My current plans involve 5 sensors in the chamber to run the controls, plus a sensor in my ice chamber and one on the outside of the entire chamber for data logging. I don't have the parts I need for a thermowell, and I'll be filling my conical tomorrow, so that'll have to wait for a few weeks until the IPA is done dry hopping
I must say, the choice of old school ice box tech with a modern control system is an interesting mash up- almost steam punk if you use some exposed mechanical actuators for doors an such.

I only bring this up because you seem to be interested in very fine temp control- using a single thermowell to control temp in a ferm vessel, conical or otherwise, can result in radial stratification during later stages, unless the location is almost ideal. From other threads, that location is very close to the wall, and about mid-way on height, but that location is variable, especially depending on how it is chilled- air, jacket(s), immersed coil, etc.

Also, controlling the vessel temp without using the actual vessel temp in the control loop borders on the impossible. This method is difficult even with passive objects if the air temp sensor is not close to the vessel.

Are you planning on have one large chamber, or multiple small ones with separate fans? I ask because it is impossible to control multiple active ferments in one chamber with only one control input. More precisely, to control n fermenters, you would need at least n+1 control inputs. If you could guarantee one vessel would always generate more heat than all others, you would only need n inputs.

A real world example is a guy who uses a single fridge and 4 heat wraps to control 4 fermenters. The fridge is set to a temp low enough to keep any active ferment in check.

The elephant in the room is why you sprang for a conical, and don't drop some coin (<$50 or free) for a Craig's list fridge to put it in, or at least use as a cooling source.

When people talk about building chambers, I always think of this thread:
http://www.homebrewtalk.com/f51/full...-200-a-175456/

The punch line is here:
http://www.homebrewtalk.com/f51/full...6/#post2616114

But what is even funnier, is that the thread continues with people asking all kinds of questions about how to do it.

 
Reply With Quote
Old 07-21-2012, 03:33 PM   #82
carlisle_bob
Recipes 
 
Apr 2012
Carlisle, PA
Posts: 1,206
Liked 29 Times on 28 Posts


Quote:
Originally Posted by Eighty2Fifty1 View Post
So I'd want something that would take a faulty sensor out of the equation? Like if it returns an obviously wrong value, it stops using that sensor to cycle the heater and cooler?
Hi

What sort of sensor are you using? If it's one of the one wire gizmos, it will return junk data from time to time. Some sensor setups get "jammed" buy nearby cell phones. It's a pretty good bet that your system has a range that's reasonable for a reading. Tossing out data past that range is the first step. Counting how much you have tossed is the next. Deciding weather you are in trouble and what to do about it is the fun part.

Most systems cluster data as it's collected. Taking 5 or more data points, sorting them, tossing out the high and low, averaging the remaining three is normal. How that interacts with a toss out process is a "that depends" sort of thing. Usually the discard high / low only gets done if there are >= 5 points left after the discard.

That's all fine if you are running a fairly slow moving system with lots of data collection. If you have a slow sensor and a fast moving gizmo, you may need to do it a bit differently.

Bob

Bob

 
Reply With Quote
Old 07-21-2012, 06:35 PM   #83
Eighty2Fifty1
 
Eighty2Fifty1's Avatar
Recipes 
 
Jun 2011
Oak Harbor, WA
Posts: 129
Liked 9 Times on 7 Posts


Quote:
Originally Posted by cwi View Post
I must say, the choice of old school ice box tech with a modern control system is an interesting mash up- almost steam punk if you use some exposed mechanical actuators for doors an such.

I only bring this up because you seem to be interested in very fine temp control- using a single thermowell to control temp in a ferm vessel, conical or otherwise, can result in radial stratification during later stages, unless the location is almost ideal. From other threads, that location is very close to the wall, and about mid-way on height, but that location is variable, especially depending on how it is chilled- air, jacket(s), immersed coil, etc.

Also, controlling the vessel temp without using the actual vessel temp in the control loop borders on the impossible. This method is difficult even with passive objects if the air temp sensor is not close to the vessel.

Are you planning on have one large chamber, or multiple small ones with separate fans? I ask because it is impossible to control multiple active ferments in one chamber with only one control input. More precisely, to control n fermenters, you would need at least n+1 control inputs. If you could guarantee one vessel would always generate more heat than all others, you would only need n inputs.

A real world example is a guy who uses a single fridge and 4 heat wraps to control 4 fermenters. The fridge is set to a temp low enough to keep any active ferment in check.

The elephant in the room is why you sprang for a conical, and don't drop some coin (<$50 or free) for a Craig's list fridge to put it in, or at least use as a cooling source.

