Default Possible Hazard

I have just completed my EBIAB control panel. Its a single PID, single element panel. 30A 240V. After the first time turning it on I was poking around with a voltage detector. My SPST toggle switch which is rated for 30A and only flip a 120v coil for my contactor cause my detector to light up. Does this mean there is current running through the actual metal toggle, or is it just registering the current that the switch is allowing through it.

Thanks


__________________
two pints homebrew
kegs...............none :(
carboys...........Brass Knuckle Ale, Rustic Black Porter
hopville.

"buy the ticket, take the ride, no sympathy for the devil."
-Hunter S Thompson
mazultav is offline
 
Reply With Quote
Old 04-18-2012, 06:28 PM   #2
ryclo
Feedback Score: 0 reviews
Recipes 
 
Join Date: May 2011
Location: marga, ritaville
Posts: 131
Liked 22 Times on 3 Posts
Likes Given: 3

Default

you answered your own question, voltage detectors detect voltage not current.


ryclo is offline
 
Reply With Quote
Old 04-18-2012, 07:29 PM   #3
stlbeer
Senior Member
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
stlbeer's Avatar
Recipes 
 
Join Date: Jan 2008
Location: Fenton, MO
Posts: 946
Liked 37 Times on 36 Posts
Likes Given: 92

Default

The current is only flowing through the switch where the contacts are on the back. It is not going through the metal front part of the toggle switch.
__________________
My RIMS eBrewery build
stlbeer is offline
 
Reply With Quote
Old 04-18-2012, 07:48 PM   #4
mazultav
Feedback Score: 0 reviews
Recipes 
 
Join Date: Jun 2007
Location: Fremont NH, NH
Posts: 85
Default

OK thanks. I think I knew that, but a flashing red light can give you The Fear.
__________________
two pints homebrew
kegs...............none :(
carboys...........Brass Knuckle Ale, Rustic Black Porter
hopville.

"buy the ticket, take the ride, no sympathy for the devil."
-Hunter S Thompson
mazultav is offline
 
Reply With Quote
Old 04-19-2012, 02:03 AM   #5
l3asturd
Feedback Score: 0 reviews
Recipes 
 
Join Date: Dec 2011
Location: Visalia, CA
Posts: 464
Liked 8 Times on 7 Posts
Likes Given: 2

Default

I'm assuming you mean an inductive voltage detector. The kind you put near an outlet to see if it's energized? Yes they will detect voltage potential at the switches terminals. The best way to test for voltage is with a voltmeter though. The inductive testers only work for AC voltage because DC only fluxes when turned on and when turned off.
l3asturd is offline
 
Reply With Quote
Old 04-19-2012, 09:52 AM   #6
mazultav
Feedback Score: 0 reviews
Recipes 
 
Join Date: Jun 2007
Location: Fremont NH, NH
Posts: 85
Default

Right it's a tester with a single probe, looks like a futuristic pencil, and when I put it near the actual metal switch, not just the terminals it lights up.
__________________
two pints homebrew
kegs...............none :(
carboys...........Brass Knuckle Ale, Rustic Black Porter
hopville.

"buy the ticket, take the ride, no sympathy for the devil."
-Hunter S Thompson
mazultav is offline
 
Reply With Quote
Old 04-19-2012, 01:25 PM   #7
kpr121
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
kpr121's Avatar
Recipes 
 
Join Date: Jul 2009
Location: Pittsburgh, PA
Posts: 3,107
Liked 121 Times on 106 Posts
Likes Given: 162

Default

Check with a voltmeter. One test probe on the switch, the other to neutral or ground. If you see a voltage, then the switch is energized. This is highly unlikely though if you were careful with your connections...

Also, most good switches will either have a seperate ground connection or will be grounded to the panel that it is installed in. So if the panel is properly grounded, and the switch was accidently energized, it should cause a short and your GFCI (you do have GFCI protection right?) will trip.
__________________
Ferm Chamber on top of Keezer / Through Wall / All in One Build


Primary: Two Hearted Clone[B]
Secondary: Table Red Wine, Table White Wine
Kegged:Oberon Clone, "Campfire" Hoppy Red Ale, Brown Trout Stout, Cider
Bottled: Random stuff(Cider, Mead, Wines)
Bulk Aging: Red wine, Blueberry "Brandy"
Up Next: Citra Blonde, Kolsch, IPA, IPA, IPA
kpr121 is offline
 
Reply With Quote
Old 04-21-2012, 02:11 AM   #8
mazultav
Feedback Score: 0 reviews
Recipes 
 
Join Date: Jun 2007
Location: Fremont NH, NH
Posts: 85
Default

I went back and check with my multimeter, no voltage on the switches. Thanks everyone.


__________________
two pints homebrew
kegs...............none :(
carboys...........Brass Knuckle Ale, Rustic Black Porter
hopville.

"buy the ticket, take the ride, no sympathy for the devil."
-Hunter S Thompson
mazultav is offline
 
Reply With Quote
Reply


Thread Tools



Forum Jump

Newest Threads

LATEST SPONSOR DEALS