote
Old 08-15-2012, 02:29 AM   #20
wilserbrewer
BIAB Expert Tailor
HBT_SPONSOR.png
 
wilserbrewer's Avatar
Recipes 
 
May 2007
Jersey Shore, Jersey
Posts: 9,368
Liked 1302 Times on 998 Posts


Quote:
Originally Posted by rack04 View Post
Anyone know if 2 120V 1500W elements can boil 7.5 gallons?
Yes, 3000w will boil 7.5 gal IME...of course not as fast as 5500w, but reasonable.



 
Reply With Quote
Reply
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
Switch element from 240v to 120v brewsme Electric Brewing 5 07-21-2012 04:29 AM
240v LED wiring - need fuses/resistors? DustBow Electric Brewing 4 07-14-2012 12:47 AM
Would this SSR work for both legs of a 240v element NinjaJoe Electric Brewing 3 03-06-2012 10:46 PM
GFI breakers and wiring a 220v heating element CanadianNorth Electric Brewing 7 05-27-2011 01:14 PM
wiring a 240V heater to a Kettle CanadianNorth Electric Brewing 9 03-31-2011 11:01 PM


Forum Jump