When people talk about building chambers, I always think of this thread:
http://www.homebrewtalk.com/f51/full...-200-a-175456/

The punch line is here:
http://www.homebrewtalk.com/f51/full...6/#post2616114

But what is even funnier, is that the thread continues with people asking all kinds of questions about how to do it.
I wish I could say I planned this project to be some sort of tech mashup. I chose not to go with a fridge quite simply because my conical is too big to fit in any standard fridge that I've seen. My ferm chamber is about 60 cf, it's sized to fit 3 of the 15g Minibrew conicals. Using the guts out of one for cooling, however, is something that I might do, depending on how the icebox works. Where I live, I'll be heating it about 90% of the time, so I don't feel like I need a cooling source with a lot of juice anyways. Originally, I bought an STC-1000 for the project, but once I started reading about Arduino and everything it does, I decided to go that route. I've learned all sorts of thing about programming that I never would have otherwise, so I'm pretty happy about that. I might use the STC-1000 to power another fridge if I ever decide to do any more lagers. As far as separate chambers, I'd be lying if I said I'd thought that far down the road yet. If I went with the idea you mentioned of having one heater blanket per fermenter and keeping the ambient temp cooler, would I really need to? As far as fine temp controls, I'll be pretty happy if my chamber can control the beer temp to +/- 2 deg F.
__________________
Beer is not the answer. Beer is the question. Yes is the answer.

 
Reply With Quote
Old 07-21-2012, 07:21 PM   #84
cwi
Registered User
Recipes 
 
Jun 2010
Austin
Posts: 845
Liked 34 Times on 28 Posts


Quote:
Originally Posted by Eighty2Fifty1 View Post
I wish I could say I planned this project to be some sort of tech mashup. I chose not to go with a fridge quite simply because my conical is too big to fit in any standard fridge that I've seen. My ferm chamber is about 60 cf, it's sized to fit 3 of the 15g Minibrew conicals. Using the guts out of one for cooling, however, is something that I might do, depending on how the icebox works. Where I live, I'll be heating it about 90% of the time, so I don't feel like I need a cooling source with a lot of juice anyways. Originally, I bought an STC-1000 for the project, but once I started reading about Arduino and everything it does, I decided to go that route. I've learned all sorts of thing about programming that I never would have otherwise, so I'm pretty happy about that. I might use the STC-1000 to power another fridge if I ever decide to do any more lagers. As far as separate chambers, I'd be lying if I said I'd thought that far down the road yet. If I went with the idea you mentioned of having one heater blanket per fermenter and keeping the ambient temp cooler, would I really need to? As far as fine temp controls, I'll be pretty happy if my chamber can control the beer temp to +/- 2 deg F.
Read the ferm chamber thread I linked. That one used fridge guts, and he still had the wood disintegrate. Using ice? Depends on your build materials.

For your setup, using a small window A/C unit is a much more appropriate solution. There are threads on how to do it. Most involve a simple trick to override the factory control/sensor. Your STC-1000 would be a good choice for controlling the A/C unit

Unless your ambient temp <50F 90% of the time, you will be using cooling much more than 90% of the time. A 15G batch can probably crank out ~60W at peak, but that is only a rough guess based on the 40W number I have heard bandied about for peak on a 5G batch. 40W actually sounds high to me, but I can't find much other info. The rule of thumb is your fermenter will be ~10F higher than ambient during peak.

The cold chamber with heat wraps for each fermenter is perfectly functional, but a little wasteful of energy. This method can give very tight control because the wraps are not limited to on/off setpoint control, although that approach would easily give ~1F variance. Search for the DIY fermwrap threads. The raw material is plastic sheeting with heating elements embedded, and pinch-on connectors to make your own on the cheap. Your arduino would be a good fit for controlling the wraps using any number of control methods- that is the beauty of software based control systems.

 
Reply With Quote
Old 07-21-2012, 11:18 PM   #85
Eighty2Fifty1
 
Eighty2Fifty1's Avatar
Recipes 
 
Jun 2011
Oak Harbor, WA
Posts: 129
Liked 9 Times on 7 Posts


Quote:
Originally Posted by carlisle_bob View Post
Hi

What sort of sensor are you using? If it's one of the one wire gizmos, it will return junk data from time to time. Some sensor setups get "jammed" buy nearby cell phones. It's a pretty good bet that your system has a range that's reasonable for a reading. Tossing out data past that range is the first step. Counting how much you have tossed is the next. Deciding weather you are in trouble and what to do about it is the fun part.

Most systems cluster data as it's collected. Taking 5 or more data points, sorting them, tossing out the high and low, averaging the remaining three is normal. How that interacts with a toss out process is a "that depends" sort of thing. Usually the discard high / low only gets done if there are >= 5 points left after the discard.

That's all fine if you are running a fairly slow moving system with lots of data collection. If you have a slow sensor and a fast moving gizmo, you may need to do it a bit differently.

Bob

Bob
I'm using DS18B20's
__________________
Beer is not the answer. Beer is the question. Yes is the answer.

 
Reply With Quote
Old 08-14-2012, 08:57 PM   #86
helibrewer
HBT_SUPPORTER.png
 
helibrewer's Avatar
Recipes 
 
Nov 2011
Santa Rosa, CA
Posts: 3,813
Liked 326 Times on 275 Posts


Quote:
Originally Posted by cwi View Post
Read the ferm chamber thread I linked. That one used fridge guts, and he still had the wood disintegrate. Using ice? Depends on your build materials.

For your setup, using a small window A/C unit is a much more appropriate solution. There are threads on how to do it. Most involve a simple trick to override the factory control/sensor. Your STC-1000 would be a good choice for controlling the A/C unit

Unless your ambient temp <50F 90% of the time, you will be using cooling much more than 90% of the time. A 15G batch can probably crank out ~60W at peak, but that is only a rough guess based on the 40W number I have heard bandied about for peak on a 5G batch. 40W actually sounds high to me, but I can't find much other info. The rule of thumb is your fermenter will be ~10F higher than ambient during peak.

The cold chamber with heat wraps for each fermenter is perfectly functional, but a little wasteful of energy. This method can give very tight control because the wraps are not limited to on/off setpoint control, although that approach would easily give ~1F variance. Search for the DIY fermwrap threads. The raw material is plastic sheeting with heating elements embedded, and pinch-on connectors to make your own on the cheap. Your arduino would be a good fit for controlling the wraps using any number of control methods- that is the beauty of software based control systems.
That is precisely what I do with this: http://www.restlesscellars.com/data/...b8ec850e53.jpg

I keep the upper chamber cooled to 35-40F depending on whether I am lagering anything or just serving.

My fermentors get wrapped with FermWrap and are controlled by their own STC-1000. This allows me to do lagers and ales together in the same chamber while still being able to serve or lager existing batches.

It does waste some energy but monitoring is minimal and control is very good.
__________________
Something is always fermenting....
"It's Bahl Hornin'"

Primary:
Kegged: Bourbon Barrel Imperial Stout
On Deck: German Lager

 
Reply With Quote
Old 08-16-2012, 06:39 AM   #87
Eighty2Fifty1
 
Eighty2Fifty1's Avatar
Recipes 
 
Jun 2011
Oak Harbor, WA
Posts: 129
Liked 9 Times on 7 Posts


Well, work took me out of the country for a bit, but I'm back and ready to get back to work on my project. Today I scored a free freezer on Craigslist, so I'll be using that, powered by my STC-1000 to cool the chamber, and the arduino to power heat wraps for the individual fermenters. Hopefully I can get it going this weekend. The way the weather has been lately, I doubt I'll need the heat yet anyways. This brings me to my next question. How do you get the data from your sensors to show up on those fancy graphs?
__________________
Beer is not the answer. Beer is the question. Yes is the answer.

 
Reply With Quote
Old 08-16-2012, 10:56 AM   #88
jpalarchio
Recipes 
 
Jan 2009
Holly, MI
Posts: 562
Liked 50 Times on 41 Posts


Quote:
Originally Posted by Eighty2Fifty1 View Post
How do you get the data from your sensors to show up on those fancy graphs?
Graphing means historical data and thus logging. You would need to store the data somewhere and then find a way to graph it (either via a web request or something more manual like importing a CSV into Excel). Several options, some by storing the data on an SD card on the Arduino, others by sending the data externally to a server of your own or one out on the Internet.

The Cosm (formerly Pachube) Arduino example is a start: http://arduino.cc/en/Tutorial/CosmClient

 
Reply With Quote
Old 03-20-2013, 12:53 PM   #89
rpierce
Recipes 
 
Mar 2013
Posts: 12

Some friends and I have done something very similar at a local hackerspace (Pumping Station: One) in Chicago.

First suggestion: Ditch the Arduino, use a Raspberry Pi. I've worked with both, and while I love the Arduino, getting it on the Internet is a pain. By comparison, a Raspberry Pi is a fully functioning Linux box on a board the size of a credit card. So you can run a web server on it, a SQL database to store historical data, and you can access it remotely. You've also got a wider choice of programming or scripting languages.

We used a Raspberry Pi running a PID loop we coded in Python. Temperature came from analog TMP36 sensors and an MCP3008 ADC. This is nowhere near as accurate as you can get with a DS18B20. (The Pi CAN do OneWire and can support DS18B20s; you need the Occidentalis Linux distribution Adafruit released which includes a OneWire kernel driver.) The Python code also broadcast data on a message bus to a web server which drew a graph on a web page, as well as the P, I, and D components, and it would also act as a bot on an IRC channel to inform people of the temperatures when someone asked it. We used hardwired ethernet; WiFi is possible, but you will probably need a powered USB hub because I don't think the Pi can power a USB WiFi dongle.

We chilled the fermenting chamber with a window air conditioner. The Pi can only provide 50 mA on its GPIO pins, so a solid state relay powered a much larger relay which powered the air conditioner. We used a 5 minute duty cycle with a minimum 2 minute off time time protect the compressor. Because the air temperature swings wildly, we averaged it every second over the five minute period, and used that to determine the error for the next 5 minutes. The resulting average at the end of each period was pretty tightly regulated by PID.

I've just designed a circuit board for the Pi to do this, and am releasing it as open hardware. I'm still waiting to get the board back from the board house, so I haven't debugged it. More info here.

 
Reply With Quote
Old 03-20-2013, 02:03 PM   #90
mirogster
Recipes 
 
May 2011
New York, New York
Posts: 125
Liked 8 Times on 6 Posts


Actually, you can use (unfortunately) only FEW unpowered usb wifi dongles. Just check RaspberryPi forum for detailed specs

 